What should I do about a sprinkler contractor who insists that rooms of dedicated Ordinary Hazard occupancy (storage, janitors, mechanical etc.) within an otherwise Light Hazard occupancy building can be protected as Light Hazard?
NFPA 13 clearly provides direction for adjacent and multiple hazard classifications. I think Chapter 5 and 11 (and common sense) are clear on this. Classroom Labs are even another matter that NFPA has addressed. Do you all run into this "it's all light hazard" belief as well? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Mike L
1/16/2020 09:05:18 am
We run into this situation very often. We design the sprinkler heads for the Storage areas as Ordinary Hazard (reduced head spacing with a density of 0.15 gpm/sf) but with a light hazard (30 minute) water supply.
Reply
Julianne
1/16/2020 10:20:49 am
You are right, the sprinkler contractor is wrong. The AHJ will tell them the same thing; give them a call.
Reply
"What should I do about a sprinkler contractor who insists that rooms of dedicated Ordinary Hazard occupancy (storage, janitors, mechanical etc.) within an otherwise Light Hazard occupancy building can be protected as Light Hazard?"
Reply
Nhat Nguyen
3/30/2020 10:05:52 pm
Dear Collin,
Reply
Nhat,
Nhat Nguyen
3/31/2020 08:18:21 pm
Dear Colin,
Max
1/16/2020 11:38:27 am
It is also worth noting in a remote area such as this the hose streams for the higher hazard must be included in the hydraulic calculation.
Reply
Henry S.
1/16/2020 12:06:11 pm
While most sprinkler contractors I work with are generally up on code or at least are open to being pointed out where they are wrong (I catch a lot of common, but unintentional mistakes). But as Colin said, I also get a lot of "that's the way we've always done it." Julianne brings up an interesting point too about calling the AHJ. I have rarely done that, but I may consider that more often, especially when I already have a working relationship with that AHJ, since they are the ones with the teeth. Some AHJ's are very knowledgeable, while others simply are not. One AHJ told me he only has about 30 minutes to review any given submittal, so leaves a lot up to the integrity of the contractor. Some contractors are better than others as far as in-house continuing education in design (to me, a good indicator is if they active in NFSA or AFSA), and the increasing use of outside designers who may be in another geographical region can create problems. And there are too many ways to circumvent licensing requirements and ethics. Good discussion.
Reply