MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Set Standpipe PRV by Flowing One or All Valves?

1/9/2023

7 Comments

 
We are working on a new (750 gpm) standpipe system.

When testing and setting the field adjustable 2-1/2" PRV hose valves, do you set each one flowing 250 gpm while also flowing 500 gpm elsewhere, to account for the hydraulically calculated design (i.e. lower inlet pressure per NFPA 14-11.5.5.1)?

Or do you just set each one only flowing 250 GPM by itself?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
1/9/2023 08:02:11 am

Our testing/Cx went as follows:

Calculations were 2 fold...

Calculation at full flow (750 GPM) - Meets NFPA 14-19 11.5.1.2 & 25-20 6.3.1.1
Calculation at single flow (250 GPM) - Meets NFPA 14-19 11.5.5.1 & NFPA 25-20' 13.5.2.2

Generally the top of the standpipe(s) were standard hose valves so we performed two full flow tests, one at the top and one at the highest level were the PRV's ended.

Generally, those two settings were the same but when they differed, it was a matter of picking a setting that does match both or getting one that met the full flow calculation. We would rather over-discharge a single hose valve than short one but we got the AHJ buy off in writing (the AHJ would rather see a static condition on a hose at 180 PSI vs a residual flowing at 95 PSI).

Fun note, upsize the gang drain at the base and don't use the plastic hoses & clamps on the sprinkler risers - always hard pipe, braided hoses, or copper.....plastic blow off.

Reply
Casey Milhorn
1/9/2023 08:11:59 am

I like Dan's method. Very comprehensive. We typically just set ours based on 250 gpm of flow. I think the conversation that Dan had with the fire department becomes even more important when you are outside of the responding departments pumping capacity/elevation. Great question.

Reply
sean
1/9/2023 08:31:30 am

it needs to be set by the flow expected downstream of the device

Reply
Jesse
1/9/2023 09:00:15 am

I second Dan's approach.

And I very emphatically agree with upsizing the drain.

Reply
Bobby Suarez
1/11/2023 01:15:51 pm

NFPA 14 requires automatic class 1 standpipes to provide 100 psi during the full system demand flow not just 250gpm. It clearly states that the hose valve manufactures friction loss should be used in determining the loss through the valve. The PRV manufacturer selection spreadsheet should use the highest anticipated static pressure (static pressure during pump churn) and the lowest anticipated residual pressure ( full NFPA 14 system flow plus friction loss) . In other words the PRV setting should be chosen based on that valve being the last 250gpm of the total system flow. If you dont choose your PRV setting using a similar method you will create a lower floor with a hydraulically more remote demand. Ken Isman's Standpipe Handbook explains this dilemma well.

If you choose your PRV setting in this manner you should have no problem meeting flow requirements in any require scenario.

When we have found this not to be done correctly we found a 30 floor building with more pressure available at the roof hose valves then at the discharge of the ground floor hose valves during the full 750 or 1000 gpm flow.

The same would not be true with a pilot operated PRV but nearly all Hose valve PRV are direct acting and therefore reduce by a fixed percentage and are oblivious to lower than expected inlet pressures. You must choose the setting using the NFPA 14 lowest anticipated residual pressure.

Reply
Brian Lukus
1/12/2023 03:48:02 pm

Bobby, In practice to account for the NFPA 14 lowest anticipated residual pressure, do you flow the extra 500gpm when setting the PRV for acceptance testing to drop inlet pressure on the tested PRV? Or do you set the PRV based on the manufacturer curve using the hydraulic calc info, and then just flow test the PRV at 250gpm for acceptance testing?

Reply
Bobby Suarez
1/19/2023 10:35:16 am

Brian we require the calculation and valve selection proving that the valve works during full system flow and then we do the acceptance test at 250gpm unless that PRV is one of the hydraulically most remote valves in the portion of the building where the standpipe acceptance flow test will occur. In which case the PRV is flowed as part of the full 750/1000 . For example a few days ago we were acceptance testing a high rise building that has only 2 risers in the upper floors but 3 risers in the lower floors. The lower floors with 3 stairwells have PRVs so those floors flowed their highest PRVs at 4 valves at 1000 gpm and then the roof without PRVs flowed 750 through standard valves.
Rsuarez AT miamiGov dot com




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT