Omit Sprinkler from 4' x 6' x 5' Skylight in Pocket?

3/12/2021

9 Comments

 
I have a skylight that is 4-ft (length) x 6-ft (width) x 5-ft (depth). The room has a drywall ceiling and the depth of the pocket is about 4-ft of dry wall between the ceiling with an additional 1'-0" of glass (for the skylight) that domes above the roof at the top of the pocket.

Can I omit a sprinkler in the skylight per NFPA 13 2016 Section 8.5.7, or do I need a sprinkler in the skylight under Section 8.6.7 due to the depth of the unprotected ceiling pocket exceeding 36-inches?

NFPA 13, 2016 Section 8.5.7 (Skylights) permits sprinklers to be omitted from skylights not exceeding 32ft² that are separated by at least 10ft horizontally from any other unprotected skylight or unprotected ceiling pocket.

NFPA 13, 2016 Section 8.6.7 (Ceiling Pockets) says sprinklers shall not be required in ceiling pockets where all of the following are met: (1) The total volume of unprotected ceiling pocket does not exceed 1000ft³.(2) The depth of the unprotected ceiling pocket does not exceed 36 in. (3) The entire floor under the unprotected ceiling pocket is protected by sprinklers at the lower ceiling elevation. (4) the total size of all unprotected ceiling pockets in the same compartment with in 10ft of each other does not exceed 1000ft³. (5) The unprotected ceiling pocket has noncombustible or limited-combustible finishes. (6) Quick-response sprinklers are utilized throughout the compartment.


​​​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Mike
3/12/2021 09:20:23 am

According to the 36" requirement, yes.

Reply
Bill
3/12/2021 09:23:33 am

Section 8.5.7 would apply since the skylight is less than 32 sq ft. The standard is silent on the depth. The concern over heat collecting in the skylight was resolved by limiting the size and requiring the minimum separation of 10' from any other skylights or unprotected ceiling pockets. Skylights greater than 32 sq ft would be required to comply with 8.6.7.

Reply
DANIEL ACOSTA
3/12/2021 09:23:42 am

I would say yes, it does require a head because it does not meet all the criteria for 8.6.7. Specifically, the second requirement of <36" in depth and 8.6.7 states that ALL requirements must be met to omit sprinklers in skylights.

Reply
DANIEL ACOSTA
3/12/2021 09:39:30 am

After re-reading the NFPA 13 handbook, I'll change my answer to no. You don't need a head in the skylight if it's the only one for the reasons that Bill and Colin explained.

Reply
Colin Lusher
3/12/2021 09:32:34 am

Sprinklers are NOT required in your skylight.

Bill is correct that section 8.5.7 does not have any depth or volume requirements. The only requirement is that it be smaller than 32 sq.ft.

The ceiling pocket rules do not apply to the skylight....the last paragraph of the ceiling pocket rules, section 8.6.7.2 confirms this: "Sprinklers shall not be required in skylights and similar pockets in accordance with 8.5.7."

Reply
Kelsey
3/12/2021 10:24:37 am

I agree with this. There is a separate skylight rule for a reason. No head would be required in this case.

Reply
Jesse
3/12/2021 10:38:37 am

Great question, because of the depth. However, its not a ceiling pocket, its a skylight. As such, 8.5.7 governs, not 8.6.7. Because 8.5.7 doesn't specify a max depth, and only specifies square footage and not volume you should be able to omit this sprinkler.

Reply
Munnawar Khan
3/21/2022 02:59:09 pm

So I'd like to propose a similar yet different scenario, where 8.5.7.1.1 states "when a sprinkler is installed directly beneath a skylight not exceeding 32 sq.ft., the distance to the ceiling shall be measured to the plane of the ceiling as if the skylight was not present". Two things I'm not understanding here: 1) "..sprinkler installed directly beneath..": does this mean a head in the opening, somewhere in the depth of the skylight, from the finished ceiling up to the clear glass? 2) "..as if the skylight was not present." : the way I'm interpreting this is the distance from where the sprinkler is installed (the deflector) at the lower ceiling level - or we could say at the ceiling level where the skylight opening is - can be measure as if the skylight isn't there, meaning the deflector should be placed a min. 1" down from the opening, even if from the opening to the skylight glass is say 5 feet?
If that is the case where if a head is installed in this manner (so as to ignore the depth of the skylight) then here's one last proposal/query: a bulkhead is installed at a lower elevation than this ceiling level. And so now are we able to implement ceiling pocket requirements? The total volume of ceiling pockets is less than 1000 cu.ft. in the compartment, and with the other requirements fulfilled from 8.6.7.2 we'd be able to get away with heads only in the the lower bulkhead ceiling. My issue with this though is the presence of the skylights. Hoping someone can help me out here. Thank you.

Reply
Jeffrey Davis
3/7/2023 09:32:32 am

Now what if this was an FM Global project? FM Global, Installation Guideline for Automatic Sprinklers 2-0 does not mention any allowance for omission of protection for this scenario. Is protection in skylights required per FM Global regardless of skylight dimensions or orientations within the space?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT