MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Recall in Shaft for Machine Room-Less Elevators?

4/12/2019

5 Comments

 
We have a machine room-less elevator where the motor is located on top of the elevator cab and the elevator equipment is located within the elevator shaft.

NFPA 13 (2016) 8.15.5.3(2) allows sprinklers to be omitted from the hoistway of "traction elevators" where the hoistway is "protected by smoke detectors, or other automatic fire detection installed in accordance with NFPA 72", and several other requirements.

NFPA 72 (2016) 21.3.3 states that only the elevator hoistway and elevator lobby smoke detectors or other automatic fire detection (as permitted by 21.3.9) shall be used to initiate Phase I Emergency Recall Operation. 

NFPA 72 (2016) 21.3.9 states that if "ambient conditions prohibit installation of automatic smoke detection" that other automatic fire detection initiating devices shall be permitted.

What type of ambient condition in an elevator shaft would qualify as prohibiting smoke detection? 

I understand smoke detectors in elevator hoistways can cause nuisance alarms (NFPA 72 2016 A.21.3.9) and are very difficult to test and replace within elevator shafts, so in my opinion a heat detector would be better for elevator recall in the shaft if it's allowed by code.

Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
5 Comments
Donovan S.
4/12/2019 10:24:49 am

The are no Smoke detectors UL list to be installed in elevator pits or shafts. If sprinkler head is below 24", you do not have to shunt trip the power. However to comply with NFPA 72 you have to recall the elevator(s) to the alternate floor. That can be done with a heat at the top of the shaft set for recall only. If above 24" then you do it all (Recall and Shunt). You can also achieve the recall via a water flow detection. Most ppl think that the elimination of sprinkler head(s) in the elevator(s) shaft has to do with electrical. This is wrong, is has to do with the emergency breaks on the elevator. If they become wet, they may not work properly.

Reply
Ronnie Morales
4/12/2019 11:16:17 am

Statement from NFPA 72 (16) Handbook

Some elevator lobbies, hoistways, and machine rooms are not suitable environments for the installation of spot-type smoke detectors. Dust, dirt, humidity, and temperature extremes may exceed the operating parameters of the smoke detector. A spot-type smoke detector installed in the elevator lobby of an unheated parking garage would likely experience problems due to vehicle exhaust, dust, dirt, humidity, and temperature extremes. The intent of 21.3.9 is to prevent nuisance alarms from smoke detectors installed in such areas and unnecessary initiation of elevator Phase I Emergency Recall Operation.
Another type of fire detector may be substituted for a smoke detector where the authority having jurisdiction or another code requires detection in an area with ambient conditions unsuitable for a smoke detector. Also refer to 21.3.8.

Reply
Mike R
4/14/2019 01:43:10 pm

This is a perfect example of when you need to use some engineering judgment and good practice in addition to what is black and white in the book. It is true when there are no combustibles in a non-combustible shaft you want no sprinkler and no fire alarm detection in the shafts. However, when the controls and elevator equipment are in the shaft, the shaft itself becomes the machine room. Typically most elevator code officials will require some sort of detection at the top of shaft for this. A modern smoke detector at the top of a shaft (assuming conditioned, dry space) would be fine. If it not heated or an exterior elevator a heat detector would be best suited. I can't speak for every jurisdiction, but in Philadelphia the latest NFPA 13 is now in effect which allows no sprinklers in shafts OR machine rooms. Here elevator code takes precedence, and the code official wants nothing more than what is absolutely required, which in the case you mention above, would be a smoke only at the top of shaft.

Reply
Nguyen Nhat
4/15/2019 09:56:37 pm

Following SFPE hand book, Elevator codes generally don't require any sprinkler protection or detection at the top of shafts since the fuel load is insufficient to actuate a sprinkler or affect persons in the cars. So, the smoke detector is better than heat detector in this situation.

Reply
Will Hunter link
12/29/2020 08:21:13 am

I have seen NJ require smokes at the top of any hoistway motors, also one in the pit for trash.
I never assume nuisance over safety, and this can be a real nasty change order if the elevator company is difficult. (they all are).

AHJ doesn't care about nuisance alarms, they care about people smoking in the cars, setting the cars on fire, motors overheating and catching fire, and trash at the bottom under the lobby in the pit catching fire.

Regards,


Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT