Saunas Considered "Bathrooms" for Sprinklers?

3/21/2024

12 Comments

 
Are Saunas within dwelling units considered bathrooms?

Bathroom: within a dwelling unit, any room or compartment dedicated to personal hygiene, containing a toilet, sink, or bathing capability such as a shower or tub.

​Would saunas fall under the definition of bathroom, since they are dedicated to personal hygiene and contain a bathing capability?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
L GOLDEN
3/21/2024 08:15:19 am

Saunas by Websters Definition are hygiene/bathing areas.

However,
Causes of sauna fires over the years have included:

Electrical malfunction
Drying of clothes or towels over the heating element
Newspapers or magazines being left in the sauna
Charring of the wood in the sauna to a point where risk of it catching on fire is increased (pyrolytic decomposition)

286 Degree Heads are typical......
As it is a higher heated room/area/space than a common "bathroom"

Reply
Anonymous
3/21/2024 08:15:20 am

Is this a sauna that would be found in a public gym, or a stand alone unit like...a sound booth? If it's a public gym, I would and have protected them as any other room (mine was over 55 sq. ft.). What type of construction; wood or tile?

Reply
James Phifer
3/21/2024 08:22:16 am

Seems to fit the definition of a compartment dedicated to personal hygiene.
The following definition is from the Oxford language dictionary.

Sauna- a small room used as a hot-air or steam bath for cleaning and refreshing the body.

Reply
Anthony
3/21/2024 08:36:36 am

Saunas =/= bathroom.

Many saunas are built out of combustible construction (wood) and pose a higher fire risk. Bathrooms 'generally' do not carry as heavy a load of combustible material.

Reply
Chris N
3/21/2024 08:38:04 am

Generally saunas are constructed of wood. While Webster dictionary says its for cleaning, generally bathrooms are constructed of tiles, porcelain, and gyp. So the rational doesn't seem to match with the intent.

See this NFPA Journal article.
https://www.nfpa.org/news-blogs-and-articles/nfpa-journal/2011/11/01/nfpa-13-and-permissible-sprinkler-omissions

Reply
S
3/21/2024 08:55:52 am

Hopefully this is helpful. I work in a 12 Jurisdiction area and in all cases we have had to put a 286F (typically use black poly or white if the lighting is white) sprinkler inside the sauna. We even had one case the sauna was out the back door installed next to the house and the AHJ required a sprinkler inside the unit. It is fully combustible, plus all the exact reasons listed above by L Golden.
I'm curious to hear more by other areas around the country.

Reply
Todd E Wyatt
3/21/2024 09:01:03 am


You did not identify what the OCs (Occupancy Classifications) are included in the building and/or what the scoping Code (e.g. IBC--2021 vs IRC-2021) is.

The adopted scoping Code (e.g. IBC-2021) determines WHERE an automatic sprinkler system (ASPS) is required to be installed based on the building’s Occupancy Classification(s) (OC) and/or Specific Building Areas and Hazards (per IBC-2021 903.2.11).

The “Referenced Standard” (e.g. NFPA 13-2019, NFPA 13R-2019) per the scoping Code identifies HOW the ASPS is to be “designed and installed.”

The “exempt location” you referenced is per IBC-2021 903.3.1.1.2 Bathrooms : “In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.”

Since “saunas” do not meet the intent (e.g. limit combustibles) of this exemption, an ASPS would be required UNLESS it is in an OC that does not require an ASPS.

Reply
Todd E Wyatt
3/21/2024 09:01:33 am

REFERENCES
IBC-2021
Chapter 35 Referenced Standards
User note:
About this chapter: The International Building Code® contains numerous references to standards promulgated by other organizations that are used to provide requirements for materials and methods of construction. This chapter contains a comprehensive list of all standards that are referenced in this code. These standards, in essence, are part of this code to the extent of the reference to the standard.
This chapter lists the standards that are referenced in various sections of this document. The standards are listed herein by the promulgating agency of the standard, the standard identification, the effective date and title, and the section or sections of this document that reference the standard. The application of the referenced standards shall be as specified in Section 102.4.

IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.

903.3 Installation Requirements
Automatic sprinkler systems shall be designed and installed in accordance with Sections 903.3.1 through 903.3.8.
903.3.1 Standards

903.3.1.1 NFPA 13 Sprinkler Systems
903.3.1.1.1 Exempt Locations
903.3.1.1.2 Bathrooms
In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.

903.3.1.2 NFPA 13R Sprinkler Systems
903.3.1.2.1 Balconies and Decks
903.3.1.2.2 Corridors and Balconies in the Means of Egress
903.3.1.2.3 Attics

Reply
Dan Wilder
3/21/2024 09:04:10 am

The reference provided is the NFPA 13 definition and if the room complies with 9.2.4.1.1 (13-22' Ed.) for noncombustible finishes possibly. As these units are typically independent of the room (pieced together), the 15 min thermal barrier may not typically be available for the front of the unit into the rest of the compartment so if the install can be the Sauna and the adjoining room all within 55ft², there may be a chance to argue.

I would argue against a Sauna being "Bathing Capable" due to the "convenience" factor of the unit going beyond the normally required bath/shower.

One big difference is the heat source located within the room. A closet that complies with omission requirements of a sprinkler, still requires a sprinkler as soon as a water heater/washer/dryer/ is placed within the space. I see the direct correlation between the two approaches and would provide protection.

Reply
Jack G
3/21/2024 09:14:11 am

Consider the following:
Most saunas have a top temperature of 194 degrees F.
Sauna is combustible - most municipalities require a 1 hour separation or sprinkler protection.
Human skin starts to feel pain at 113 degrees. Sauna temperatures could boil a person. A fire ( from electrical or wood charcoal or towels ) would definitely cook a person whether they were conscious or not.
Sauna manufacturers ( steam rooms also) indicate fire sprinklers should be installed ( that’s good enough for me) 286 F or higher head.
So it’s best to protect them ( domestic water - sprinkler ) is ok if installed with proper protection from back flow- expansion)
Opinion.

Reply
RayJ link
3/21/2024 11:06:56 am

Bottom line, it would be really cheap and petty to place the value of a life over the cost of 1 fricking sprinkler head.

Reply
Franck
3/21/2024 11:31:05 am

Definetly not a bathroom.
As indicated above : saunas have an electrical heating system, they are made of wood (as wood does not heat up as much as metal or some other surfaces), the combustible load is far more important than in a bathroom and sources of ignitions are more present as well.
Definetly require sprinkler protection.

Note that situation is slightly different with Hamam where moisture is at a higher level and wood is not used for constrcution (but tiles, instead of wood). Mostly for hygienic purposes.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT