A high rise building has pressures of 9 kg/cm^2 (128 psi) at its lowest floor. What does NFPA 13 require in regards to the high pressure or standard industry practice suggest to reduce pressure at the lowest levels? Should an orifice plate be used?
Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
7 Comments
Darin
9/6/2017 08:12:08 am
I'm getting these emails because I'm studying for the PE test, but I don't know if these are questions designed to help us study or if they are from actual people with actual questions. Please let me know. Thanks.
Reply
These are part of the Daily Discussion series we started a couple weeks ago to help answer questions and spur discussion; they are actual questions from actual people.
Reply
Patrick Turner, P.E.
9/6/2017 08:59:00 am
With regards to the Sprinkler System, most components on a sprinkler system are listed up to 175psi (mainly sprinklers). There are High Pressure Sprinklers available that are listed up to 300psi working pressure. In this case, since pressure at the lowest level is 128psi, your sprinkler systems should be fine and would not need any Pressure Regulating Valves. However, Standpipe Systems are a different animal. If your Standpipe requires a 1.5" Hose Connections, if Residual Pressures exceed 100psi at the required flow then NFPA 14, 2016 Edition Section 7.2.3.1 requires an approved Pressure Regulating Device be provided to reduce the residual pressure to 100psi or less. The Pressure Regulating Device is not required if you have 2.5" Hose Valves or 2.5"x1.5" Reducers at the hose valves (per Section 7.2.3.1.1). Pressure Regulating Devices are only required on 2.5" Hose Valves if the Static Pressure exceed 175psi (per Section 7.2.3.2). Therefore, in your case, if you have 2.5" Hose Valves or 2.5"x1.5" reducers on a 2.5" Hose Valve, no Pressure Regulating Device is required since your Static pressure is less than 175psi. If you have 1.5" Hose Valves then you would need a Pressure Regulating Device to get the residual pressure below 100psi at the required flow at each 1.5" Hose Valve.
Reply
Darin
9/6/2017 09:04:28 am
Thanks Joe. Regarding the original question, the answer is pretty complicated with a lot of if/then scenarios. Is the 128 psi on the discharge side of an existing fire pump? Of is that city static?
Reply
There is a lot to this issue, as you and Patrick have both alluded.
Reply
David
9/6/2017 09:54:21 am
Both of Darin and Patrick's comments are spot on. There would need to be much discussion on the specific project to verify the actual pressures on the system side.
Reply
CJ
9/6/2017 10:17:56 am
Going out on a limb, but I believe that pressure MUST be greater than 128 psi at the lowest floor for a high rise.
Reply