MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Omit Sprinklers in Small Stadium Water Closets?

9/8/2023

11 Comments

 
I'm reviewing a stadium project. The maximum available open vertical distance from WC stalls to the ceiling is 11.8-inches (300mm).

According to NFPA 13, table 10.2.7.2.2 (2019 Edition), the horizontal distance allowed from stall to sprinkler is 14.8-inches to 17.7-inches (375mm to 450mm). The width of the WC cubicle is 33.5-inches (850mm), so sprinklers must be provided in each cubicle.

This will result in many sprinklers in a wet area that has non-combustible or limited combustibility materials. Therefore, I've suggested sealing the cubicles up to the ceiling to create small WC rooms less than 55 sqft (5.1 sqm) to eliminate sprinklers. To my knowledge, there are no references that support this option for such an occupancy.

Is my suggestion to omit sprinklers in these small compartments consistent with the spirit of NFPA 13?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
9/8/2023 07:06:04 am

I'm sorry, but no.

What you're suggesting would work if these were bathrooms in an existing hotel/dormitory lodging/rooming houses and apartment buildings guest room bathrooms (NFPA 13 2016 D.1.1.3 - D1.1.8). But that doesn't apply to new structures, or common area bathrooms, or stadium occupancies.

If you made the toilet cubicles all separate rooms in a stadium, you'd need to sprinkler each one.

Reply
Chad
9/8/2023 07:21:21 am

Agreed. Even if you could, I would not skip coverage in a stadium, small or not if required.

Reply
Anthony
9/8/2023 07:58:41 am

As Pete says, that's not an acceptable interpretation of the code. you could "skip several stalls by placing the sprinkler directly over the divider and go every other stall.

Reply
Glenn Berger
9/8/2023 08:12:14 am

Concurring with the previous responses!

Reply
Dave Branson link
9/8/2023 08:32:32 am

One should not “game the codes” by closing the openings between stalls to make small compartments that would fall below room size minimums for requiring sprinklers. I recommend that you put the sprinklers in the currently-required locations. Placing them at the dividers to allow a sprinkler to cover two stalls would provide an economical solution.

Reply
Todd E Wyatt
9/8/2023 08:42:44 am

The scoping Code (e.g. 2021 IBC) determines the scoping requirements WHERE (903.2 Where Required) an automatic sprinkler system (ASPS) is required based on the building's Occupancy Classifications (OC) and/or based on "Specific Building Areas and Hazards" (e.g. Commercial Cooking Operations). The scoping Code references applicable standards, NFPA 13, NFPA 13D, or NFPA 13R, in HOW an ASPS is to be "designed and installed" (903.3.1 Standards).

"Exempt locations" per 2021 IBC for NFPA 13 Sprinkler Systems is listed in "903.3.1.1.1 Exempt Locations" and "903.3.1.1.2 Bathrooms". The only applicable "exempt location" that matches your description could be :

903.3.1.1.1 Exempt Locations
4. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.

Because of the toilet paper and paper towel supply & waste storage, most AHJs would not consider a toilet room in a stadium "with wholly noncombustible contents".

The referenced NFPA 13 by 2021 IBC is the 2019 edition. NFPA 13-2019 includes "9.2 Allowable Sprinkler Omission Locations" and lists (18) rooms/areas that an ASPS can be omitted but the situation you described is NOT included.

Reply
Todd E Wyatt
9/8/2023 08:43:52 am

REFERENCES
2021 IBC
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.3 Installation Requirements
903.3.1 Standards
903.3.1.1 NFPA 13 Sprinkler Systems
Where the provisions of this code require that a building or portion thereof be equipped throughout with an automatic sprinkler system in accordance with this section, sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in Sections 903.3.1.1.1 and 903.3.1.1.2.
903.3.1.1 NFPA 13 Sprinkler Systems
903.3.1.1.1 Exempt Locations
Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. Sprinklers shall not be omitted from a room merely because it is damp, of fire-resistance-rated construction or contains electrical equipment.
1. ​A room where the application of water, or flame and water, constitutes a serious life or fire hazard.
2. A room or space where sprinklers are considered undesirable because of the nature of the contents, where approved by the fire code official.
3. Generator and transformer rooms separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of not less than 2 hours.
4. Rooms or areas that are of noncombustible construction with wholly noncombustible contents.
5. Fire service access elevator machine rooms and machinery spaces.
6. Machine rooms, machinery spaces, control rooms and control spaces associated with occupant evacuation elevators designed in accordance with Section 3008.
903.3.1.1.2 Bathrooms
In Group R occupancies sprinklers shall not be required in bathrooms that do not exceed 55 square feet (5 m2) in area and are located within individual dwelling units or sleeping units, provided that walls and ceilings, including the walls and ceilings behind a shower enclosure or tub, are of noncombustible or limited-combustible materials with a 15-minute thermal barrier rating.

2019 NFPA 13
9.2 Allowable Sprinkler Omission Locations.

ENHANCED CONTENT
Section 9.2 contains a consolidated list of specific locations where sprinklers can be omitted. It was developed to consolidate all the specific allowances that were scattered throughout Chapter 8 of the 2016 edition.

Section 9.2 can be expected to be a very active part of NFPA 13 during future revision cycles. It is the one section where the basic principle of NFPA 13 — that sprinklers must be installed throughout the premises — is allowed to be altered. During each code development cycle, the Technical Committee on Sprinkler System Installation acts on inputs and comments seeking to “excuse” a specific portion of a building from the requirements of sprinkler protection due to a special situation. The case is typically made that, under certain conditions, the presence of sprinklers does not provide any greater protection, and the omission of sprinklers in these specific areas and spaces within a building should be permitted. (Section 9.3 identifies those spaces and conditions.)

It is important to note the following two points regarding Section 9.2:
1. It is imperative that when the elimination of sprinklers from a space based on this section is being considered, the space must comply exactly with the description and requirements found within the applicable paragraph(s). In other words, any deviation from the description in the applicable paragraph negates its application, and, as a result, the space must be sprinklered.
2. If a space is not specifically detailed in this section, it is intended to be protected by sprinklers under 9.1.1(1).

9.2.1* Concealed Spaces Not Requiring Sprinkler Protection.
9.2.2 Spaces Under Ground Floors, Exterior Docks, and Platforms.
9.2.3* Exterior Projections.
9.2.4 Dwelling Units.
9.2.5* Hospital Clothes Closets.
9.2.6* Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met ...
9.2.7 Cloud Ceilings.
9.2.8 Revolving Doors Enclosures.
9.2.10* Equipment Enclosures.
9.2.11 Noncombustible Vertical Shafts.
9.2.12 Noncombustible Stairways.
9.2.13 Elevator Hoistways and Machine Rooms.
9.2.14 Duct Protection.
9.2.15 Open-Grid Ceilings.
9.2.16 Drop-Out Ceilings.
9.2.17 Skylights.

Reply
Chris
9/8/2023 10:12:05 am

The omission of sprinklers in bathrooms under 55 ft² applies to bathrooms within dwelling units. In commercial spaced this does not apply, and 100% of the building is required to have protection, except where omissions are allowed per the standard. If the stalls are not full height, and you are attempting to protect each stall individually, at 33.5" wide per stall you would run into sprinklers being less than 6-0 on center, or floor mounted obstruction issues that would be almost impossible to protect with obstruction rules. NFPA 13(19) 12.1.10.2.3 SHADOW AREAS, takes into account situations like this. With allowable shadow areas up to 15 ft² per sprinkler. NFPA 13 does not require that 100% of the floor area must get protection, but does require that the building is 100% protected.

Reply
Chris
9/8/2023 10:57:17 am

To be clear, my above comment references a Residential section. In NFPA 13. There are many references to shadow areas in the standard, but are not quantified in size, with the exception of 13D and 13R. As you stated in the 'sprit of NFPA 13' in you question, the point I am making is there are situations in buildings that require quality knowledge of fire protection and common sense. Also, I am assuming that there is a gap from the floor to the bottom of the partitions that would allow water to cover the floor area freely without obstruction.

Reply
DAVE
9/8/2023 12:22:17 pm

If you have scrolled down this far... I also agree, that would be a mis-application of the standard. There are reasons that exception is limited in application.
Make sure you are measuring vertically from partition to deflector (B), not to ceiling.
Table 10.2.7.2.2 can be used A-to-B, or B-to-A but unless I mis-read the question (which is possible), I am getting a different result. And are you interpolating?
Horizontal Distance (A) tells the maximum range of sprinkler placement beyond which the sprinkler can no longer throw "over" the partition. (Like a "backwards upside-down" beam-rule)

I can usually get a sprinkler to cover stalls on both sides of a partition so half as many sprinklers are needed. And watch
out for minimum sprinkler-to-sprinkler distance.
We are starting to see architects design multiple very small gender-neutral stalls with partitions going full-height, so no escaping a sprinkler in every stall. In school situations I try to utilize concealed sprinklers, and smaller orifice for calc purposes.

Reply
Jesse
9/8/2023 03:00:15 pm

Ahhh gotta emphatically say "No" here. I think that's a pretty significant mis-interpretation of 13.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT