Distilled alcohol storage on single/double row racks. I feel like I am loosing my mind in a big way.
I currently have a larger liquor store that I am trying to design that will have a stock room which will utilize 10-ft tall single and double row racks. These racks can contain alcoholic beverages that exceed 20% (Everclear). What standard/section does this fall under? So far I've only found sections that exclude this kind of commodity. I am sure I'm missing something stupid simple on this one. Thanks ahead for the help. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Dan Wilder
9/17/2021 07:12:12 am
NFPA 30 - Class III Liquids (typically), water miscible, cartoned, stored in non-metallic containers and typically less than 1 gallon
Reply
Alex
9/17/2021 07:47:11 am
Hi Anonymous,
Reply
Brian Cockburn
9/17/2021 08:14:20 am
I agree with Alex that Table A.5.6.3 in NFPA 13 would be the place to start. This would fall under Table 13.2.1 in Chapter 13 - Miscellaneous Storage.
Reply
9/17/2021 08:22:42 am
Everclear is 95% alcohol and is a class IB Flammable liquid.
Reply
Anthony Crispo
9/17/2021 08:29:08 am
http://www.klausbruckner.com/blog/distillery-storage-dilemmas/
Reply
Franck
9/17/2021 08:35:36 am
I usedd to be a loss prevention engineer (Insurance side) for Seagrams quite a long time ago.
Reply
Jesse
9/17/2021 08:38:13 am
2018 NFPA 30 Table 10.7.1 directs us back to NFPA 13 with protecting this as OH 2 presuming that we don't exceed the MAQ and storage height limitations.
Reply
Anthony C Brown
9/17/2021 08:45:19 am
I have designed several Liquor Stores some of which have had large on-site product storage. The storage racks were 10' 0r less and where back-to-back and I successfully obtained Sprinkler Permits designing with Ord. Haz., Gp II
Reply
JD
9/17/2021 09:58:11 am
Great info!
Reply
Moderator (Joe)
9/17/2021 10:45:28 am
LOL. It's 100% you all who make it a helpful destination.
Reply
Joshua Freedman
9/17/2021 10:34:25 am
Yeah, it was pretty well answered above. NFPA 13 and 30 do not cover it, I have spoken with NFPA engineering about it and they said they will be covering liquor in future editions of NFPA 30. I have used FM 7-29 - Ignitable Liquid Storage in Portable Containers to assess locations before. And just FYI, a lot of the big insurance companies will write to FM standards when it comes to the higher hazard stuff.
Reply
Connor
9/17/2021 11:15:22 am
Just to add my experience on to all the contributions above:
Reply
Todd E Wyatt
9/20/2021 04:36:14 pm
The IBC and IFC determine the Maximum Allowable Quantities (MAQ) for assigning the appropriate Occupancy Classifications (OC) for buildings containing "Hazardous Materials Posing A Physical Hazard." These Codes provide prescriptive requirements for determining the OC (e.g. Mercantile vs S-1 Moderate-hazard Storage vs Group H High Hazard) based on the MAQs and if the story(s) are divided into Control Areas (CA) protected by fire-resistive rated (FRR) assemblies per IBC Table 414.2.2 Design and Number of Control Areas. Lastly, how the "hazardous materials" are to be stored (e.g. high-piled stock or rack storage?) will affect the design of the automatic sprinkler sysytem.
Reply
Any addition of NFPA 13 Appendix A will only focus on alcohol <20% in various containers.