Sealed Fire Sprinkler for Conveyor Protection?

12/22/2022

10 Comments

 
Hi all, is anybody aware of a sealed sprinkler that is available in the market with an elongated spray pattern?

I'm looking for something specifically designed for conveyor protection.

Have tried the main manufacturers (Reliable, Tyco, Viking etc.) but nothing seems to be out there. The FM data sheet (FMDS0711) suggests that they are out there.

Many thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Jesse
12/22/2022 08:08:29 am

I learned long ago that just because the code (NFPA or FM) suggests a certain sprinkler may be used, that doesn't mean said sprinkler exists yet, or ever will.

There are numerous sprinklers with an elongated spray pattern - think corridor protection / attic protection- but if they aren't specifically listed for the application you shouldn't use them. I'm not familiar with a sprinkler specifically listed for what you're wanting other than ubiquitous standard spray sprinklers. Other may, so good luck!

Reply
Glenn Berger
12/22/2022 08:36:59 am

I have always just used standard spray sprinklers, open or closed type based upon site specific conditions.

Reply
Franck
12/22/2022 08:38:42 am

I do agree with Jesse
Protection of conveyors is a real challenge (fast moving, combustible load possibly on the conveyor, many aggravating factors such as slope…) and deviation from existing standard installation should be avoided.

If the aim is to provide less sprinklers with a larger spacing, this does not seem to me as a good idea.

Reply
Jesse
12/22/2022 08:47:47 am

I too have always just used standard spray sprinklers. And while not part of the sprinkler discipline per se but rather the overall fire protection engineering of the facility, Glenn touched on a very important point. These are moving - usually pretty fast. We know that numerous areas of ignition creating a bunch of little incipient fires along the way that grow to become bigger fires will overwhelm the water supply pretty quick. That interlock to shut it all down on water flow is pretty critical.

Reply
Shane
12/22/2022 09:37:13 am

I agree with the above. Also, corridor and attic sprinklers are listed for light hazard use only. Conveyors are usually in ordinary group 2 and higher hazards. Stick with the Standard Spray Sprinkler Heads.

Reply
Matt C.
12/22/2022 09:42:35 am

The ONLY sprinklers I have come across that have narrow spray patterns like this are corridor/hallway sprinklers, which are obviously NOT designed for this application. They do however have crazy long coverage areas in the neighbourhood of 28'x10' or 28'x12' (see Viking VK638, Reliable RA5814, Tyco TY4282).

TL;DR - yes there are sprinklers which are designed to cover long/narrow areas, but none are for protecting conveyors (to my knowledge)

Reply
Dan Wilder
12/22/2022 10:40:27 am

I think the wording of sealed is not referring to a closed head sprinkler but sealing the opening through an enclosed conveyor. It's not a smoke/heat/fire barrier and does not have to be rated so we have utilized everything from a 2" coupling rubber turned inside-out over a 1.5" pipe to having their sheet metal guys cut a horseshoe out of scrap and Tek screw it to the shroud

We have used Viking Model E Nozzles (any nozzle MFG will due) to spray bearings, rollers, and motors (upper and lower) with a deluge system interlocked to the electrical controlling that conveyor. When overhead tunnel protection was required, it would be either a deluge system with standard spray sprinklers or nozzles depending on the height/width of the tunnel.

Tyco has the TN-25 sprinkler for tunnels (not quite this application I think), other than that I don't know of a wider than longer throw pattern available for conveyers.

Just leave a bag of the nozzle caps with the owner for their maintenance guys, they will appreciate you.

Reply
Alex
12/22/2022 02:09:20 pm

As others have mentioned, I do not believe there is an extended spray sprinkler for this application.

Reply
Dwight Havens
12/24/2022 02:34:42 pm

I would like clarification of the meaning of "sealed". If it means closed head, the use of directional nozzles, like the Tyco EA-1 may be appropriate. If looking at an open head nozzle, a Tyco D3 might work. Other manufacturers also may have them in their catalogs.

Reply
Phil Watkins
12/28/2022 03:46:43 am

Hi all and many thanks for the input on my question. Just to clarify, I did mean a sealed sprinkler (i.e. thermal bulb or soldered strut) as opposed to an open nozzle.

The reason for the specific question on whether there was a sprinkler with an elongated spray pattern was not to necessarily keep the number of sprinklers low, but was more about an more efficient distribution of the water delivered so that more or it lands on the conveyor as opposed to outside of it.

The conveyors in question are non-inclined, elevated and more than 10m from the roof sprinklers. The use of sprinklers as opposed to water spray is already specified and permitted by NFPA 850. The use of water spray on inclined conveyors is provided already for those conveyors.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT