Sprinkler Required Within Each Toilet Stall?

2/28/2024

12 Comments

 
We have a project with non-gender specific toilet stalls/water closets.

I am of the opinion that NFPA 13 does provide an exception for having to install sprinklers within each water closet. However, this project is has the water closets in restrooms which are not within a dwelling unit, so no relaxation is given in NFPA 13 for dwelling unit bathrooms.
Picture
As I understand NFPA 13, a sprinkler would be required within each of these water closets. Do I believe it’s overkill? Yes, but until it is addressed in NFPA 13, there wouldn’t be much to do about it.

What is your opinion?

​Non-gender specific toilet facilities are becoming increasingly common, see a conceptual layout below.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Dan Wilder
2/28/2024 06:26:24 am

We have to do this for about every resort, spa, or convention center (at times) as they always have the individual, walled toilet areas.

While omitting the installation of sprinklers isn't an option, you can use NFPA 13 to remove the sprinklers from the calculated area. It does require a non-reduced remote area, but it can help greatly during hydraulic calculations.

16'-23.4.4.7.2
19'-27.2.4.7.2

And yes, I have also seen properties use a room or two as a storage room at times.

https://www.sprinklerage.com/omitting-flow-sprinklers-design-area/

Reply
Daniel LeFave
2/28/2024 08:16:53 am

Dan, Came here to say this. Your best best would be to take the full remote area square footage and exclude the sprinklers from the calculations per the code reference above!

Reply
Pete H
2/28/2024 06:53:33 am

It's a common bathroom, if the walls go all the way up and compartmentalize each toilet room, then you need a sprinkler head in each one.

-

Fun side fact, in 2013 (they fixed it in 2016 and this wasn't in 2010 to my knowledge) the ability to omit the sprinklers from calculations if you did not use a reduced remote area didn't have the 55 square foot small compartment and was just written as "23.4.4.6.2 Where the design area is equal to or greater than the area in table 23.4.4.6.2 for the hazard being protected by the sprinkler system, the discharge for sprinklers protecting small rooms such as closets, washrooms, and similar small compartments that are in the design area shall be permitted to be omitted from the hydraulic calculations."

So with only the guidance of "small room" and no 55 square foot limitation you could have a 799 square foot bathroom in your 1500 square foot design area and omit it.... granted by the time most jurisdictions adopted 2013, 2016 edition was already written and available for viewing, so if you did this you should also have had complete knowledge you were using the letter of the law to fly in the face of the spirit of the law.

Which I imagine is why they fixed that in 2016 edition.

Reply
Josh
2/28/2024 08:04:36 am

I interpret NFPA 13 exceptions to solely be for a dwelling unit. If I have a commercial gig, it install.

Reply
Glenn Berger
2/28/2024 08:08:15 am

If the walls goes within the specified distance of the ceiling then sprinklering each enclosure is required.

Reply
Ricardo Gonzales Jr link
2/28/2024 08:44:15 am

The 1st item is to determine how high the stall walls go up towards the ceiling. If the clearance is there, no you don't. But if the clearance isn't there, then yes. That is allowed in NFPA 13. No different than bookshelves (if the architect provides the furniture layout and elevations).

The same goes for Fire Alarm Visual.

Reply
Jack G
2/28/2024 09:02:58 am

Rule only applies to bathrooms in a residential occupancy ( in this case )
It does not apply to limited care facilities or bathrooms that open up to public areas.
This area if a small room rule can be applied, could use area reduction method ( looks like 21 sprinklers are required for the room- 800 sf or less)
This looks like your “ hydraulic remote area” !

Reply
Dert
2/28/2024 10:04:16 am

Use a K2.8 head to reduce hydraulic demand.

Reply
Andrew
2/28/2024 07:43:26 pm

Not always a realistic option, but if a lower open cell ceiling could be installed that would mitigate the multiple heads.

Reply
Dave
2/29/2024 10:43:39 am

I got an architect lower the partitions ONCE, and the contractor was able to use the "partition rule" and cover two stalls with one sprinkler, but every other time it's been one sprinkler per stall. Often suggesting smaller K as suggested above. If it's a school, I often spec less-noticeable concealed sprinklers.

Reply
Jesse
2/29/2024 08:40:50 am

If its a full 13 design, there are no two ways about it. You need to protect each individual stall.

Reply
Tom
7/17/2025 08:58:14 am

What if this was an NFPA-13R installation? My understanding is that the individual stalls would not need to be protected.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT