Relief Valve for Wet Pipe Sprinkler Systems?

5/3/2019

10 Comments

 
NFPA 13 (2016 Section 7.1.2 or 2019 Section 30.3.1) requires a relief valve on all wet pipe systems. The only exemption is where air reservoirs are installed to absorb pressure increases, then a relief valve isn't required.

This seems straightforward but I don't recall seeing independent relief valves on the far majority of the wet pipe systems I've come across. How is this requirement typically met from a design standpoint? Am I missing something or looking in the wrong place?

Posted anonymously for discussion. Discuss This | Submit a Question | Subscribe
10 Comments
Wayne Ammons
5/3/2019 06:54:19 am

Prior to the 2010 edition of NFPA 13, only gridded wet pipe systems were required to have this relief valve. Tree systems typically have more trapped air than gridded but with air venting becoming more popular for mitigating corrosion (also required with the 2016 edition of NFPA 13), there should be less trapped air in all wet pipe systems. This can cause increased pressures within the system due to water fluctuations, solar heating, etc.

I typically include the relief valve on the inspector's test on the riser. You can buy an inspector's test and drain assembly (i.e. AGF) or piece it together with individual components.

Reply
Jim McHugh link
6/4/2019 11:55:59 am

Hi Wayne,
Prior to 2010 you also needed to install a relief valve downstream of all pressure reducing valves. One of the issues is code recommend 1/2" valves in one area and 1/4" in another.
This was cleaned up in the 2010 edition.
Thank for mentioning our AGF TESTanDRAIN valves. Our models 1011A and 2511A included a UL/FM pressure relief valve and drainage piping.
Thanks, Jim McHugh

Reply
TJ Jones III
5/3/2019 10:16:39 am

Your Ready Risers can come with a Relief valve on the Test and Drain. You can also order them in an assortment of settings. 175 PSI is the standard for them so you have to plug them during testing.

Reply
Franck
5/3/2019 10:23:57 am

As indicated above, this is quite a new requirement (less than 10 years) and is not retroactive. So many systems are installed without this piece of equipment.
But it is not a bad requirement. Not only for possible air trapped in the system (and corrosion issues) as indicated by Wayne, but also for possible pressure built-up in some systems.
Some sprinkler systems are regulated at quite a high pressure. And the pressure downstream the ACV remains at a high level, whatever the possible fluctuations on the pressure upstream on the water supply side.
If the building has high difference of temperature between day and night (heated by the sun under the roof, for example) or for systems running close to hot equipment, the pressure might increase even more (this is a closed system and a fluid that is heated will expand) and could reach very high levels, sometimes up to 175-200+ psi... which is not good for long term operations on sprinkler systems (sprinkler heads are normally rated at 175 psi).
This is when this pressure relief valve is interesting, even for old systems.

Reply
Ivonn
5/3/2019 10:29:30 am

Relief Valve are require in a wet system agree with section 8.1.2 NFPA 13 Ed.2019 in each system except where have an air reservoirs like you said, typically the inspector, test and drain have a 1/2" relief valve and you comply with that point.

Reply
StephenJ
5/3/2019 11:18:13 am

I just wanted to point out that the requirement you pointed out are different. Section 30.3.1 in the 2019 version of NFPA 13 is a requirement specific to merchant vessel systems. Chapter 30 is titled marine systems.

Section 7.1.2 in the 2016 version is now 8.1.2 in the 2019 version. The intent of 8.1.2.1 is to prevent pressure in wet pipe systems from exceeding 175 psi for sprinkler systems or the maximum working pressure. You would have to use a little judgment here and evaluate the supply to determine the likelihood of exceeding this pressure.

Reply
David Toshio Williams, PE/FPE link
5/6/2019 11:24:57 am

Before this change in the Code we were the A/E firm on a project fairly near a city water system pump station, the pressure pulsations from the pump station would gradually build in the sprinkler system until the heads would blow. In the end the system check valve was drilled with a small hole to relieve pressure (and the City checked how it was operating their pumps). (Back in the day we only provided a single check valve on the water service connection).

Today we would have called for the installation of the relief valve and that would have taken care of this issue.

I have seen more than one "new" installation where the relief valve has been skipped even if we show it in the design details we call for in a performance design project. I think the trades are still learning about this 10 years later!

The test connection with 3/4 inch relief valve tapping seems to be the way to go.

Reply
Jon Paton
5/17/2020 10:22:28 pm

My system was poorly designed. Static fire water pressure is constantly at or above the relief valve rating. This causes the valves to constantly leak. I can't rebuild the fire system. Can I put two valves in parallel or in series to reduce pressure? Would that invalidate the system?

Thank you

Reply
Jim McHugh link
5/18/2020 07:39:42 am

Hi Jon,
You can get different pressure ratings on the pressure relief valves. The pressure marked on the valve indicates an operating range. An example would be a 175 PSI valve begins opening at 90% of its range so it would begin opening at 158 psi. Also the valves are designed to be fully closed once the pressure drops below 80% of it indicated range or 140 psi. You may need to simply swap out the valve you have for a different pressure such as 205 psi or 225 psi. If you have other technical questions please give me a call at 610-240-4900 Thanks Jim McHugh

Reply
Tom Molnar
2/15/2022 12:04:10 pm

In the previous conversations, it appears that the two separate requirements for "Relief Valves" (Sect 7.1.2 in NFPA 13 2016, which first appeared in the 2010 edition) and " Air Venting" (Sect 7.1.5 in NFPA 13 2016, which first appeared in the 2016 edition) have been used interchangeably as the same item, but are two separate requirements - one for pressure relief (7.1.2) and one for air relief (7.1.5) requiring both items at each sprinkler floor control valve assembly. Please let me know if I am wrong.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT