MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Required Location for Waterflow Notification?

2/18/2019

8 Comments

 
I understand there's a tradition of locating a horn/strobe or other exterior waterflow notification appliance on the exterior of the building, but where is it required and is a location stipulated?

Posted anonymously by a member for discussion. Discuss this  | Subscribe
8 Comments
James
2/18/2019 10:16:55 am

It is usually in your local building code. For example, it is located in the 2015 international building code chapter 9, 903.4.2. Check the exceptions to see if you need one.

Reply
Patrick
2/18/2019 10:43:08 am

James is correct. It is also in the same section of the fire code, and requires an approved audible device located on the exterior of the building in an approved location. In my jurisdiction, the AHJ typically requires it on the address facing wall of the building.

Reply
Raul Vasquez link
2/18/2019 11:31:17 am

Above the FDC. Some AHJ are replacing bells with horn strobes and color coding the lens to blue or red if the clear is being used to signify FACP annunciator location.
- mostly Chicago suburbs

Reply
Jon Nisja
2/19/2019 07:09:07 am

From an AHJ perspective, I have always preferred that the waterflow alarm be both audible and visual (but it doesn't need to be a "strobe" light). The device should be located above and in close proximity to the fire department connection. This assists responding firefighters in locating the FDC.

Reply
Scott McCormick
9/5/2022 07:22:39 am

Do you really want an audible alarm at the FDC? i would feel bad for the Engine Operator who is going to be close to this alarm and will have a headache after an hour. I feel a strobe of flashing light

Reply
David C
2/19/2019 08:50:00 am

As indicated above the location(s) and types of these devices are dependent on the AHJ where I am we have 5 AHJ and each has some requirement that's different.

Reply
Franck Orset
2/19/2019 10:51:43 am

Is it for a building located within a city (outside wall of a supermarket, office building...) or for buildings inside an industrial facility ?

In the first case, it is interesting to have this external alarm (gong) as it will indicate that there is a fire and people passing by can alert the fire department. In addition, the fire department may use the gong to quickly determine which sprinkler system is concerned and where to possibly connect to the FDC.

In the case of an industrial building, it could be the same (gives a local alarm and people can alert accordingly) but might not be absolutely necessary where the plant is occupied 24/7 and alarms from the sprinkler systems are reported to a constantly attended location.

In NFPA 13 (2019 Edition), it is indicated : §A.16.11.1.1 Outside alarms might not be necessary where the sprinkler system is used as part of a central station, auxiliary remote station, or proprietary signaling fire alarm system, utilizing a listed audible inside alarm devices.

Regarding the position, it is only indicated (§A.16.11.1.2) that the alarm apparatus should located and installed so that all parts are accessible for inspection, removal and repair and that the motor gong bell mechanism should be protected from weather related elements such as rain, snow or ice. It should also be protected from other exposures, such as birds, small animals that could make a nest in the bell, mechanical damages, possible vandalism...
There is no requirement in the standard to provide it close to the FDC, but it could be a local requirement from the AHJ.

Reply
Aaron Easter
9/7/2023 03:45:57 pm

I believe the exterior horn is nessisary. As a FD Driver, the extra help locating the FDC at a 3am fire was helpful.

There has been some debate with my peers on notification requirements INSIDE structures that only require "deticated function" (etc., waterflow) moitoring. 907.5 says...Systems while 903.4 speaks on cmponents

907.5 Occupant Notification Systems
A fire alarm SYSTEMS shall annunciate at the fire alarm control unit and shall initiate occupant notification upon activation, in accordance with Sections 907.5.1 through 907.5.2.3.3. Where a fire alarm system is required by another section of this code, it shall be activated by:
1. Automatic fire detectors.
2. Automatic sprinkler system waterflow devices.
3. Manual fire alarm boxes.
4. Automatic fire-extinguishing systems.


903.4 Sprinkler System Supervision and Alarms
Valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and water flow switches on all sprinkler systems shall be electrically supervised by a listed FIRE ALARM CONTROL UNIT.
Exceptions:
(1-7)

FIRE ALARM CONTROL UNIT. A system COMPONENT that receives inputs from automatic and manual fire alarm devices and may be capable of supplying power to detection devices and transponder(s) or off-premises transmitter(s). The control unit may be capable of providing a transfer of power to the notification appliances and transfer of condition to relays or devices.

FIRE ALARM SYSTEM. A system or portion of a COMBINATION SYSTEM CONSISTING OF COMPONENTS and circuits arranged to monitor and annunciate the status of fire alarm or supervisory signal-initiating devices and to initiate the appropriate response to those signals.

Love to hear how others interpret this: Sorry to high jack the thread: /

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT