For exposed copper piping in Ordinary Hazard occupancies, can the joints be soldered (sweat) together or must they be brazed?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
1/18/2023 06:40:00 am
They must be brazed as they are exposed.
Reply
Alex
1/18/2023 01:47:16 pm
Nailed it! I wasn't sure of the answer here either, appreciate the in-depth response Dan.
Reply
Anthony
1/18/2023 08:21:05 am
Just curious where you're using this? I'm imagining sensing lines for a pump or line piping for an MRI room?
Reply
Jesse
1/18/2023 09:20:06 am
Gotta be brazed
Reply
David Kendrick
1/18/2023 10:47:05 am
Viega ProPress fittings are UL listed for fire protection use including dry pipe systems.
Reply
Kris Humbrecht
1/8/2025 03:33:00 pm
Jumping into this older post because this came up for us recently - Propress for copper and stainless is no longer listed/approved for fire sprinkler, and their product data was updated to reflect this.
Reply