MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Sidewall Sprinklers Allowed for Water Curtain?

12/29/2022

12 Comments

 
Can sidewall heads be used for water curtain application?

While typically pendent are used to provide a water curtain around a vertical opening, I am working on a project where the arrangement led to sidewall heads being preferred by the architect.

NFPA 13 is not explicit about water curtain needing to be a specific type of sprinkler, it just says it should be a standard spray with 3gpm /lineal ft applied.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
12/29/2022 08:04:49 am

I see no code reason why not as long as you don't have any gaps in coverage or have any sprinklers too close without baffles.

It still seems wrong though.

Reply
Jesse
12/29/2022 08:12:10 am

Architects....

What most architects don't know about what we do can fill a book. And that book is NFPA 13...

I often answer questions in this forum by referring to the listing. If there is a sidewall sprinkler listed for that application, I'd go for it. But I'm not sure there is. There are sprinklers that are listed for that application. If it were my project I'd have the architect come up with a sidewall sprinkler listed for that use. And when he or she couldn't do that I'd use a product that is specifically listed for that.

Reply
Glenn Berger
12/29/2022 08:16:28 am

IMO, it depends on your specific application. Your application is a curtain system around a floor opening, I would use pendent sprinklers in this application. There are published limitations where vertical sidewall sprinklers can be used.

Also, do not let the architects dictate type of sprinkler to be used.

Reply
Todd E Wyatt
12/29/2022 09:27:08 am

SUMMARY
The use of an “Approved Alternate Method” (e.g. deluge sprinkler system) for determining the “fire resistance of building elements, components or assemblies” shall be approved by the AHJ.

Protection of “Vertical Openings” (VO) shall meet the requirements of (1) of the (16) prescribed solutions per 2021 IBC Section 712 Vertical Openings :
712.1 Each vertical opening shall comply in accordance with one of the protection methods in Sections 712.1.1 through 712.1.16.

An automatic sprinkler system (ASPS) is NOT an approved protection method for VOs.

EXPLANATION
The adopted Building/Fire Codes (e.g. 2021 IBC/IFC) are the scoping Codes as to WHERE an automatic sprinkler system (ASPS) is required to be installed based on the building’s Occupancy Classifications (OC) and/or “specific buildings and hazards” per 2021 IBC Section 903 Automatic Sprinkler Systems. The scoping Codes reference the applicable standard (e.g. NFPA 13) as HOW automatic sprinkler systems are to be “designed and installed.” Per 903.3.1.1.1 Exempt Locations, the IBC lists exempt locations for ASPS.

The only scoping Code reference to a “deluge ASPS” is per “404.6 Enclosure of Atriums” as an alternative to protection by 1-hour fire barrier and/or 1-hour horizontal assembly.

“Alternative Materials, Design and Methods of Construction and Equipment” can be submitted to the AHJ for consideration. As a former AHJ, I would not accept an active system (e.g. ASPS) in lieu of a passive system (e.g. fire-resistance rated shaft enclosure for a VO) for this condition but the AHJ may have a different take on this.

REFERENCES
2021 IBC
Chapter 7 Fire and Smoke Protection Features
Section 702 Multiple-Use Fire Assemblies
703.2 Fire Resistance
The fire-resistance rating of building elements, components or assemblies shall be determined in accordance with Section 703.2.1 or 703.2.2 without the use of automatic sprinklers or any other fire suppression system being incorporated, or in accordance with Section 703.2.3.
703.2.1 Tested Assemblies
703.2.2 Analytical Methods
703.2.3 Approved Alternate Method
The fire resistance of building elements, components or assemblies not complying with Section 703.2.1 or 703.2.2 shall be permitted to be established by an alternative protection method in accordance with Section 104.11.

104.11 Alternative Materials, Design and Methods of Construction and Equipment
The provisions of this code are not intended to prevent the installation of any material or to prohibit any design or method of construction not specifically prescribed by this code, provided that any such alternative has been approved. An alternative material, design or method of construction shall be approved where the building official finds that the proposed alternative meets all of the following:
The alternative material, design or method of construction is satisfactory and complies with the intent of the provisions of this code,
The material, method or work offered is, for the purpose intended, not less than the equivalent of that prescribed in this code as it pertains to the following:
1. Quality.
2. Strength.
3. Effectiveness.
4. Fire resistance.
5. Durability.
6. Safety.
Where the alternative material, design or method of construction is not approved, the building official shall respond in writing, stating the reasons why the alternative was not approved.

404.6 Enclosure of Atriums
Atrium spaces shall be separated from adjacent spaces by a 1-hour fire barrier constructed in accordance with Section 707 or a horizontal assembly constructed in accordance with Section 711, or both.
Exceptions:
1. A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
a. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;
b. The glass wall shall be installed in a gasketed frame in a manner that the framing system deflects without breaking (loading) the glass before the sprinkler system operates; and
c. Where glass doors are provided in the glass wall, they shall be either self-closing or automatic-closing.

Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.1.1 Alternative Protection
Alternative automatic fire-extinguishing systems complying with Section 904 shall be permitted instead of automatic sprinkler system protection where recognized by the applicable standard and approved by the fire code officia

Reply
Todd E Wyatt
12/29/2022 09:28:19 am

REFERENCES (Part 2)
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.1.1 Alternative Protection
Alternative automatic fire-extinguishing systems complying with Section 904 shall be permitted instead of automatic sprinkler system protection where recognized by the applicable standard and approved by the fire code official.
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.

Exception: Spaces or areas in telecommunications buildings used exclusively for telecommunications equipment, associated electrical power distribution equipment, batteries and standby engines, provided that those spaces or areas are equipped throughout with an automatic smoke detection system in accordance with Section 907.2 and are separated from the remainder of the building by not less than 1-hour fire barriers constructed in accordance with Section 707 or not less than 2-hour horizontal assemblies constructed in accordance with Section 711, or both.

Section 712 Vertical Openings
712.1 General
Each vertical opening shall comply in accordance with one of the protection methods in Sections 712.1.1 through 712.1.16.
712.1.1 Shaft Enclosures
712.1.2 Individual Dwelling Unit
712.1.3 Escalator Openings
712.1.3.1 Opening Size
712.1.3.2 Automatic Shutters
712.1.4 Penetrations
712.1.5 Joints
712.1.6 Ducts and Air Transfer Openings
712.1.7 Atriums
712.1.8 Masonry Chimney
712.1.9 Two-Story Openings
712.1.10 Parking Garages
712.1.10.1 Automobile Ramps
712.1.10.2 Elevators
712.1.10.3 Duct Systems
712.1.11 Mezzanine
712.1.12 Exit Access Stairways and Ramps
712.1.13 Openings
712.1.13.1 Horizontal Fire Door Assemblies
712.1.13.2 Access Doors
712.1.14 Group I-3
712.1.15 Skylights
712.1.16 Openings Otherwise Permitted

Reply
Jay
12/29/2022 03:52:05 pm

Todd, please see the section you referenced above, 712.1.3 Escalator Openings for the requirement of closely spaced sprinklers with draft stops, aka water curtain sprinklers.

Jay
12/29/2022 05:07:51 pm

Also, the code does not require the "window" sprinklers used for atrium enclosure, in lieu of 1-hr fire resistant glazing, to be a deluge sprinkler system.

Todd E Wyatt
12/30/2022 07:10:21 am

The commentor did not state that the Vertical Opening (VO) was an esculator opening. If it is, it would be required to meet the prescriptive requirements of 712.1.3 Escalator Openings :

712.1.3 Escalator Openings
Where a building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, vertical openings for escalators shall be permitted where protected in accordance with Section 712.1.3.1 or 712.1.3.2.

712.1.3.1 Opening Size
Protection by a draft curtain and closely spaced sprinklers in accordance with NFPA 13 shall be permitted where the area of the vertical opening between stories does not exceed twice the horizontal projected area of the escalator. In other than Groups B and M, this application is limited to openings that do not connect more than four stories.

712.1.3.2 Automatic Shutters
Protection of the vertical opening by approved shutters at every penetrated floor shall be permitted in accordance with this section. The shutters shall be of noncombustible construction and have a fire-resistance rating of not less than 1.5 hours. The shutter shall be so constructed as to close immediately upon the actuation of a smoke detector installed in accordance with Section 907.3.1 and shall completely shut off the well opening. Escalators shall cease operation when the shutter begins to close. The shutter shall operate at a speed of not more than 30 feet per minute (152.4 mm/s) and shall be equipped with a sensitive leading edge to arrest its progress where in contact with any obstacle, and to continue its progress on release therefrom.

"Draft curtain and closely spaced sprinklers" does not necessarily equate to "water curtain around a vertical opening."

2019 NFPA 13
3.3.57* Draft Curtain.
A continuous material protruding downward from the ceiling to create a reservoir for collecting smoke and heat.

ENHANCED CONTENT
The definition of draft curtain clarifies that, for sprinkler system purposes, the intent or function is to bank heat or smoke. The definition correlates with NFPA 204, Standard for Smoke and Heat Venting. Although not explicitly addressed within NFPA 13, NFPA 204 requires the curtain to be constructed of rigid materials.

The term "water curtain" does not occur in 2019 NFPA 13.

"Deluge Sprinkler System" is defined as follow :

3.3.206.3 Deluge Sprinkler System.
A sprinkler system employing open sprinklers or nozzles that are attached to a piping system that is connected to a water supply through a valve that is opened by the operation of a detection system installed in the same areas as the sprinklers or the nozzles. When this valve opens, water flows into the piping system and discharges from all sprinklers or nozzles attached thereto.

ENHANCED
A deluge system’s mode of activation is similar to that for a preaction system. With the exception of the non-interlock preaction system, the activation of these two types of systems depends on the operation of a supplemental detection system. The difference between the two types of systems is that preaction systems employ automatic sprinklers that respond to heat, and deluge systems use open (nonautomatic) sprinklers or open nozzles. Operation of the detection system in a preaction system fills the system piping with water once certain interlocks are triggered. Water is not discharged from the system until a sprinkler operates. For a deluge system, operation of the detection system results in flow from all system sprinklers or nozzles. Deluge systems are normally used for high hazard areas requiring an immediate application of water over the entire hazard. An aircraft hangar is an example of a facility that is likely to use deluge systems. The exhibit below illustrates an example of a deluge system using a supplemental electronic heat or smoke detection system.

Todd E Wyatt
12/30/2022 07:15:23 am

"Also, the code does not require the "window" sprinklers used for atrium enclosure, in lieu of 1-hr fire resistant glazing, to be a deluge sprinkler system."

I stated that the 2021 IBC permits (not requires) the substitution of an atrium's Fire Barrier with a prescriptively complying automatic sprinkler system (ASPS) :

404.6 Enclosure of Atriums
Exceptions:
1. A fire barrier is not required where a glass wall forming a smoke partition is provided. The glass wall shall comply with all of the following:
a. Automatic sprinklers are provided along both sides of the separation wall and doors, or on the room side only if there is not a walkway on the atrium side. The sprinklers shall be located between 4 inches and 12 inches (102 mm and 305 mm) away from the glass and at intervals along the glass not greater than 6 feet (1829 mm). The sprinkler system shall be designed so that the entire surface of the glass is wet upon activation of the sprinkler system without obstruction;
b. The glass wall shall be installed in a gasketed frame in a manner that the framing system deflects without breaking (loading) the glass before the sprinkler system operates; and ...

Anthony
1/2/2023 11:26:04 am

First off you can only use closely spaced sprinklers for: atrium protection or if you have a letter from the AHJ saying that sprinklers that are closely spaced are an approved alternative.

in such a cases I do not believe that side wall heads would be appropriate as the goal of the "curtain" is to create a cooling area around the vertical opening reducing the heat transferred between floors.

In architect speak: "Sprinklers do not create wall/hr ratings they reduce the requirements of wall ratings."

That sentence has stopped a lot of long e-mail exchanges in my life.

Reply
Aidan Bird
10/11/2023 01:41:28 pm

In the case of the protected opening exception, 705.8.2 (Seattle Building Code, 2018) sprinkler system with heads designed for water curtain can be used. Is this a deluge system? Or area the heads just added along the area of windows that need protection... ?

Reply
Moderator
10/13/2023 01:41:37 pm

Hi Aidan,

Recommend to submit as a new question since this is an old thread - go.meyerfire.com/ask and you can submit it for consideration.

Thanks!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT