MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Omit Fire Sprinkler in Auditory Testing Booth?

5/31/2021

18 Comments

 
​Does anyone have experience with auditory testing booths?

We have a 6-ft x6-ft audiology testing booth with a fully enclosed ceiling. It is about 7-ft tall and has been installed in a school for over seven years. Recently on an inspection, it was noted that it was required to have a sprinkler. I have dug through the code and can't see where it would not be required.

The only thing I found was in IBC 903.3.1.1.2 that it is "A room or space where sprinklers are considered undesirable because of the nature of the contents, where approved by the fire code official." In that case, it looks like we could add a smoke detector in there if it was approved by the code official.

They are very similar to office pods or even walk-in coolers and they are required in those situations. Because of the nature of the booth, I'm getting a lot of pushback from the users of the booth.

​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Franck
5/31/2021 08:20:32 am

Several questions in my answer :
- do you have a significant combustible load inside the booth (that would require sprinkler protection)
- do you have a sprinkler protection above the booth (or around it), that would control the fire spread if it starts inside the booth ?
In most cases, I would personally won’t require a sprinkler protection if the unprotected area is less than 100 sq ft within a fully adequately sprinklered building, unless you have the following conditions :
- significant combustible load inside or aggravating conditions such as flammable/combustible liquids
- several such « small » unprotected booths which, if you combine the area, would represent a threat for the building sprinkler protection

As an example, I have seen small offices (for a guard, or to house a computer) within a production building (or warehouse) and if less than 100 sq ft, considered the situation as acceptable

If you provide sprinkler inside, I would recommend recessed sprinkler or sprinkler with guards

Reply
Chad
5/31/2021 08:40:12 am

I concur with this except the 100sq ft, too large of an area to except, in my opinion. There are reasonable exceptions if the fire load is negligible.

And there are exceptions that prove the rule. Recently has a restaurant build a 4x8’ 4-5’ tall wooden box with a solid metal roof to hold trash cans… that is literally going to be filled with a sizeable fire load and ideally configured for rapid fire growth at times….inside. They couldn’t change it to a perforated roof due to the fact they wanted to store garbage in it, inside the dining room (yes that sounds like an awful idea). They had to drop a head in or find another place to store the trash, they found another place.

Reply
franck
6/1/2021 11:29:02 am

The 100 sq ft “rule of thumb” is coming from the fact that sprinklers at the ceiling level should cover 100 sq ft each (sometimes more, but 100 sq ft is normally the maximum for EH and storage).
This being said, if the unprotected area is less than 100 sq ft, it will obstruct max one head and you will control the fire with the first ring around (if you take a square, to be conservative, it will end up with 9 sprinklers in addition to the one obstructed, ie 10).
It is a large area, you will end up with more smoke and water damage than with just one head inside, but you will save your building and damages will be somehow limited (except if other adverse conditions exist).
I am not saying that sprinkler inside would not be beneficial, but saying that no sprinkler inside might be acceptable.

The same way, you don’t protect all cupboards, underneath all tables, all small footprint cabinets, etc.

Anechoic chamber is another issue and should be protected (just remember to put upright sorinklers in the pendent position as the goal is to spray the water towards the combustible cones).

Glenn Berger
5/31/2021 08:55:19 am

I have used this exact clause to not provide a sprinkler in a "piece of equipment." Be careful on the installing of any type of smoke detector as it may also have detrimental effects of the testing apparatus.

Reply
Pete
5/31/2021 09:48:06 am

I absolutely loathe when people want to "push back", but they can't formulate an argument, because they don't know the first thing about it. So you end up with, "We never had to have a sprinkler before.", and a bunch of other nonsensical permutations.
Are there ever kids in the booth? Assuming this is where they put the cans on and respond with the keyboard arrows which ear they hear a pure sine wave tone in, it needs a sprinkler.

Reply
Zev Schramm
5/31/2021 04:31:26 pm

A sprinkler is definitely indicated, and should be installed.

Since there is pushback, the question then becomes an engineering judgement - is this a reasonable place to make an exception? Without knowing the exact details of the situation, my primary concern would be that the various foams and insulations used to sound proof the booth could be quite flammable. This means an exception should NOT be made, and a sprinkler SHOULD be installed.

I would work with the users of the booth to better understand and address their concerns. Presumably they think the sprinkler will negatively impact the soundproofing of the booth. This can probably be mitigated by proper air sealing of the sprinkler pipe at the penetration, and by adding additional insulation around the pipe. A flex-head style pipe or sprinkler may be desirable to help isolate the booth from building vibration.

Reply
Jay
6/1/2021 08:08:36 am

Doesn't the ceiling of the booth represent an obstruction over 4ft in width that prevents the sprinkler discharge from reaching the hazard?

Reply
James
6/1/2021 08:13:28 am

Yes, it does.

Reply
James
6/1/2021 08:13:05 am

I have not worked on an anechoic chamber myself, but they do make telescoping sprinklers (which I believe are FM approved) that are on flexible drops (to avoid sound transmission) and only drop down into the space with activation.

Just a quick search kicked this out: https://www.sprinklerinnovations.com/

Not inexpensive, but it does address the challenge and keeps protection within this area. As I understand it, NFPA 13 requires coverage throughout a building except for specific areas, and this would not be one of them.

Reply
Brad K
6/1/2021 10:51:21 am

I too have seen these used in the past.

Reply
Jesse
6/1/2021 09:29:21 am

I think instead of trying to find a place in 13 that says a sprinkler is required - you should begin with the presumption that protection is required, and then look for a code section allowing you to omit it.

Reply
James
6/1/2021 09:34:03 am

Agreed; NFPA 13 says as much right at the beginning (2016 Edition):

Chapter 4 General Requirements
4.1 Level of Protection. A building, where protected by an automatic sprinkler system installation, shall be provided with sprinklers in all areas except where specific sections of this standard permit the omission of sprinklers.

Reply
Franck
6/5/2021 03:00:20 am

From a code perspective, sprinkler would certainly be required because of the obstruction.
But from a fire exposure/hazard perspective? And possible consequences in case of fire ?
Working for a property damage insurance company, and acting as an AHJ at a certain level, we always make the balance cost/benefit.
If the result of omitting sprinkler is an uncontrolled fire, it is definitely required.

In that case, with a small footprint, and probably not such a big combustible load nor a serious aggravating factor, there are high chances that the fire would be controlled by the ceiling sprinklers without sprinkler inside the booth.
In that case, we would probably consider the situation as acceptable (and maybe make a recommendation for reliability).
What would be the situation if it was a big storage box/crate with limited combustible content 6’ x 6’? Would you require sprinkler inside the box ?
And with an equipment (tool machine, electric cabinet) 6’ x 6’ : would you ask for sprinkler inside (which is sometimes impossible) ot consider the situation as acceptable?

This is why insurance companies work with loss scenarios, one of them being the NLE (Normal Loss Expectancy), i.e.: the consequences of a fire in the area with the actual conditions and fire protection systems in service (no impairment).
And for recommended improvement, we make an NLE before (actual situation) and NLE after (if recommendation is implemented).
If there is no difference or if the difference is small compared to the cost of implementation (NLE / Cost), then it is considered acceptable.
But again, this is not a code/standard approach, it is an acceptability approach.

Reply
sean
6/5/2021 07:27:48 am

I would not accept that section as justification. I would tell you to put a head in there. It doesn't help the case you are asking for forgiveness instead of permission.

Reply
Mike
6/9/2021 08:17:17 am

Ask the AHJ. The auditory rooms could be considered pre-manufactured furniture where a sprinkler head may not be required. On the other side, I've had to put sprinkler heads in pre-manufactured phone booths. It all depends on the AHJ's interpretation.

Reply
sean
6/9/2021 10:44:35 am

In my opinion using the furniture exemption does not apply. You do not occupy furniture.

Reply
JOSEPH GLASKI link
10/20/2021 10:01:37 am

See NFPA 13:(2019).9..2.10 -Sprinkler are not required in hearing booths.

Reply
Jay
10/21/2021 10:41:14 am

9.2.10 is for unoccupiable equipment enclosures. A hearing testing booth is an occupiable space

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT