MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Second 2.5" Outlet on Same or Different Hydrant?

9/13/2022

11 Comments

 
When conducting flow tests and the desired flow (gpm) for the test is not obtained via a single 2-1/2" fire hydrant outlet, should additional flow be achieved by opening an additional 2-1/2" outlet on that SAME fire hydrant, or should a single 2-1/2" outlet be opened on an ADDITIONAL fire hydrant?

So for multiple 2-1/2" outlets opening and flowing, should this be done:
  • (A) using one fire hydrant with two 2-1/2" outlets flowing, or
  • (B) with two fire hydrants with one 2-1/2" outlet flowing each?

I have heard people say that (A) is correct and (B) is incorrect, and vise versa. Thank you.

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Alex
9/13/2022 06:18:50 am

Hi,

(B). You want to use multiple hydrants.

NFPA 291 outline the testing procedures. Figure 4.3.4 outline suggested test layouts for multiple hydrants.

4.3.5 states the number of hydrants to be used depends on the strength of the system

4.3.6 states to obtain a satisfactory test, you need to achieve a drop in pressure of at least 25 percent, or to flow the total demand necessary for fire-fighting

4.3.7 states if the mains are small, a single hydrant can be flowed but..

4.3.8 states if the mains are strong, you need to flow multiple (seven or eight) hydrants

Thanks,
Alex

Reply
Dan Wilder
9/13/2022 07:59:56 am

This will be interesting...I am in the (A) school of thought.

The handbook commentary states

"In order to produce a pressure drop of 25 percent, or the total fire demand, multiple outlets on the flowing hydrant may need to be opened during the test. In some cases, this may require that several hydrants be flowed simultaneously to produce a sufficient pressure drop and/or flow." So, we open a hydrant to it's capacity before adding additional hydrants.

Our flow tests always start with the pumper outlet no matter what, then add in the 2½" ports on a single hydrant before adding in an additional hydrants. If we provide an compound test, we do follow the suggested test layouts per Figure 4.3.4. as best as possible with the known water supply routing.

We have an AHJ that will request us to provide minimum water required and provide a test meeting that minimum.....however, their own paperwork states that the test is invalid due to the 25% drop not being achieved. When we have requested a 25% drop, they won't do the test without a GPM (even if we say "X" GPM or 25%, whichever is greater). If we request a GPM that we think will produce a 25% drop based on previous tests, we get push back because of the manpower resources and water depletion required to get the 25%, and it takes weeks to complete....but they accept the invalid test for submittals so....

Reply
Eric R
9/13/2022 08:27:31 am

I don't see this question so much as an either/or but more of priority of selection. Opening the second 2.5" on the hydrant is an easy first step, and there certainly isn't anything wrong in doing so. From there, if you still need more water then a second hydrant should be opened up,

We generally default to two 1.75" hose monsters on our flowing hydrant which gives us a good range of throttling control and increased accuracy. I feel this is generally sufficient for a light or ordinary hazard system designs. Even for systems that only need 300-600 total gpm I think it's good practice to flow at least 1000gpm if the utility can handle it, as it provides a much more accurate curve to base a design on.

It gets a bit trickier when you get into the higher hazards however. In our area, some jurisdictions allow us to perform our own hydrant tests, while others require they be done by the utility. This can be problematic when the utility says they cant flow the demand we need due to lack of equipment, but also wont allow us to supply the necessary equipment/manpower to get the results ourselves.

For high demand systems like ESFR the flow test arrangement needs to be carefully planned based on knowledge of the underground layout, peak water demand times, and proper selection of hydrants to get a balanced flow per NFPA 291.

Reply
Jay
9/13/2022 10:01:17 am

The intent is to flow more outlets on a single hydrant. You flow more than one hydrant only if you can't achieve the pressure drop or flow you're seeking from the single hydrant.
The recommended 25% drop in pressure was changed to 10% in the 2022 edition of 291.
If you're flowing from the pumper outlet, there is a reduction factor (coefficient) that needs to be applied to the calculated flow (typically 0.83) due to the likelihood that cross sectional area of the large orifice is not completely filled with water (air pockets).

Reply
Jesse
9/13/2022 10:03:23 am

Multiple hydrants, and NFPA 291 has some great examples of where the additional hydrants can be in relation to the test hydrant.

Reply
Joe F
9/13/2022 10:20:38 am

I agree with Dan & Eric. (A) If you can achieve the desired 25% drop in pressure with a single hydrant flowing both ports that is completely acceptable. If not add additional hydrants as needed.
When we are talking about Hydrant Flow Testing, is the objective to obtain the data for the projects “Fire Flow Demand” or “Fire Sprinkler Demand” In Light and Ordinary Hazard Occupancies the demand is dramatically different. It is much easier to prove water availability for fire sprinkler demand vs the required fire flow for a project.
Another item to keep in mind is knowing the high elevation point of the water system. Our terrain is extremely hilly area, and the pressure difference between the high and low points of the water system can vary greatly. The residual pressure should not drop below 20 psi anywhere in the water system. Knowing the water systems high point is important and placing a residual pressure gauge on the nearest high point hydrant is a great safety precaution.

Reply
Dave
9/13/2022 11:05:18 am

I am with the majority (so far) above, the greatest majoriy of the the time we flow the (2) 2-1/2" on one hydrant, which in my experiernce is usually sufficient. If additional drop is needed, we flow two from an appropriately selected additional hydrant (if available). I agree with Eric as well, not so much an either/or.

Reply
Chris
9/13/2022 11:32:34 am

Where I live the typical water supply is very strong, sometimes as good as 90-100psi static pressure with drops of only 5-10psi while flowing 1100gpm+. So when working with LH and OH we generally only flow one outlet, but when working with ESFR or storage we flow multiple outlets.

I read 291 as multiple hydrants, except for 4.7.9 in the 2022 edition it says "...by the number of hydrants used and the number of outlets opened on each." Other than that I don't see anywhere else where it mentions multiple outlets on single hydrants.

My vote goes to option (B)

Food for thought, I conducted two flow tests at the same location one conducted like (A) where static was 62, residual was 56 and flow was 2,106gpm. Then I conducted one like (B) and got static of 66, residual was 50 and flow was 2,042gpm (Hyd#1 1,186gpm, hyd#2 856gpm). The tests were done over a year apart though, although development in the area between tests has been minimal.

Reply
Franck
9/13/2022 01:01:39 pm

You can do both
What is important is the total flow (that is what is leading the friction losses, and therefore the pressure drop).
Remember that with such a flow test you measure your system at the hydrant where you measure the pressure, not the flow.
This means that for a dead end line, there is no difference in the results if you open 2 outlets at one hydrant or 2 hydrants, as long as they are all located downstream the “pressure hydrant”. With a loop system, it becomes more problematic and you should chose carefully the location of the flowing hydrants compared to the pressure hydrant. See NFPA 291, they have nice sketches for the selection.
In that case, opening 2 outlets on the same hydrant (option A) will give you more accurate information.
After making a lot of hydrant testing in my long life of loss prevention engineer, I always use option A as it is easier (I am lazy), flow less water (if you test with a pitot tube and need to walk from one hydrant to the other… you will spoil a huge amount of water… This may be my environmental side), and is more accurate at the end.

Reply
Glenn Berger
9/13/2022 02:52:04 pm

As others have said, you need to follow NFPA 291 as the recommended practice for hydrant flow testing.

Questions to be answered prior to an appropriate answer:

1) Are you testing hydrants on a dead-end system?

2) Can you shut a valve such that you can simulate worst case scenario with a looped or gridded system out of service?

3) If testing multiple hydrants can you maintain line of sight and/or communication with the people at the other hydrants?

My personal preference is to simulate an one-way flow condition and then open as many outlets as required to achieve the proper pressure drop. A pressure drop of 25% is what is stated in NFPA 291, but not always easily achievable.

Before conducting the test, you need to understand the system configuration and preferably have historical data available to determine the adequacy of the test information recorded.

Reply
schulman
9/15/2022 06:12:55 am

constantly receiving flow tests NOT done to NFPA 291 ...makes my job difficult if not frustrating. Please do tests per NFPA 291 if you are a testing contractor !!!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT