Are office privacy pods such as Framery O, Q, and Q2 required to have sprinkler protection in the United States?
Their literature says there is no need for installing sprinklers within them in Europe? Here is a link to an example: frameryacoustics.com Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Thomas Jones III
4/23/2020 09:40:48 am
For the Q2, yes, any obstruction over 4'-0 requires a fire sprinkler. For your other options I would say yes as well, especially if they cannot move and do not count as furniture.
Reply
Donna Kimler
4/23/2020 10:35:21 am
Yes, to all. The small one would be treated like a closet. You could possibly state a case that they are furniture to the AHJ. As always, the AHJ would have the final say.
Reply
Mike L
4/23/2020 10:51:46 am
We deal with these a lot in the modern open-office concept in NYC. We apply the requirement of IBC Section 903.3.3. Obstructed Locations "....automatic sprinklers shall be installed in or under covered kiosks, displays, booths, concession stands or equipment that exceeds 4 feet in width."
Reply
Jonathan Joseph
4/23/2020 11:07:16 am
I would have to say that is an occupied compartment and obstruction, so yes. I would treat this as a light hazard Tenant Improvement if there is an existing system.
Reply
Jesse
4/24/2020 08:53:25 am
In the US, each AHJ is autonomous. So each would have its own final say. That being said, this is clearly an obstruction to ceiling level sprinklers, and would require protection.
Reply
Bruce Verhei
4/27/2020 11:15:36 am
Good morning.
Reply
Ck
4/27/2020 02:18:40 pm
This will depend on what the AHJ chooses to enforce. This issue has been coming up as new and existing office buildings continue to add these. For me, it is an easy call if it is over 4 feet, and we have looked at everything else on a case by case basis.
Reply