Sprinkler, Occupancy Group for Fire Pump Room?

5/7/2020

10 Comments

 
Hello Fire Pro People! I am retrofitting an existing stand alone fire pump room.

The existing design had both an electric fire pump and diesel fire pump for back up. We are getting rid of the diesel, and going with just one electric fire pump. The existing building has a sprinkler system, fed from the piping in the Fire Pump room. We would like to get rid of sprinklers. Are they required by code? And can anyone tell me what classification this building is by IBC standards? I read through them all, and I didn't feel that the Fire Pump building fit into any of the categories. Thanks for any love you can send my way!

​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Mike
5/7/2020 07:50:14 am

The fire pump room doesn't generally fall under an Occupancy Classification in the IBC. Requirements for protection are listed in NFPA-20. The required room rating is dependent on whether sprinkler protection is provided or not.

Also, if the fire pump room is located within a building that is required to have sprinkler protection, then all spaces must have sprinklers installed. There is no exemption for fire pump room as there is for electrical rooms.

Reply
Jonathan Sullivan
5/7/2020 10:16:08 am

Without knowing your building size, construction type, distance to lot line or adjacent buildings, or opening size it's hard to say about the sprinklers. Buildings where IBC is enforced require an occupancy classification, I can't think of an exception to this.
Typically we see U or F-1 for pump houses and similar buildings depending on the jurisdiction. Side note, if you are heating the enclosure and IBC applies, you need to comply with the energy code including the thermal provisions of the envelope, no exception.

Reply
Franck
5/7/2020 10:41:33 am

It is a good practice to protect the diesel fire pump room (recommended density is .25 gpm/sq ft over the entire room), preferably with high temperature sprinklers (286°F).
In case of fire in the pump room (it happens with diesel engines), the sprinkler protection will limit the fire spread and will reduce the time out of service for the pump (reliability).
It is largely accepted that electric fire pumps are only equipped with smoke detection when there is no additional hazard/exposure (detached building, for example).
But this point of view is mainly an insurance industry consideration (property damage).
If the room houses both types (diesel and electric), then a sprinkler protection for the entire room is normally advised.

Reply
sean
5/7/2020 11:04:38 am

this is a question for a design professional (licensed architect or engineer).

There are many factors in the IBC that dictate sprinkler design. To many to run though everything.

If I was the building official i would need to confirm that the building design does not use any of the sprinklered options.

Reply
Julianne Heredia
5/7/2020 11:25:32 am

Take a look at NFPA 20:Table 4.12.1.1.2 Equipment Protection.
These are the essential guidelines for protection of any fire pump room.

Reply
Nimal Tissa Wijetunga
5/7/2020 11:29:39 am

As per NFPA 20,

1) Electric driven fire pump only - the pump room shall be considered as OH1 for Sprinler Design.

2) If the diesel engine driven fire pump is also included - the pump room shall be considered as Extra Hazard 2 for Sprinkler design.

Reply
Ivonn Ochoa
5/7/2020 12:56:58 pm

Agree with Nimal,

You can check this on sections 4.13.1.3 and 4.13.1.4 of NFPA 20 Ed.2016


Or sections 4.14.1.3 & 4.14.1.4 Ed.2019

Reply
Mahmud link
2/23/2021 11:30:58 am

Hello
I am Mahmud from Bangladesh. In our country the readymade garment factories (F1) are audited by international organizations. They said that, every fire pump rooms shall be provided with sprinklers either it is located in the factory building or outside of the building.

Though fire pump rooms are separated by 2-hr fire rated construction, nonetheless the auditors stated that,

"Automatic sprinkler protection was not provided for the fire pump building /room with diesel engine pump driver(s) and day tank(s). Provide automatic sprinkler protection for the fire pump building / room installed in accordance with NFPA 13 as an Extra Hazard Group 2 occupancy."

We asked them that, our fire pump rooms are separated by 2-hr fire rated construction and located in the main building or outside the building. So why we need to provide sprinkler in every pump room?

The auditor clarified that" as per NFPA 20 it is a mandatory rule to provide sprinkler in fire pump room though they are separated"

So my question is the above clarification is correct or not?

Note: Few buildings are provided with sprinkler system and few are provided with class III standpipe system.

Reply
FAIYAZ AHMAD
6/22/2023 02:59:49 am

Dear Mr. MAHMUD,

As per NFPA 20, Table 4.12.1.1.2, this is not mandatory to install sprinkler system in fire pump room however, if installed the fire rated enclosure construction time shall be reduced from 2 hour to 1 hour.

This depends clients to clients that who want to install sprinkler system in fire pump room or not?

Reply
Anas
11/2/2023 05:02:59 am

Which type of sprinkler used in fire pump room

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT