MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Smoke Detector Required in Elevator Pit?

7/19/2018

6 Comments

 
Daily Discussion question submitted from a member:

It seems that I must have missed something in the 23 years I've been in Code Enforcement.  Since when has it been required for a smoke detector to be in the pit of the elevator?  This is absolutely insane.  We've had more nuisance alarms recently in new buildings.  One is a 4 story nursing home, that the alarm has gone off 4 times.  The alarm company changed the detector and it been good now.  However there is still dirt, moisture, humidity, etc.  All the things that smoke detectors don’t like.

I've looked and Googled it and have only come up with a heat detector within 24" of the sprinkler head, which I understand.  I know smoke rises so why isn't the top of the shaft sufficient?  I feel we are going backwards.

Discuss this topic here.
6 Comments
JOE
7/19/2018 01:24:20 pm

Heat detectors can be required for elevator pits, whenever a sprinkler is located within the elevator pit (NFPA 72-2016 Section 21.3.7).

There are exemptions for locating heat detectors in the pit now, however; if a waterflow switch and valve serve only the sprinkler within the shaft, with no time delay, then a heat detector is not required (NFPA 72-2016 Sections 21.3.3, 21.3.7, and 21.4.3).

I haven't had a smoke detector be required within the pit of an elevator - it would be difficult to test and service so there's naturally a reason to avoid locating smoke detector where it's not practical or necessary.

Reply
Jason Lupa, PE
2/4/2021 09:56:08 am

This is a common question usually raised in the field. The are no smoke detectors which meet the NFPA 72 or UL listing requirements for spacing to be installed in elevator pits. All electrical equipment within 4 feet of the pit must be NEMA rated for wet locations. The are no smoke detectors which meet the NFPA 72 requirements for spacing or the UL wet locations listings, to be installed in elevator pits NFPA [2016] 21.3.8.

If the sprinkler is above 24“ from the floor, then the WP pit heat detector is used to initiate the Firefighters’ Emergency Operation (FEO). Activation should only initiate alternate recall to position the cab further from the pit fire event. NFPA 72 [2016] 21.3.12.2 (3). This same function can also be achieved via a sprinkler water flow switch dedicated for the elevator pit (NFPA 72 [2016] 21.3.3).

Reply
James
10/7/2019 11:57:10 am

since 2007 code smokes have been removed from pits and replaced with heats in the pit as dust and the amount of space in the area of devices it too detrimental to it. If no electrical devices are in the pit and everything electrical is exterior of shaft or pit the only thing required would be a smoke in the shaft as there are electrical equipment on the elevator cab itself. If shaft is sprinkled then there would need to be a heat in the shaft with 2' of the sprinkler head. SInce there id the NFPA 72, NFPA 101, ASME17.1, Construction Code as well as locality Code, all would have to be referenced. but even after all this the AHJ has the Final decision. So if unsure always call the AHJ.

Reply
Benjamin ORegan link
11/19/2020 02:19:00 am

It seems the 2019 version of NFPA 72 requires detectors in elevator pits to be accessible. How would we achieve that? A fire rated trap door in the elevator shaft perhaps, or aspirated smoke detection?

Reply
Brian Scruggs
12/21/2020 05:42:53 pm

The word “accessible” is up to interpretation. Run the elevator to another floor and insert the elevator key in the door. You now have access.

Reply
Braden Bills link
12/20/2021 09:06:08 am

I want to get an elevator installed, but I want to make sure that it's safe. It makes sense that getting smoke detectors installed would be important. I'll be sure to work with a professional to help me out with getting those installed.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT