Sprinkler Pressure for "ESFR-Ready" Design?

4/1/2021

8 Comments

 
We are currently working on a project with a building height of 36-feet that currently has K16.8 ESFR sprinklers installed to protect open rack storage of Class I-IV commodities at 12-feet in height.

The hydraulic calculations are based on Ordinary Hazard Group 2, with a 0.20 gpm/sqft density over 1,500 sqft with a starting pressure of 7 psi. The design area is based on 18 ESFR sprinklers flowing at 100 sqft per sprinkler. The total sprinkler demand is 834 gpm. 

They are calling this an "ESFR-Ready" sprinkler system.

It seems to me that the building height would drive the starting pressure for this scenario and the calculation should actually be 12 sprinklers with a minimum starting pressure of 52 psi when using K16.8 ESFR sprinklers. This comes after examining Chapters 12-20.

What would the lowest starting pressure be for K16.8 ESFR sprinklers protecting open rack storage of Class I-IV commodities to 12-feet in height with a building height of 36-feet?

​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jesse
4/1/2021 09:14:03 am

Interesting. Flowing 18 K=16.8 - I hope we have a great water supply.

12-25-ft rack storage of Class I-IV Commodity in a 36-ft building would require end head pressure of 52-psi for K=16.8. Figure a loss of psi due to elevation at 15.59-psi = 67.59 psi without factoring in any friction loss.

I wondered about the original OH2 design and figure that the storage was previously less than 12-ft for Class I-III and / or less than 10-ft for Class IV.

"ESFR-Ready" is a new one for me......

Reply
Josh
4/1/2021 09:40:18 am

12.6.7.1 of NFPA 13 2016 says ESFR sprinklers designed to meet any criteria from chapter 12 or chapters 14 through 20 may protect light, ordinary or any storage arrangement referencing OH1, OH2, EH1 or EH2 in chapter 13 (misc/low-piled storage)

So to protect miscellaneous storage with ESFR, you think you'd be able to just pick the least demanding criteria from any of these chapters (while still taking into consideration building height) and that would be good to protect an ordinary hazard group 2 occupancy, but nowhere in any of these chapters would allow you to do a 7 psi starting pressure in a 36' high building with 16.8k ESFR sprinklers that we could find.

Reply
Eric
4/1/2021 09:32:43 am

Your research is correct. Based on NFPA 13 (2016), chapter 16 addresses rack storage of class I-IV commodities. Based on building height and storage height, K16.8 ESFR sprinklers will protect up to 20' of storage in a 40'-0 building, with a starting pressure of 52 PSI. The calculations will be based on 4 sprinklers flowing on 3 branchlines with a hose demand of 250 GPM.

When designing per NFPA, storage height and building height determine starting pressure of the sprinklers. When designing to another standard like FM Global for instance, the building height is the determining factor for starting pressure. In both design scenarios, obviously the commodities being stored is the starting point to the design. In this situation you described, there is no relief for starting pressure at 20' of storage until your ceiling height is 35'-0.

Reply
James Evans
4/1/2021 10:09:23 am

Just a comment on an ESFR-Ready building. These buildings are constructed to provide ESFR systems in the future. Normally they will base the pipe size on future tenants, even if the actual tenant only needs ordinary group 2. THe key is to have the outlets big enough for ESFR sprinklers and the pipe sizing to support it. Normally that means adding a fire pump and changing out the sprinklers.

Normally that would require a 8" riser 6" front main 4" back main and 2 or 2.5" lines.

You might want to make sure that the pipe you are installing will meet those requirements in the future.

Reply
Brian Gerdwagen FPE
4/1/2021 10:10:20 am

We used to design "ESFR Ready" systems. We didn't install ESFR sprinklers as you can not use an ESFR sprinkler and calculate a density/area design with it. The sprinkler isn't designed that way.

The "ESFR Ready" was intended to, at a future date, replace all the K17 CMDA sprinklers with K17 ESFR and drop in a fire pump. Start pressure of 7psi versus 52psi is a big deal.

I wonder if the sprinklers were changed from K8 or K11.2, which would be more appropriate for that arrangement. 800gpm is the minimum discharge for K17 at 7psi, but you are still wasting water if you use a K8 head with a 0.20 density at 100sqft.

If the sprinklers were changed from a CDMA to an ESFR, is the deflector distance correct for ESFR?

Reply
Josh
4/1/2021 10:39:11 am

They are actual 16.8k ESFR sprinklers installed currently. Our thoughts were switching to a CMDA sprinkler such as a K8 or 11.2 and the calculations would probably work for the current storage arrangement and then swap to ESFR later with a fire pump when the storage arrangements exceed it.

This is an existing building that has been passed and approved and we were doing a small tenant revision on it. It just seemed so wrong for the base building contractor to install 16.8k ESFR heads and calc them with a density/area method with a 7 PSI starting pressure.

Reply
matt
4/1/2021 10:12:15 am

one thing to watch out for - depending on your AHJ, the area/density calculation method may not apply to ESFR sprinklers. just because they are discharging .2/1500 does not mean that they are functioning properly. ESFR heads have specific listing requirements and they have probably not been tested or listed for a 7psi starting pressure.

Who has provided the design for this system? Unless they are qualified to produce a new performance based design, you may just have a mash-up of design approaches that don't necessarily work together.

Reply
Franck
4/1/2021 11:24:10 am

ESFR operating at 7 psi would not work correctly.
Because of the large orifice, there is a need for a minimum pressure/flow, otherwise the distribution pattern will be completely eratic, not covering adequately the ground floor area and with droplet sizes not adequately distributed.
Remember ESFR are working on the suppression mode (not control mode) and thus require specific limitation, such as minimum operating pressure, distance from ceiling, no obstruction, specific number of operating sprinklers (usually 12)...
The design with 18 ESFR at 7 psi makes no technical sense and does not seem to appear in any design approach with ESFR (to my knowledge).

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT