Size Rod to Trapeze Separately than Rod to Pipe?

1/4/2024

8 Comments

 
In regards to a trapeze pipe support, isn't there an option to size the rod that connects structure to the trapeze pipe separately from the rod from the trapeze pipe to sprinkler pipe?

Couldn't that be two separate calculations considering there are two rods for the trapeze and only one to the sprinkler main?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
1/4/2024 08:10:13 am

I'm not sure if I understand your question fully, but to size the rods, NFPA 13 (2013) Table 9.1.2.1 should be used.

Reply
Pete H
1/4/2024 09:07:22 am

Table 17.2.1.1 in 2022 edition, but other than section it looks virtually unchanged

Reply
Dan Wilder
1/4/2024 08:34:28 am

NFPA 13 - 2019

It's possible, but not viable as it typically will cost more to prove (and likely field test) the smaller sized components via a structural engineer per 17.1.2.

17.2.1.1 For Hanger Rods
17.2.1.2 allows for smaller rod if tested AND LISTED for the HANGER ASSEMBLY (not just an individual component) ...just because the supported weight indicates a number below the total weight (15' of water filled pipe, x5, +250), there are typically additional safety factors required that are not met.

17.3.5* All components of each hanger assembly that attach to a trapeze member shall conform to 17.1.6 and be sized to support the suspended sprinkler pipe.

The below section is important because it requires the ring hanger to be sized per the pipe it's attached to but still comply with the support of the actual water filled pipe noted in 17.3.5 (this is where using the "Heavy Duty" rings like the Tolco Fig 200H using a 1/2" knurl nut but to attach to a pipe that is <4" instead of the standard 3/8")

17.3.6 The ring, strap, or clevis installed on a pipe trapeze shall be manufactured to fit the pipe size of the trapeze member.

There are some exceptions for some fasteners to be a lesser diameter but are then required, or already manufactured, to have the increaser to the correct rod size (The Hilti HUS-EZ-I is a good example with a 1/4" shank but a 3/8" coupler for the ATR). Section 17.2.3.3 has this language.

Reply
Anthony
1/5/2024 07:27:35 am

I agree with Dan here, especially with the use of the 200H. Those seem to be forgotten every time with trap hangers.

Reply
Casey Milhorn
1/4/2024 11:02:45 am

As Dan said, it is possible if you involve a structural engineer. If the project is large enough, and you have a line on an economical structural engineer, it might pay off, but unlikely.
If this is more of a practical issue (for example the roof structural engineer isn't allowing certain size penetrations, attachments, etc.) then you might have to go that direction. Or even ask them to prove it for you (at a small cost to you).

Reply
Dave
1/4/2024 11:10:54 am

Incorrectly-sized trapeze hangers components is one the most common review comments I make. As Dan pasted above, “All components of each hanger assembly that attach to a trapeze member shall conform to 17.1.6 and be sized to support the suspended sprinkler pipe.” By that I interpret that as EACH component. The NFPA #13 Handbook has a long commentary on this including, “One of the most common mistakes with pipe trapezes is to use an incorrect ring, rod, and/or attachment size.” Violations include ring-to-ring hangers that do not utilize special trapeze rings, trapezes whose ends are suspended by say, 3/8-in rod yet supporting a 6-in diameter pipe. Short of a specifically-engineered hangar assembly, about the only part you can get creative with on trapeze hangers is where along the trapeze the pipe is being suspended.

Reply
Glenn Berger
1/4/2024 02:16:27 pm

Dan nailed it. When reviewing submittals I prefer to see standard and approved designs that apply to the specific project.

Reply
Janak Patel link
1/10/2024 12:52:41 pm

A sprinkler pipe may not always be at the center of the trapeze structural member. In the worst-case scenario, the rod (very) close to the sprinkler pipe will carry almost all the load (i.e., as if it alone is supporting the pipe). Therefore, an option of sizing the rod size by special structural calculation which must be signed by a PE, is not provided.

Please note that a (ferrous) rod is not required to be 'Listed' per NFPA 13 (2019), Section 17.1.6.2.

The method,15' of water filled pipe x 5, + 250 has factor of safety already included in it, and it is applicable to the hanger component in tension only. In fact, this load is equal to the 'test load' per UL 203. For the trapeze member, (beam), the design load is (wt of 15' or 12' water filled pipe+250 lb.) acting at the center of trapeze, bending stresses not to exceed 15 ksi.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT