MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Required Duration for Secondary Water Supply?

1/26/2023

8 Comments

 
What is the required duration for a Secondary Water Supply within Seismic Zone?

IBC Section 403.3.3:
​
"The secondary water supply shall have a duration of not less than 30 minutes as determined by the occupancy hazard classification in accordance with NFPA 13."

Does this mean minimum 30 minutes, with the gpm/demand determined by NFPA 13?

Or the minimum duration is also determined by NFPA 13, such that the secondary water supply could require an even longer duration, like 60 minutes?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Anthony
1/26/2023 08:11:47 am

Per NFPA 13-2016:

Table 11.2.3.1.2 Hose Stream Allowance and Water Supply
Duration Requirements for Hydraulically Calculated Systems

Go check out that table there are waterflow minimums required for the secondary water supply. This is usually used for sizing you tank. The two times listed there differentiate between monitored systems and non-monitored systems see: NFPA 13-16 11.2.3.1.3

Eg for light hazard 30 min x ((1500sqft x 0.1 gpm/sqft) + 100gpm) = 7500 gallons required for a tank in this example

Reply
Glenn Berger
1/26/2023 08:28:59 am

As I re-read and re-read your question and I am understanding why this question was asked to the group.

I would recommend using NFPA 13 to determine the required water flow and the required supply duration.

Reply
Todd E Wyatt
1/26/2023 09:03:50 am

IBC 403.3.3 (2021) is the subsection for “Section 403 High-Rise Building” (HRBs) so the 30 minute duration of the secondary water supply is only required for HRBs :

Section 403 High-Rise Buildings
403.3 Automatic Sprinkler System
Buildings and structures shall be equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 and a secondary water supply where required by Section 403.3.3.
403.3.3 Secondary Water Supply
An automatic secondary on-site water supply having a capacity not less than the hydraulically calculated sprinkler demand, including the hose stream requirement, shall be provided for high-rise buildings assigned to Seismic Design Category C, D, E or F as determined by Section 1613. An additional fire pump shall not be required for the secondary water supply unless needed to provide the minimum design intake pressure at the suction side of the fire pump supplying the automatic sprinkler system. The secondary water supply shall have a duration of not less than 30 minutes as determined by the occupancy hazard classification in accordance with NFPA 13.

Otherwise, the applicable chapter for automatic sprinkler systems (ASPS) is ...

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.2 Where Required
903.2 Where Required
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.

... which references NFPA 13 as the standard for ASPS installation, classifying the “Hazard”, and development of “hydraulic calculations” :

Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3.1 Standards
Sprinkler systems shall be designed and installed in accordance with Section 903.3.1.1 unless otherwise permitted by Sections 903.3.1.2 and 903.3.1.3 and other chapters of this code, as applicable.
903.3.1.1 NFPA 13 Sprinkler Systems
Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Sections 903.3.1.1.1 and 903.3.1.1.2.

The only reference to “Secondary Water Supply“ in “Chapter 9 Fire Protection and Life Safety Systems” is as follows “

Chapter 9 Fire Protection and Life Safety Systems
Section 904 Alternative Automatic Fire-Extinguishing Systems
904.11 Automatic Water Mist Systems
904.11.1.4 Secondary Water Supply
Where a secondary water supply is required for an automatic sprinkler system, an automatic water mist system shall be provided with an approved secondary water supply.

The applicable edition of NFPA 13 per 2021 IBC is the 2019 edition. The 2019 NFPA 13 includes an entire chapter (Chapter 5) to “water supply” but this chapter does not reference “secondary water supply”.

5.1 General.
5.1.1 Number of Supplies.
Every automatic sprinkler system shall have at least one automatic water supply.

ENHANCED CONTENT
It is not necessary for a single water supply source to be sized to account for the simultaneous operation of all systems. The water supply must be capable of meeting the most hydraulically demanding area of the systems. If a building’s size requires that it have three separate sprinkler systems, each system is not required to be connected to its own water supply. Instead, the water supply must be capable of meeting the demands of the hydraulically most demanding areas of the three systems. NFPA 13 assumes that only one fire will occur in a building at any given time and that the sprinkler system will control the fire before it spreads to adjacent portions of the building.

Chapter 5 includes (13) references to “water supply” but (0) referencing secondary water supply”.

Reply
Dan Wilder
1/26/2023 09:18:02 am

If the building needs a secondary water supply, I recommend looking at the volume from the standpipe calculations in addition to the sprinkler.

Durations would be per
NFPA 13 - 19'
Durations as shown in the storage tables (4.3.1.7.1 goes up to 120 minutes in some cases for example)
8.7.9.5 - for exposure protection
9.3.15(7)/19.4.4 - for window sprinklers based on the wall rating
19.3.3.1.2 - for Light, OH, EH
20.12.2.6 - for storage*

*There are several storage subsections that have individual duration requirements.

NFPA 14 - 19' - 9.1.4.1 - 30 minute duration

Reply
COLIN LUSHER
2/1/2023 12:04:57 pm

I just dealt with this in a long battle with our AHJ, and we won the dispute, see my other comment. IBC 403.3.3 specifically states that the secondary supply is only for the SPRINKLER system. In fact, section 403.3 only relates to "Automatic Sprinkler System". Standpipe systems do not need to be accounted for in this calculation.

Reply
Colin Lusher
2/1/2023 12:25:06 pm

I just dealt with this issue in an ongoing battle with our AHJ, and we ended up winning the dispute and convincing them that our interpretation was correct.

Your second statement is correct, the duration needs to be per the occupancy classification of NFPA 13, with a minimum duration of 30-minutes (which coincides with NFPA 13 light hazard min duration).

One thing we did discover by conferring with the AFSA experts was that the "hose stream" is NOT referring to outside hose stream, but rather to the sprinkler system small hose connections covered in chapter 8.17.5 of NFPA 13-2016, used for mop up operation, with demand covered by 11.1.6.3 (50gpm or 100gpm). Since most sprinkler systems do not utilize these small hose connections, the secondary supply size on most projects can be calculated with 0 gpm hose demand. If the outside hose is supplied by the fire pump (rare in my experience), then that is a different story, and it would then be practical to include this in the tank calculations where that is the case.

NFPA 14 standpipe system demand need NOT be included either, as section 403.3 of IBC only relates to "Automatic Sprinkler System" per the title, and 403.3.3 only states that the supply should be for the sprinkler system.

Reply
Matt Kindall
5/18/2023 12:39:39 pm

I am struggling with a review for this very situation, and hoping someone can help me understand. I work for a small city in Oregon and we have a new high-rise courthouse being built (the first in our town, and the first I've ever reviewed). The building will be six stories and a basement, with the 30,000 gallon auxilliary water tank installed in the basement. I am having a really hard time understanding the tank sizing requirement for this. Is the tank based on the most demanding remote area gpm requirement, the combined remote areas, or just off of (NFPA 13 2016) Table 11.2.3.1.2? So far they have only submitted the basement for this phased submittal, which includes four separate remote areas, and I'm sure there will be others in the floors above. I'm a bit out of my element here and would love any help y'all can provide.

Reply
Colin Lusher
5/21/2023 05:04:42 pm

Matt, assuming the auxiliary supply is to satisfy IBC, the required duration is based on most demanding remote area flow requirements (based on hydraulic calculations or a conservative estimate), and the duration for the supply is per NFPA 13 for the hazard being protected (e.g. 30 minutes for Light Hazard, 60-90 minutes for Ordinary Hazard, etc.). The 30k gallon tank is fairly typical for Ordinary Hazard Group 2 with no area reduction used. The tank size can be reduced down if Quick Response area reduction or other flow reduction methods are used, but this size sounds pretty safe for your application.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT