Remove a Redundant Fire Pump from Service?

3/13/2020

11 Comments

 
My employer owns several properties in with 2 fire pumps that are discharging to the same loop. The pumps were there when we bought the buildings.  In most cases there is one electric and one diesel, but in other cases there are two diesel fire pumps.

The power purveyor is not considered unreliable by any criteria.

Is there anything you can think of that would prohibit me from decommissioning a redundant pump for the purpose of saving on maintenance costs?

Each pump is 2000 gpm and the greatest demand on the loop is less than 3,000 gpm. The pumps are provided in parallel. 

​​​​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Scott
3/13/2020 10:04:00 am

There might be an insurance company requirement above the normal fire/building code requirements. I used to work for a large insurance company and once buildings got to a certain insurable value, they would require redundant pumps with separate power supplies.

Reply
Efi Sher
3/13/2020 10:10:43 am

2 diesel pumps doesn't make sense.
One electric and diesel is OK.

Reply
sean
3/13/2020 01:13:13 pm

you still get redundant pumps.

RJ
3/13/2020 10:14:13 am

The maintenance costs on your existing fire pump would be far less then you would spend if you would have to replace it. Penny wise and dollar foolish. ( Not calling anyone foolish, but that is how he saying goes.)

Reply
Joseph
3/13/2020 10:17:22 am

Consider consulting a maintenance and reliability professional to determine the availability and reliability of your system. Any reported failures or periods of unavailability could help derive the reliability of each pump. Note, consider including lead time for parts and repair personnel schedules in the periods of unavailability to calculate "operational availability". If the respective reliability calculations for each individual pump drops to 70%, having them in a redundant configuration still achieves a system reliability of 91% assuming the switch from one pump to the next is 100%. Compare the availability and reliability the owner desires against the cost of liability and cost of maintenance on the additional pump.

Reply
Jesse Cecil
3/13/2020 10:26:16 am

Undoubtedly an insurance requirement. If the properties were designated as High Protected Risk, there would most likely be 2 pumps, even two diesel pumps - though the more common arrangement is primary electric and secondary diesel.

Before working as a design manager, I was an insurance HPR engineer for 13 years. This arrangement is very common.

I'm curious as to what the occupancy is and what the extant AS protection is. J

Reply
Paul Pinigis link
3/13/2020 10:32:37 am

This is most likely an insurance company requirement.

I would not recommend removing one because the maintenance costs should not be very high, but the cost to replace the remaining one in the event of a failure would be very high. The maintenance is a small price to pay for peace of mind.

Reply
Chris
3/13/2020 11:26:46 am

The pump is 2000gpm and the greatest demand in the system is 3000gpm?
Than doesn't tell me much.
I heard so many people referring to a pump capacity as 20HP or 30HP.
The main thing when addressing a fire pump is the rated pressure and the rated flow.
Since any fire pump must deliver 65% of the rated pressure at 150% of the rated flow we don't know where is this 2000gpm is located on the graph.
When selecting a pump you want to pick a point on the graph somewhere between 90% and 130% of the rated flow and enough pressure to overcome the gap between the system demand and city's water pressure.
If your pump is rated at 100psi and 2000gpm you may be happy with the 3000gpm but you will only get 65psi at that flow so make sure both values for flow and pressure are in the right area on the graph.
Otherwise your insurance provider has a file on these systems (pumps) and your owner must have signed up for that plus the right approvals were given by local A.H.J. (Factory Mutual of IAO most likely. They are the only ones who can approve the eventual change you are talking about.

Regards

Reply
Franck
3/13/2020 11:39:13 am

All the above comments are right

In addition to possible insurance requirements (depending on Total Insured Value), in particular for HPR locations, there are also many other possibilities.

One may be a change on the design of some systems that goes beyond the characteristics of just one pump.
Normally, the pump is to be sized upon the most demanding system. And if the most demanding system is close to 3000 gpm (which is a huge demand!) then the fire pump should be rated at 3000 gpm, not 2000. So maybe the change of commodity/occupancy required that 2 pumps are needed to meet the most demanding areas.

What is your activity for having such a demand ? Storage facility ?
Maybe the previous design for the previous owner is not suitable for your activities and your actual demands are lower than the designed for 3000 gpm ? Or maybe it is even higher and you need for sure 2 fire pumps !

In any case, having 2 pumps in service is a "gift" and I wouldn't get rid of it. More flexibility for maintenance (if one pump is out of service, you don't impair all your sprinkler systems at the same time) and as already indicated by others, it can save you a lot of money when you will need to replace one pump.

Not to mention that in case of fire, the probability to have both pumps not operating is much lower than having one pump not operating.

Reply
DTC
3/14/2020 06:23:30 pm

In addition to insurance I would say consult the AHJ in our area you are required to have redundant pumps if your pump is feeding multiple buildings.

Also until last code cycle we did not consider the electric company as a reliable source.

Reply
Kevin Green
11/15/2020 03:10:44 am

If a sprinkler system is installed in a business premise must it be maintained or can it be redundant.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT