Split-Case Fire Pump with Suction Under -1.5 psi?

10/23/2020

8 Comments

 
Can a split-case fire pump be used with a suction that is below negative 1.5 psi of pressure (below 1.0m)?

Would this be acceptable under NFPA 20?

Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Michael Fertal
10/23/2020 10:06:15 am

Can you provide additional info on the conditions? Is the supply city-fed or a water tank. Is the basis of the question from a design or NFPA 25 inspection?

Reply
Cameron Spence
10/23/2020 10:06:51 am

NFPA 20 permits up to -3 psi at the pump suction flange when pulling water from a storage tank that has its outlet at or above the pump suction elevation. Other than that, I believe 0 psi or greater is required at the suction flange when pulling from a water supply.

Are you getting the -1.5 psi at the system demand or at 150% of pump capacity?

Reply
Glenn Berger
10/23/2020 10:25:32 am

Simple answer - Do not use a split case fire pump in that application. NFPA may permit it - but the mfg or the water supplier may not.

Reply
Franck
10/23/2020 11:20:53 am

It depends on many conditions and if the AHJ allows you to do so.

If you have -1.5 psi at 150% because of friction losses in the suction pipe, this is related to NPSH and probably a too long suction piping that is not desirable.

If it is because you are taking suction under lift with an horizontal split case pump (your water level is below your pump level), it is normally not approved by NFPA as you should use a vertical pump in that case (NFPA allows the use of horizontal split case pump under head).

In Europe, we often have horizontal fire pumps under lift. And it was possible in older versions of NFPA 20 (prior to 1974).

In that case, we use a priming tank.

But remember this is not anymore in line with NFPA... NFPA 20 does not allow horizontal fire pumps taking suction under lift since its 1974 Edition, after several foot valve failures that caused the loss of the priming water destroyed the pumps running them dry. ...

But the following arrangement (if approved by AHJ) may prevent you to have problems with your current installation...

The maximum depth from which the pump would suck should not exceed 10 ft 6 in.
In practice, the pump should be installed at the nearest position to the suction location. When sucking from deeper points, separate suction lines should be arranged for each pump instead of a single collector in multi-pump systems.

The suction pipe should be immersed in water with an elbow, and a filter flap (or foot valve) should be installed to the suction pipe end side to keep water between the water level in the tank/pond/river and the pump casing.
There is no need to install a shut-off valve onto the suction line. The filter at the suction flap end should be occasionally cleaned up and prevented to be clogged with dirt and foreign substances.

A priming tank should be installed to fill the volume between the backflow preventer and the foot valve (upstream and downstream).
• The bottom of the priming tank should be at least 5 ft above the top of the pump
• Automatically filled tank only are accepted: volume at least 130 gal. or 3 times the volume of the suction pipe + pump casing, whichever is the greater
• The priming tank should be connected to the pump discharge upstream of the check-valve, with minimum 2 in. diameter pipe
• The priming connection should be fitted with a gate valve and a check-valve, as close as possible to the pump
• The priming tank should be fitted with a low level gauge, set at 2/3 of tank volume, to automatically start the pump on a low level condition, and allowing tank refill through a calibrated orifice

Reply
SK
10/23/2020 01:56:19 pm

If you are taking the suction from storage tank, then it's allowed as per NFPA 20. Section 4.15.3.2 otherwise not less than o psi. This means NPSHa can be lower when using tank.

NFPA 20, A.4.15.3.2. It is permitted that the suction pressure drop to –3 psi (–0.2 bar) for a centrifugal pump that is taking suction from a grade level storage tank where the pump suction elevation is at or below the water level in the water storage tank at the end of the required water flow duration. This negative suction pressure is to allow for the friction loss in the suction piping when the pump is operating at 150 percent capacity.

Reply
Eissa link
12/21/2024 01:25:03 pm

In any edition this provision is mentioned, Sir?

Reply
koray uluç link
10/25/2020 11:34:22 am

NFPA20 permits 0,2bar negative pressure at %150 flow when pump room floor and atmospheric water storage tank bottom is at same level.
This means that any NFPA20 fire pump must have NPSH required value at %150 flow lesser than 0,8 bar approximately.
Pump manufacturers should achieve this performance to be listed.
if your pump require less NPSH (Net positive suction head) than it can still supply enough pressure at %150 flow according to its curve even your suction line is not applicable according to NFPA20.
Keep in mind that generally low rpm pumps require less NPSHr

Reply
SHOAIB
10/31/2020 05:52:54 am

"This means that any NFPA20 fire pump must have NPSH required value at %150 flow lesser than 0,8 bar approximately."

Sir, Do you have any reference for this sentence?
If yes, would you please provide this reference number?
I need to know this.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT