I would like to double check on the coverage of attached garages in an NFPA 13R system.
NFPA 13R 2010 6.6.6: Sprinklers shall not be required in... other concealed spaces that are not used or intended for living purposes or storage and do not contain fuel fired equipment. NFPA 13R 2010 6.6.5: Sprinklers shall not be required in any ... carports, and stairs that are open and attached. There is a separate reference other than 6.6.6 on the coverage of attached garages. The way I read it, they must be covered under this standard. Please advise. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Thomas Jones III
4/17/2020 10:04:17 am
I agree that they need to be covered and I have always done so in my drawings.
Reply
Arthur Pursell
4/17/2020 10:07:19 am
Typically always covered; residential heads utilized; calc at .15 density
Reply
sean
4/17/2020 10:08:05 am
Sprinkler are required in garages. Carports are not garages.
Reply
Jesse
4/17/2020 10:08:57 am
Using 13R, you'll need to protect the garage. The question being whether you protect the garage with 13D or with 13. Look at 13-D Chapter 7.2. Even though you're calculating 4 sprinklers if you meet the conditions, you're going to need to provide a ceiling level density of 0.15 / area for OH1
Reply
sean
4/17/2020 10:16:25 am
No.
Reply
Jesse
4/17/2020 10:11:13 am
Full disclosure though, I don't design a lot of 13D projects though. I do oversee designers that do. We did run into this recently however on a project we took over from a competitor that ceased operations. So maybe someone that does more 13R work will have a different perspective.
Reply
Franck
4/17/2020 11:02:58 am
Protection of the garage makes sense, all the more since you will likely find miscellaneous storage in addition to a car.
Reply
4/17/2020 11:21:21 am
Isn't the concept of 13-D and 13-R to be "life-safety" (evacuation) as opposed to "building fire protection"?
Reply
sean
4/17/2020 11:46:59 am
garages are specifically discussed in NFPA 13R. You need to control fire in most parts of a building to permit egress.
Reply
Jesse Reynoso
9/2/2021 08:00:31 pm
2022 NFPA 13D chapter/section 8.3.4 states sprinklers are not required in garages. Am I missing something
Reply
Angie Kamm
9/28/2023 08:00:39 am
If you look at NFPA 13R (2016) it states a lot of directives to sprinkler garages, this building is per 13R, yes.