MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Solar Panels Require Sprinkler Protection?

5/20/2022

21 Comments

 
Do solar panels on a roof level of a parking garage require sprinkler protection?

The parking garage is six-level open air garage, and the roof level (the sixth level) is used for parking. Solar panels would cover 30% of the roof level and may potentially in future cover the entire roof.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
21 Comments
Pete H
5/20/2022 06:47:45 am

As in solar panels on top of the roof?

I don't see how you could protect them with sprinklers. There's no ceiling above them to collect heat and set off the sprinkler.

I don't think these can require protection unless there is some form of structure above them.

Reply
SCHULMAN
5/20/2022 08:23:04 am

i don't know of any code but these could have used some...

https://www.thesolarnerd.com/blog/can-solar-panels-cause-fires/

Reply
Dan Wilder
5/20/2022 08:29:05 am

We have been required to install them on the structural framing below the panels for one project and argued our way out of it on a couple others due to lack of structure and some creative help wordsmithing from the arch based on spacing and angle of the panels.

Are they setup as single rows all at the same angle, individual panels at an angle, or just flat? That help with our argument based on deflector spacing and heat collection.

Reply
XIAO LI
5/24/2022 09:16:54 pm

Thanks for you answer. The PV panels are flat and with tiny gaps between modules. The slope is about 5%. The PV panels are installed on steel canopy structure looking like a roof a few meters above the roof.
The sprinkler designer augured the heat collection as well, but I think smoke could accumulate beneath the panels due to delay in smoke travel.
The panels looks like a large canopy though without a soffit.

Reply
Roy J.
5/20/2022 08:29:33 am

Are you looking at it as a concealed combustible space under the solar panels? It is an interesting question, there is no definition of concealed space in NFPA 13, but I don't believe it would not apply here, but as always the AHJ is the final authority. If it was decided it is a concealed combustible space there are some options to work through it without coverage, see 8.15.1.2.7.1 and 8.15.1.2.6 and most likely more...…remember my opinion is worth what you paid for it :)

Reply
XIAO LI
5/24/2022 09:19:08 pm

I could not relate to the space beneath the panels as concealed space. The panels are a few meter above the roof parking, acting like a roof canopy.

Reply
Glenn Berger
5/20/2022 08:30:58 am

The recently published NFPA 88A requires open parking garages to be provide with sprinkler protection.

As far as installing sprinkler below the solar panels, you just need to ensure the framing assembly that supports the solar panels is designed to allow the installation of the sprinklers.

Reply
Franck
5/20/2022 08:55:24 am

Even though solar panels represent a potential fire exposure to your roof assembly, there is no requirement to provide sprinkler protection.
One of the main issue is that you won’t be able to disconnect the production of electricity (even at night, as they can continue to operate with lighting from the outside) and therefore create a real problem for firefighters.
In some countries, fire fighters will just let the building burn if solar panels are installed so as not to unnecessarily expose them.

To come back to the fire hazard, if all panels could take fire (poor maintenance, damaged panels by hail, loose electrical connections…), they won’t all have the same consequences depending on your roof assembly (if on concrete roof, no issue, if on combustible roof assembly, big issue) and the way they are installed (detached from the roof with a given angle, lesser problem, buit-in the roof assembly, bigger problem)

Reply
Todd Wyatt
5/20/2022 09:20:46 am

The adopted building Code (e.g. 2021 IBC) is the scoping document that determines what Occupancy Classifications (e.g. Group S-2 Low-Hazard Storage) require an automatic sprinkler system. The referenced standards regarding spinklers per IBC Ch 35 (e.g. NFPA 13/13D/13R/16) are only applicable per the "prescribed extent of each such reference" as listed in the adopted building Code (IBC).

IBC Ch 4 includes prescriptive information to determine if a parking garage (PG) is "open" or "enclosed." This chapter includes scoping requirements such as "402.5 Automatic sprinkler system, Exception" which states that an "automatic sprinkler system shall not be required in ... open parking spaces separated from the covered or open mall building ..." Ch 4 also includes an exception that some PGs are not to be considered a "high-rise building" and that some PGs are not to be considered an "underground building." Section 406 Motor-Vehicle-Related Occupancies specifically addresses PGs and provides "Height in Tier" limitations for PGs that include an automatic sprinkler system or not. The Design Professional should determine if an automatic sprinkler system is required to meet these "allowables".

"406.6.3 Automatic sprinkler system" requires an automatic sprinkler system for an "enclosed parking garage" in accordance with 903.2.10.

"Ch 9 Fire Protection and Life Safety Systems" includes several exceptions to providing an automatic sprinkler system for "open parking garages" (903.2.1.6, 903.2.2, 903.2.6) depending on the adjacent Occupancy Classification(s).

"903.2.10 S-2 Parking Garages" provides (3) prescriptive requirements where auatomatic sprinklers systems are required for parking garages :

1) Where the fire area of the enclosed parking garage in accordance with Section 406.6 exceeds 12,000 square feet (1115 m2).

2) Where the enclosed parking garage in accordance with Section 406.6 is located beneath other groups.

Exception: Enclosed parking garages located beneath Group R-3 occupancies.

3) Where the fire area of the open parking garage in accordance with Section 406.5 exceeds 48,000 square feet (4460 m2).

This section also addresses Commercial Parking Garages (903.2.10.1) & Mechanical-Access Enclosed Parking Garages (903.2.10.2).

Once you determine IF the scoping Code (IBC) requires an automatic sprinkler system or not, then you review the referenced standards (NFPA 13) as to how the automatic sprinkler system is to be designed.

Reply
Franck
5/22/2022 10:47:43 am

I think that the question is not to protect the garage, but the solar panels on the roof of this garage

Reply
Todd E Wyatt
5/23/2022 08:34:04 am

The scoping Codes do not include specific components of a building (e.g. "solar panels") that require protection by an automatic sprinkler system in a building not required to be sprinklered. Sprinkler protection is per Occupancy Classification. The question refers to a "roof level" and not to an unoccupied roof so it is unclear. Parking garages are regulated by the number of "tiers" and not by "stories". If a parking garage is not required to have an automatic sprinkler system and the roof "tier" includes "solar collectors", it would not be required by the structure's Occupancy Classification to protect the rooftop solar collectors with an automatic sprinkler system.

Eric R
5/20/2022 09:26:57 am

This topic is definitely something that will need to be worked on at the model code level. I've been involved with two commercial rooftop solar fires where the fire was hot enough to punch down through the roof membrane and ignite the insulation on the interior side. Both of these buildings had sprinklers inside, so fire damage was limited on the interior, but even for the sprinklers it was a bit of the challenge as they aren't normally required to spray above themselves!

I wouldn't be surprised if fire rated horizontal assemblies become required below fixed roof solar installations someday with all the appropriate penetration detailing, etc.

Reply
Andrew Thul
3/11/2024 09:10:16 am

California has developed code language for this in Chapter 9 of the CBC (speinklering under PV arrays)

Reply
Sanjeev Gupta
5/20/2022 09:31:04 am

Garage and parking area will require sprinkler protection due to associated fire hazard. But not required for solar panel as we donot see any thing fire hazard to burn there on panel.

Reply
Franck
5/22/2022 10:50:14 am

There has unfortunately been a number of fires with solar panels on roofs. They definitely do present a fire hazard by themselves. And a fire exposure if the fire can then spread to the roof itself.


Reply
Jack G
5/20/2022 07:03:37 pm

I recall a rooftop fire, years ago, NJ, Morestown, where firemen couldn’t get on the roof—- electricity from sun, water, humans.
I considered, back then, a high pressure ss system, with 600 psi tube, Bette fog nozzles, or mist nozzles under the panels, every 8 feet, dry, triggered by the fire alarm. Should do the job. That should also knock down any fire up there.

Reply
sean
5/20/2022 07:40:15 pm

no

Reply
Franck
5/22/2022 10:51:19 am

That’s a good summary
;)

Reply
Alex
5/24/2022 06:08:55 am

Hi,

I'm late to the game here - I was out of the office with no access to a computer

As far as the code goes, I believe others have stated that there aren't any true design guidelines out there. In a year or so, I'm sure we will see a change in the code.

Thanks

Reply
XIAO LI
5/24/2022 09:35:21 pm

Hi All, thanks for the replies. It is a surprise there are so many great comments. Some additional information about the building. The parking garage is located in Canada. It is a six-tier/level open-air parking garage proposed to be mass timber CLT floors with concrete topping. Columns and beams are mass timber as well. The building is proposed to be fully sprinklered. However, the code does not require a concrete building of the same size to be sprinklered. Sprinkler protection is a mitigation measure in order to get approval from the AHJ.
The PV panels are a few meters above the occupied roof (parking). The panels are flat with 5% slope. There are minimal gaps between PV modules. The discussion of sprinkler the PV panels is partially due to it is a mass timber building.

Reply
Christopher Anderson
6/2/2022 12:36:48 pm

Buildings based on the NBCC model code defines a building as follows:

"Building means any structure used or intended for supporting or sheltering any use or occupancy" (from the 2018 BCBC).

The PV panels above the top level of the garage are analogous to a roof over that level and shelter the parking occupancy on that level.

If the mitigating feature of the sprinkler protection requires sprinklers on all levels; then the argument could be made that sprinklers are required below the PV panels.

This should be clarified with the consultant that developed with the mitigating feature requirement.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT