MeyerFire
  • Blog
  • Forum
  • THE TOOLKIT
    • SUBMIT AN IDEA
    • BACKFLOW DATABASE*
    • CLEAN AGENT ESTIMATOR*
    • CLOUD CEILING CALCULATOR
    • DOMESTIC DEMAND*
    • FIRE FLOW CALCULATOR*
    • FIRE PUMP ANALYZER*
    • FIRE PUMP DATABASE*
    • FRICTION LOSS CALCULATOR
    • HANGER SPACER*
    • IBC TRANSLATOR*
    • K-FACTOR SELECTOR*
    • NFPA 13 EDITION TRANSLATOR ('19 ONLY)
    • NFPA 13 EDITION TRANSLATOR ('99-'22)*
    • LIQUIDS ANALYZER*
    • OBSTRUCTION CALCULATOR
    • OBSTRUCTIONS AGAINST WALL*
    • PLUMBING FIXTURE COUNTS
    • QUICK RESPONSE AREA REDUCTION
    • REMOTE AREA ANALYZER*
    • SPRINKLER DATABASE*
    • SPRINKLER FLOW*
    • SYSTEM ESTIMATOR*
    • TEST & DRAIN CALCULATOR
    • THRUST BLOCK CALCULATOR
    • TRAPEZE CALCULATOR
    • UNIT CONVERTER
    • VOLUME & COMPRESSOR CALCULATOR
    • WATER STORAGE*
    • WATER SUPPLY (US)
    • WATER SUPPLY (METRIC)
  • UNIVERSITY
    • JOIN
    • CATALOG
    • CONTENT LIBRARY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE Prep Series
    • PE 100-Day Marathon
  • LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Restraint for Long Sprinkler Drops in Seismic Area

8/23/2019

13 Comments

 
I have a warehouse with a roof 20 feet above. The designer has branch lines hanging under the ceiling joists. He has 10 foot drops of 1-1/2" sched 40 to an ACT ceiling over office spaces. We are in a "D" seismic design category building. I am unable to find any requirements for vertical restraint in the NFPA 13 or ASCE 7-10. Can anyone direct me? 

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
13 Comments
Jonathan
8/23/2019 10:22:22 am

NFPA 2016 9.3.6.7 Drops and arm-overs shall not require restraint


NFPA 2019 19.6.7 States the same


I recommend providing a lateral restraint on the branch line or arm over.

Reply
jonathan
8/23/2019 10:34:13 am

New code NFPA 2019 18.6.3.1 (Restraint of Branch Lines)


The location of the restraint at the end of the line shall not be greater than 36 in. for 1in. pipe 48 in. for 1 1/4 pipe and 60 in. for 1 1/2 pipe or larger


But if your rod is less than 6 in. from top of pipe to the attachment, restraints can be omitted 18.6.5 2019 and 9.3.6.5 2016

Reply
James Phifer
8/23/2019 10:36:14 am

below is what I found from NFPA 13, 2016 edition

9.3.6.7 Drops and armovers shall not require restraint.

9.3.2.3.1 The flexible couplings shall be installed as follows:
Within 24 in. (600 mm) of the top of drops exceeding
15 ft (4.6 m) in length to portions of systems supplying
more than one sprinkler, regardless of pipe size

Reply
Don
8/23/2019 10:47:32 am

Thank you Jonathan. I fail to understand the reasoning behind this. A 4' vertical sprig requires lateral restraint but a drop of any length with a vertical sidewall head doesn't. Hmmmm...I'll have to chew on this some more.

Reply
Jonathan
8/23/2019 11:15:34 am

Yeah it's strange but I'm assuming they think since the head will be in ceiling tile there will be little to no lateral movement. I don't see grids handling to well during an earthquake. Depends on how bad the earthquake will be I guess.

Good Luck Don


Reply
Rusty Scott
8/23/2019 10:54:03 am

Normally they have one feed main pipe drop down to just above the office (which is seismically braced with four way brace) and use long hangers that use connector nuts to extend the all thread rod to make it reach the structure. They will have end of line restraints on the horizontal branch piping. I've seen seismic cable used in a lot of spaces for the mains. If you locate the main 8" above ACT they'll have normal sized drops. Also make sure they have retaining straps and surge clips.

I have a similar case to you in a school in South Carolina where it's a 15'-0" drop pendent for an office in a theater office space only needing one sprinkler. Since we have it in our company specs and install notes that they have to brace branch piping longer than 4'-0".

If you look at NFPA 13-2013 9.3.6.6 springs 4 ft or longer shall be restrained against lateral movement. In A9.3.6.6 it discusses using wire from 9.3.6.1 and the length does not include the fitting and sprinkler. We basically have adopted this code to brace drops over 4'-0". To me I don't know why a sprig would be treated differently than a drop, I don't really see the logic in it, so that's why it's in our specification and notes. Maybe it's because of the difficultly to actually brace it vs a sprig being close to structure.

Reply
Brian Gerdwagen
8/23/2019 11:32:39 am

You never want to brace drops to a single sprinkler. Drops are supposed to have flexibility so that the differential movement is absorbed. Springs are restrained so they do not fall over and twist through lever action on the fitting below. You can not equate the two.

In seismic D, ASCE 7 says you must cut an oversize hole 1" larger than the sprinkler or use a flexible drop.

Reply
Rusty Scott
8/23/2019 03:45:20 pm

The long 15'-0" drop does have a flexible hose connection at the ACT ceiling. Would it be deemed acceptable to brace the drop then?

Brian Gerdwagen
8/26/2019 08:25:05 am

Acceptable, but not code-required.

Reply
DTC
8/26/2019 08:37:02 am

Good discussions. In our area the local AHJ's have all amended NFPA 13 9.3.6.7 to state any drops and arm-overs over 10' shall be restrained.

Reply
JAL
3/5/2021 12:49:08 pm

@DTC That's great your AHJ has a clear definition!

I'm encountering this argument recently...some say the piping which feeds only one sprinkler is considered an "arm-over," therefor eliminating the requirement. Albeit, I don't agree with the way either definition is written (branchline or arm-over).

Reply
Mark S
4/5/2021 10:13:54 am

I would counter that with: Arm-overs that are more than 2' long (cumulative length of horizontal pipe) are required to be supported (steel pipe).

Reply
Daniel morris
5/8/2022 04:12:06 am

This is a little late I realize but better late than never. What I figured when interpreting this matter is simple physics. You have to brace a sprig over 4’ because gravity is working against you so that if it were to go off the pressure along with the force of gravity would pull the sprig down affecting the operation of the sprinklers ability to do what it’s supposed to do. Where as a drop on the other hand would be reversed and gravity would be the very force holding it in place therefore it wouldn’t need to be braced because no matter how long if the drop were to go off it wouldn’t affect its ability to operate properly. Of course this is just speculation or interpretation of my own but I am also dealing with this issue and peoples opinions on the matter vary. I hope this helps clear up some confusion on the matter but the rule on drops and bracing seems nonexistent because it is. I assume there’s nothing on the matter because you wouldn’t right an explanation as to why there isn’t a rule.

Reply



Leave a Reply.

    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top ​April 2023 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A117.1
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Daily Discussion
    Design Documents
    EN 12845
    Explosion Protection & Prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable & Combustible LIquids
    FM Global
    Human Behavior
    IBC
    ICC-500
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 30B
    NFPA 33
    NFPA 400
    NFPA 409
    NFPA 415
    NFPA 495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3 600 01
    UFC 3-600-01
    UFC 4-021-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    Fire Protection PE Exam Prep
    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2023 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • THE TOOLKIT
    • SUBMIT AN IDEA
    • BACKFLOW DATABASE*
    • CLEAN AGENT ESTIMATOR*
    • CLOUD CEILING CALCULATOR
    • DOMESTIC DEMAND*
    • FIRE FLOW CALCULATOR*
    • FIRE PUMP ANALYZER*
    • FIRE PUMP DATABASE*
    • FRICTION LOSS CALCULATOR
    • HANGER SPACER*
    • IBC TRANSLATOR*
    • K-FACTOR SELECTOR*
    • NFPA 13 EDITION TRANSLATOR ('19 ONLY)
    • NFPA 13 EDITION TRANSLATOR ('99-'22)*
    • LIQUIDS ANALYZER*
    • OBSTRUCTION CALCULATOR
    • OBSTRUCTIONS AGAINST WALL*
    • PLUMBING FIXTURE COUNTS
    • QUICK RESPONSE AREA REDUCTION
    • REMOTE AREA ANALYZER*
    • SPRINKLER DATABASE*
    • SPRINKLER FLOW*
    • SYSTEM ESTIMATOR*
    • TEST & DRAIN CALCULATOR
    • THRUST BLOCK CALCULATOR
    • TRAPEZE CALCULATOR
    • UNIT CONVERTER
    • VOLUME & COMPRESSOR CALCULATOR
    • WATER STORAGE*
    • WATER SUPPLY (US)
    • WATER SUPPLY (METRIC)
  • UNIVERSITY
    • JOIN
    • CATALOG
    • CONTENT LIBRARY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE Prep Series
    • PE 100-Day Marathon
  • LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT