Rolled Mattresses: Unexpanded or Expanded?

5/1/2023

9 Comments

 
Hi all - I am currently reviewing an ESFR sprinkler protection of compressed, rolled-mattresses in cartons.

During a fire, once the carton burns, the mattresses will be able to retrieve, at least partially, its initial uncompressed configuration. Considering this, I'm skeptical about it being classified as a cartoned unexpanded plastic.

It seems to me that the proper classification should be cartoned expanded plastics, as I've found nothing justifying this optimistic opinion. 

Do you have an opinion on how this should be properly classified, or how you would view it?

I'd love to hear about your point of view on the subject and choices made for similar projects.

Thanks and regards.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
5/1/2023 06:40:27 am

Ultimately it depends which type of foam is used to make your mattress.

In a lot of cases, it's going to be polyurethane foam.

Polyurethane is noted in the Appendix of Chapter 5 of NFPA 13 (2016 edition) as an Expanded Group A Plastic.

So in a lot of cases, it's an expanded group a plastic.

Ask for an MSDS sheet of the mattress.

Reply
Pete H
5/1/2023 06:42:39 am

Also worth noting in Table A.5.6.4.1 (NFPA 13 2016 edition) is that "Mattress; foam (in finished form)" is also noted as an Expanded plastic.

It seems really likely this is an expanded plastic.

Reply
Dan Wilder
5/1/2023 07:09:49 am

I'm with Pete...

First, what is the foam type
Second, what is it's final use

There is some ability for prewetting the exterior box (assuming it's not one of those plasticizer infuser cardboard boxes that are around everything and it's not already encapsulated on a pallet) , but then you have the foam encapsulated in plastic that's been compressed. Ya, understanding the mattress used to say 24 hours for "final form" but I've seen them in under an hour meaning it's well expanded just out of the packaging.

Reply
Anthony
5/1/2023 07:30:35 am

As you said, and I agree:

"During a fire, once the carton burns, the mattresses will be able to retrieve, at least partially, its initial uncompressed configuration. Considering this, I'm skeptical about it being classified as a cartoned unexpanded plastic."

Thus expanded.

Reply
Jesse
5/1/2023 08:06:19 am

I agree with the others. I'd definitely treat this as cartoned / expanded.

The type of foam is indeed important, but even if some of the foam is polyurethane, that will drive the commodity class.

Reply
Jesse
5/1/2023 08:08:58 am

I hit submit too fast.

The other issue involves the mattress when the carton is compromised. Yeah they say it takes 24 hours or more to achieve full shape, but in my experience these achieve 90% of their size and shape within minutes of leaving the box.

Reply
Franck
5/1/2023 12:45:44 pm

You can compress it as much as you want, an expanded plastic remains an expanded plastic (mainly because of its chemical characteristics, not only because of the possible amount of air trapped).
Some are worst than others, but they are all classified as expanded plastics.
(same with wood, some are worst than others, because of their chemical arrangement, but all are considered class III).

Reply
Bjørn B
5/1/2023 02:51:18 pm

I agree with the others. When you have a fire it will quickly become exposed expanded,

Maybe if you have kept it compressed for 10 years or so ........

Reply
Mary Bran link
6/21/2024 08:48:51 am

Hello everyone,

I'm currently evaluating a sprinkler protection for compressed, rolled mattresses in cartons. A key concern is their classification during fires, where they can partially regain their uncompressed shape after the carton burns.

I'm skeptical about labeling them as cartoned unexpanded plastic and lean towards classifying them as cartoned expanded plastics. I'd appreciate your insights on this classification and any experiences with similar projects.

Looking forward to hearing your thoughts.

Thank you.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT