Sprinkler or Nozzle in Grease Exhaust Duct?

4/10/2019

13 Comments

 
We have an AHJ that is requiring a sprinkler be located in a grease exhaust duct - but I'm finding it difficult to see where this would be required (reviewed NFPA 96 and 13).

The duct serves a Type I kitchen hood, has an Ansul suppression system, and then has a roughly 45 foot run to exhaust to the outside. We haven't come across a requirement for a duct run like this before, is it required?

Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
13 Comments
Dave L..
4/10/2019 10:24:17 am

At least pre-2019 edition, start at paragraph 7.10 in NFPA #13.

Reply
Franck
4/10/2019 10:35:28 am

On NFPA 13, 2016 Edition, this is § 7.9 Commercial Type cooking equipment and ventilation. Became 8.9 in the 2019 Edition of NFPA 13.

Fire often occurs in grease exhaust ducts, mostly after fires on deep far fryers, extending quickly to the grease deposits inside the ducts. Fire could then spread to adjacent area/floors/levels as ducts are running through walls / ceilings.

Note that sprinkler protection is not required where all cooking equipment is served by listed grease extractors.
Sprinkler might also be omitted in the ducts, depending on their configuration.

An alternative solution could be the provision of a saponification system (wet chemical system - Class K in the US - designed for cooking oil).

Reply
PETE
4/10/2019 11:57:06 am

The Ansul R-102 system is a UL300 listed K-class wet extinguishing system. The duct protection stops with a single nozzle pointing up toward the exhaust. The exhaust is not interlocked because it aids in cooling. The hood return air and cooking power or gas are shut down. For long runs of type 1 hood exhaust, the preferred installation may be Ansul Pihrana which follows with water from above. But, note that IMC dictates duct clean-outs in the design. This is to facilitate periodicly cleaning the grease out of the duct all the way to the roof or exit point. With a Type 1 hood, Ansul R-102 should be able to protect. Check with the authorized Ansul distributor.

Reply
Mike
4/10/2019 11:57:37 am

Good responses above and AHJ has the authority to require anything they want. It's their jurisdiction.

Reply
PEte
4/10/2019 12:04:11 pm

I agree, but horizontal duct for type 1 slopes back to the hood. Flowing water over an existing Ansul installation may result in the Ansul not performing as designed and listed and Ansul not paying a claim if their system fails to extinguish.

Reply
Sue
4/11/2019 01:12:56 pm

I do not agree with the statement that the AHJ can as for anything. I am an AHJ and I must follow the codes. AHJs are not all knowing. I firmly believe that I don't know everything. If a customer has a way that is not typical, why not look at it.

We require a UL 300 listed fixed fire protection system or a fire sprinkler system designed for the type 1 hood. Having said that we also do alternate means and materials evaluations for special applications, which is allowed by code. If we do this we would take proposals from the customer and verify that the solution they are proposing meets or exceeds the intent of the code.

Nhat Nguyen
4/10/2019 08:23:58 pm

Both nozzle and sprinkler are allowed in NFPA 13 (you should see A8.9.2 NFPA13 2019, and that figure existed in previous version). The purpose of sprinkler or nozzle inside duct is for fire cause by grease attached on that, not for fire in equipment. Sorry for my bad English

Reply
Dat Huynh
4/11/2019 08:21:44 am

.... are allowed or are required?

Reply
Nhat Nguyen
4/11/2019 08:17:40 pm

It shall be provided. I mean you can use either sprinkler or nozzle for kitchen. NFPA 13 clearly stated that in 8.9 Commercial-Type Cooking Equipment and Ventilation.

Roger link
12/16/2019 01:43:16 pm

Hi Pete,

we often sell Duct boxes for round and square ducts and exhaust pipes. Including nipples for wet and dry sprinklers with a diameter from 1/2" up to 1" to suppress fire in ducts.

If you want to know more please feel free to contact [email protected]

Reply
Mark Anthony Ver
4/12/2025 04:42:01 am

Providing sprinkler heads inside the kitchen exhaust ductwork is a painful requirement. I can't imagine the penetrations of the sprinkler pipe into the ductwork. This may cause grease leaking to these penetrations and not be known by the engineering staff since it is inside the ceiling. How about maintenance? These heads will be covered by grease at no time. I believe the AHJ (NFPA 1) will accept a reasonable equivalent like an "Ansul" Piranha under the hood and will serve as primary protection for the entire exhaust ductwork.

Reply
Access Doors and Panels link
2/26/2021 03:20:49 am

The facts that have been discussed here are really important. Thank you so much for sharing a great post.


Reply
Best Access Doors link
3/1/2021 06:10:45 am

Excellent explanation. Anyone can easily comprehend since it’s simple & focused. Keep up the great work!


Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT