MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Sprinkler Line Through Elevator Machine Room?

7/9/2019

9 Comments

 
Are you allowed to run a branch line through an elevator machine room? ASME 17.1 Section 2.8.2.3 clearly states that you can. Section 2.8.2.3.1 disallows only risers and returns. Am I missing something? 

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Mike
7/9/2019 10:13:02 am

I don't have the text you refer to but in my experience you cannot run through it - i.e. enter and exit. Can only extend the fire sprinkler line into it.

Reply
Wayne Ammons
7/9/2019 11:06:14 am

I can't find anything that says you cannot run sprinkler piping through an elevator machine room. I do know that you CAN run sprinkler piping through an electrical room as long as you do not enter the dedicated electrical space or the working space of the electrical equipment. NFPA 13 added text and annex material to clarify this in the 2019 edition (section 9.2.6). Hopefully, someone familiar with ASME 17.1 can give some additional input.

Reply
Dan Wilder
7/9/2019 12:01:16 pm

ASME A17.1 Rules 2.8.3.3, 2.8.3.4, 2.8.3.5 (check your local adoptions and modifications)

-Sprinkler protection shall supply only branch lines into the machine/control room or control space
-Pipes or ducts conveying gases, vapors, or liquids that do not pertain to the elevator are prohibited
-Pipes (i.e. sprinkler) or similar equipment that contains liquid shall not be located directly above elevator or electrical equipment. Pipes shall not encroach upon any required clearances

Reply
Wayne Ammons
7/9/2019 12:33:11 pm

Dan, is there any annex material for the first rule "...shall supply only branch lines into..."? Does the word "into" imply that the branch line cannot pass through the room?

Reply
Dan Wilder
7/9/2019 06:01:17 pm

I only have some handouts that an elevator sub gave to me a while back. I don't own a full book so I can't speak to what they define as a Branch Line.

Mitchell O'Bryant
7/11/2019 10:54:07 am

Text from ASME A17.1 (2010)
2.8.3.1.2 - All risers and return pipes shall be located outside the hoistway. When the machinery space, machine room, control space, or control room is located above the roof of the building, heating pipes for the machinery space, machine room, control space, or control room shall be permitted to be located in the hoistway between the top floor and the machinery space, machine room, control space, or control room.

2.8.3.3 - Sprinkler systems conforming to NFPA 13 or the NBCC, shall be installed in the hoistway, machinery space, machine room, control space, or control roof subject to 2.8.3.3.1 through 2.8.3.3.4.

2.8.3.3.1 - All risers shall be located outside these spaces. Branch lines in the hoistway shall supply sprinklers at not more than one floor level. When the machinery spaces, machine room, control space, or control room is located above the roof of the building, risers and branch lines for these sprinklers shall be permitted to be located in the hoistway between the top floor and the machinery space, machine room, control space, or control room.

2.8.3.4 - Other pipes or ducts conveying gases, vapors, or liquid and not used in connection with the operation of the elevator shall not be installed in any hoistway, machinery space, machine room, control space, or control room. (It goes on to talk about above roof line spaces).

My take - I don't have a section 2.8.2.3 that you reference (likely different versions), but if the branch line is serving another space and simply routed through the machine room for convenience, I do not believe this is permitted.

Reply
Steven Lopez link
7/15/2019 03:48:21 pm

Upon further review I contacted our local state inspection office and asked for their interpretation of the code (I'm in California). They referenced Title 8 Industrial Relations code section 3012 (b); link here: - https://www.dir.ca.gov/Title8/3012.html
It reads very similarly to ASME A17.1 which can be found online here: https://ia800302.us.archive.org/26/items/gov.law.asme.a17.1.2004/asme.a17.1.2004.pdf

Ultimately they agreed that their was no where in the code that explicitly did not allow sprinkler pipe to pass through the machine room. However they informed me that the majority of all inspectors would flag it regardless and not allow it; as this has been common practice since the 80's.

Reply
Sarah Maman P.E.
7/14/2020 07:49:11 pm

A client of mine (sprinkler contractor) was having an disagreement with the elevator AHJ about running sprinkler piping through an elevator machine room. I did a web search and came across your discussion on the matter. I agree that there is nothing in ASME 17.1 that would not permit sprinkler piping in an elevator machine room. Here is the entire text of this section of ASME 17.1-2007.

SECTION 2.8
EQUIPMENT IN HOISTWAYS, MACHINERY SPACES,
MACHINE ROOMS, CONTROL SPACES, AND
CONTROL ROOMS
2.8.1 Equipment Allowed
Only machinery and equipment used directly in connection
with the elevator shall be permitted in elevator
hoistways, machinery spaces, machine rooms, control
spaces, and control rooms.
2.8.2 Electrical Equipment and Wiring
2.8.2.1 Installation of electrical equipment and
wiring shall conform to NFPA 70 or CSA-C22.1, whichever
is applicable (see Part 9).
2.8.2.2 Only such electrical wiring, raceways,
cables, coaxial wiring, and antennas used directly in
connection with the elevator, including wiring for signals,
for communication with the car, for lighting, heating,
air conditioning, and ventilating the car, for fire
detecting systems, for pit sump pumps, and for heating
and lighting the hoistway and/or the machinery space,
machine room, control space, or control room shall be
permitted to be installed inside the hoistway, machinery
space, machine room, control space, or control room.
2.8.2.3 Bonding conductors from the lightning protection
system grounding down conductor to long vertical
metal bodies in the hoistway such as elevator rails
and vertical wireways shall be permitted to be installed
in the hoistway as required by NFPA 780, or
CAN/CSA-B72, whichever is applicable (see Part 9). The
lightning protection system grounding down conductor
shall not be permitted in the hoistway, and the elevator
rails shall not be used as the lightning protection system
grounding down conductor. Bonding conductors
installed in the hoistway shall not interfere with the
operation of the elevator.
2.8.3 Pipes, Ducts, Tanks, and Sprinklers
2.8.3.1 Steam and hot-water pipes shall be permitted
to be installed in hoistways, machinery spaces,
machine rooms, control spaces, and control rooms for the
purpose of heating these areas only, subject to 2.8.3.1.1
through 2.8.3.1.3.
2.8.3.1.1 Heating pipes shall convey only
low-pressure steam [100 kPa (15 psi) or less] or hotwater
[100°C (212°F) or less].
2.8.3.1.2 All risers and return pipes shall be
located outside the hoistway. When the machinery
space, machine room, control space, or control room is
located above the roof of the building, heating pipes for
the machinery space, machine room, control space, or
control room shall be permitted to be located in the
hoistway between the top floor and the machinery space,
machine room, control space, or control room.
2.8.3.1.3 Traps and shutoff valves shall be provided
in accessible locations outside the hoistway.
2.8.3.2 Ducts shall be permitted to be installed in
the hoistway, machinery space, machine room, control
space, or control room for the purpose of heating, cooling,
ventilating, and venting these areas only and shall
not encroach upon the required clearances.
2.8.3.3 Sprinkler systems conforming to NFPA 13
or the NBCC, whichever is applicable (see Part 9), shall
be permitted to be installed in the hoistway, machinery
space, machine room, control space, or control room
subject to 2.8.3.3.1 through 2.8.3.3.4.
2.8.3.3.1 All risers and returns shall be located
outside these spaces. Branch lines in the hoistway shall
supply sprinklers at not more than one floor level. When
the machinery space, machine room, control space, or
control room is located above the roof of the building,
risers, return pipes, and branch lines for these sprinklers
the top floor and the machinery space, machine room,
control space, or control room.
2.8.3.3.2 In jurisdictions not enforcing the
NBCC, where elevator equipment is located or its enclosure
is configured such that application of water from
sprinklers could cause unsafe elevator operation, means
shall be provided to automatically disconnect the main
line power supply to the affected elevator and any other
power supplies used to move the elevator upon or prior
to the application of water.
(a) This means shall be independent of the elevator
control and shall not be self-resetting.
(b) Heat detectors and sprinkler flow switches used to
initiate main line elevator power shutdown shall comply
with the requirements of NFPA 72.
(c) The activation of sprinklers outside of such locations
shall not disconnect the main line elevator power
supply. See also 2.27.3.3.6.
2.8.3.3.3 Smoke detectors shall not be used to
activate sprinklers in these spaces or to disconnect the
main line power supply.
2.8.3.3.4 In jurisdictions not enforcing the
NBCC, when sprinklers are installed not more than
600 mm (24 in.) above the pit floor, 2.8.3.3.4(a) and (b)
apply to elevator electrical equipment and wiring in

Reply
Jonathan Sullivan
8/4/2020 12:36:09 pm

Sarah - what was the result of your conversation?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT