|
In NFPA 13R, sprinklers may be omitted from bathrooms and closets provided they meet the area and size requirements, and are constructed with limited or non-combustible materials (gypsum/drywall).
Should sprinklers be installed in bathrooms and closets on the top floor regardless of area/size and construction to prevent a fire on the top floor from getting into the ceiling space and spreading? I have seen other designers do this but I can't find any formal requirements for this approach. Has anyone else ever done this? Would it matter if the ceiling and roof assembly were fire rated? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
19 Comments
Fred
8/4/2021 06:19:50 am
No there is no requirements that I am aware of in 13R that would require that on top floor. 13R systems are designed for life safety not for the building. This is why we have seen R-2 occupied buildings burn to the ground due to no protection in combustible voids and attics.
Reply
Rob
8/4/2021 08:48:18 am
This is exactly why many jurisdictions are no longer recognizing 13R.
Reply
Pete
8/4/2021 06:43:22 am
Nothing I know of in 13R, possibly an insurance requirement in the jobs the other designers have.
Reply
Dan Wilder
8/4/2021 08:11:27 am
Not required and no in my opinion. There are several other areas (combustible concealed spaces that are open to the attic like plumbing shafts, wall cavities, exterior concealed areas below projections) that I would prefer to have some protection within before I start dropping sprinklers into a gyp board enclosed space for the top floor.
Reply
Brian Willis Spurrell
8/4/2021 08:18:09 am
Here in Canada all top floor rooms wash rooms closets ect. need to be sprinklered. A national building code requirement not NFPA.
Reply
MattC
8/4/2021 09:43:24 am
Note that not all provinces follow the National Model...
Reply
Brian Cockburn
8/6/2021 03:52:55 pm
Look at Section 3.2.5.13 (6) in the Ontario building code. It appears to require sprinklers on the top floor unless the roof is a rated assembly. 8/6/2021 02:15:32 pm
The same requirement is in the BC Building Code.
Reply
Todd Wyatt
8/4/2021 08:34:25 am
The adopted building Code (e.g. 2021 IBC) is the scoping Code which identifies where (and where not) automatic sprinkler systems (ASPS) are required (or not). The NFPA 13 is the reference standard identifying how an ASPS is installed and maintained but should not be used as a scoping document.
Reply
Chad
8/4/2021 02:27:53 pm
The original question was not IF a system in a specific building was required but WHERE coverage is required. I realize this assumption may require a small leap of faith but it appeared his question presupposed a system is required or at least is being provided or is already installed.
Reply
Todd Wyatt
8/5/2021 09:22:46 am
Unless a jurisdiction has formally adopted the NFPA 13 (and not as a reference standar), the adopted building Code determines the scoping requirements (e.g. locations) for automatic sprinkler system protection.
Reply
Chad
8/6/2021 10:54:56 am
I do not understand how a standard adopted by reference would not co-occur as the "scoping" document.
Alex
8/4/2021 09:21:10 am
Hi Anonymous,
Reply
John
8/4/2021 10:45:39 am
It s always a good idea to protect all areas on a top floor with an unprotected attic, albeit not required.
Reply
Jesse
8/4/2021 11:08:51 am
If its a 13R project, there is no requirement for protecting closets and restrooms on the top floor.
Reply
Adam
8/4/2021 11:19:03 am
In Ontario Canada, we are governed by the Ontario Building Code. Depending on building construction and size, the roof structure may or may not require a fire resistance rating, and buildings may or may not require sprinkler protection. If the roof does require a fire resistance rating, and the building is protected by a sprinkler system, then all ceiling spaces on the top floor require sprinklers, even if 13R provides an exception.
Reply
Chad
8/4/2021 02:37:12 pm
Adam,
Reply
Matt Cornell
8/4/2021 11:32:37 am
You really stepped in to a hot topic! 13R is intended for Life Safety. Fire Departments forget this and wonder why the building burned to the ground. Local Fire Marshals try to fix this by adding amendments. Don't get yourself in trouble by trying to protect the structure with a 13R system. If the goal is to protect the structure design a 13 system.
Reply
8/6/2021 02:11:46 pm
There's a good playlist on YouTube called "NFPA 13R Problems" that shows one low rise building after another burning down from attic fires.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
September 2026
PE PREP SERIES |
RSS Feed
