PE Problem #72

9/12/2018

10 Comments

 
What is the foam friction loss (in head per 100 ft) and flow velocity for a 4:1 expansion foam flowing 130 gpm in a 2-1/2" schedule 40 pipe (with a c-factor of 100) most nearly?
a. 4.5 ft head/100 ft pipe and 4.75 ft/s
b. 8 ft head/100 ft pipe and 4.75 ft/s
c. 10 ft head/100 ft pipe and 4.5 ft/s
d. 30 ft head/100 ft pipe and 5.5 ft/s"

Solution | Posted 09/13/18
So much for trying to stump you all. As several people point out in the comments, the tables used to write this problem is not in the required reference material, so this problem needs to be scratched. NFPA 11 does address expanded foam velocities (see NFPA 11-2016 Figure A.5.2.6.2(a) on page 11-54).

On a side note, had the foam been a 1:1 expansion and Hazen-Williams been applicable, it could be solved by the Hazen-Williams formula or via the Hazen-Williams nomograph of page 1394 in the 5th Edition of SFPE.

Great discussion and feedback, keep up the great work everyone.

​                                      - Joe
10 Comments
Colleen
9/12/2018 11:08:02 am

I'm really confused on how to solve this...

when I used Hazen-Williams (inside diameter or 2.469"), I got 0.0900 psi/1ft, then multiplying by 2.317 ft per 1 psi, and 100, I got 20.858 ft of head/100 ft...so I guess I would guess either C or D??

Did anyone else figure this out? I've never done a calculation specific to foam systems.

Reply
KC
9/12/2018 11:09:45 am

A. Used figure 4-5.A-1 in SFPE, 4th. Not sure if that's in the 5th. Meyer 18, pg 272 solution references 4th, but not 5th.

Reply
John Frank
9/12/2018 02:11:46 pm

Colleen, you cannot use HW for this. KC found the correct figure in HFPE 4 but it is not in HFPE 5. HFPE 5 says to consult NFPA 11 for the figure. Therefore it cannot be directly answered with HFPE 5. However, the fact that HW or Darcy cannot be used is still important to know. The figure in NFPA 11 (the same one KC found in HPFE 4) is the only want to do it that I know of. I have never seen an actual equation. This is only done with subsurface injection and forcing foam makers where you have expanded foam flowing through pipes. Unexpanded (1:1) foam solution (by far the most common situation) uses HW and foam concentrate (not mixed with water) uses Darcy or manufacturer's charts.

Reply
Colleen
9/12/2018 02:34:09 pm

Thank you for the explanation! That explains why I was unable to solve the problem.

Reply
John Frank
9/12/2018 02:45:54 pm

If anyone wants real photos of what these systems look like, e-mail me at [email protected]. I can't paste a photo into the comment block.

Reply
Brian Jarvis
9/12/2018 03:54:06 pm

Hello JOHN,
Good to see you are helping us on here, thank you.

Reply
GD
9/12/2018 03:21:12 pm

A per SFPE Handbook Ph. 4-151 (4th edition)

I doubt this question would be on the test since I don't think this figure is in the 5th edition

Reply
MHK
9/12/2018 07:26:58 pm

Clause 10.7.1 of NFPA 11 (2016 ed.) says that foam solution shall be considered to have the same hydraulic characteristics as water. Since the expansion ratio 4:1 is in the rage of low expansion, I guess the caluse 10.7.1 can be valid for the problem. By the way, I simply calculated the velocity as V=Q/A, and this brought me with 8.72 ft/s, which seems not close to any of the choices. Can anyone tell me how to calculate the velocity?

Reply
Pari
9/13/2018 12:44:01 am

I have a hard time even with the mention figure to get the right answer
Foam velocity is in p 4-152 sfpe book but is not easy to find the answer
Probably with higher flow and lager pipe sizing these figures should be useful.

Reply
John Sternitzke link
9/15/2018 12:23:24 pm

Hi Joe, would somebody be able to send me (i dont have SFPE 4) a copy of Appendix figure 4-5.A.1, p-451 and 4-5.A.3 p4-152, I have NFPA 11, I read John Frank comment, a I just want this if it is not too much trouble.

Thanks.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT