OK to "Tent" a Wet Sprinkler System in 0°F Attic?

4/1/2024

13 Comments

 
Is "tenting" wet system piping (in an unheated attic) an appropriate approach to protect the pipes when the outside air temperature can drop to approximately 0 degrees F for multiple consecutive days?

In this case, the soffit and ridge vents allow exterior air into the attic space and there is no air barrier to prevent cold air infiltration. I have reviewed NFPA 13 and 13R and cannot find a definitive answer.

​Many thanks for assisting.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Anthony
4/1/2024 07:54:13 am

It's appropriate if you have sufficient insulation above and heating bleed through form below.

I'd add keep the pipes away from the edges of the building and make sure you have at least R30 above the piping.

Reply
Dan Wilder
4/1/2024 08:09:13 am

The installation is to be in warm areas, not subject to freezing, or provide means to avoid freezing (antifreeze, tenting, dry system, heat trace, circulating, heat loss calculation) is defined within 16.4.1 (19' Ed). It's up to the installer to comply with the warm space installation as required per NFPA.

Tenting, within NFPA 13, just pushes over to 13D and the figures within A.9.1.1 as with the other reference 8.2.3.1.1 (19' Ed.) so both are more directed to a residential application but not specifically "not allowed" or "allowed", it's just an option.

If at all possible, keep the piping as far away from the exterior as available for the install, install the piping as close to the ceiling, and avoid wrapping the piping with insulation (hence the "tenting" method to allow the lower warm air to directly impact the piping) which can be difficult with the blown in insulation that is more being used (at least in my area) vs the rolled, (cellulose vs fiberglass). However, based on the short description and temps, this would not likely be an installation path my company would allow without some very specific language and details in the contract and plans.

See below as well:
https://nfsa.org/wp-content/uploads/2021/02/Insulation-White-Paper-final-2.pdf

Reply
RayJ
4/1/2024 08:18:09 am

Here in IL, or as I call it, the land of ice and snow, the best way to protect the pipes is a dry system. No matter how much tenting and insulation you have, all it takes is for someone to forget to replace the insulation.

Reply
S
4/1/2024 08:35:43 am

ND = Frozen Tundra. I would say any area where temps drop below 30 degrees for consecutive days (especially where wind flows through the attic) a dry system is the only way to go. Tenting is a joke because the insulation required never stays put. IMO

Reply
Glenn Berger
4/1/2024 09:28:09 am

Tenting sounds like a good engineering approach until the first time the system freezes and then breaks. Once this happens, then the approach of never again will be utilized.

Reply
Jesse
4/1/2024 09:53:16 am

It is appropriate, but I'd probably want to see a heat-loss to support it.

Reply
Jack G
4/1/2024 10:14:04 am

First rule of Fire Protection- wet systems :
1.0 Insulation does not create heat !

Reply
Pete H
4/1/2024 12:50:00 pm

In NFPA 13R (2016 edition)

Check out figure A.5.4.2(f) Insulation Recommendations - Arrangement 6.

It'll be a claim you can make in 13R, but antifreeze or heaters would still be better.

Reply
S
4/1/2024 01:13:04 pm

Correct me if I'm wrong, but I believe this is only for an area above the ceiling and 'not' in the attic space. Insulation over piping in the attic space will not stop the water in the pipe from freezing in North Dakota, so I imagine it is the same in any place above the freeze line? I think there may need to be a separation between the two areas, pipe in the joist vs attic space. Maybe separated by sheet rock or plywood?

Reply
Pete H
4/1/2024 01:40:34 pm

The exact ruling is that piping covered by insulation as shown in those diagrams is part of the area below the ceiling and not part of the unheated attic area.

Except, it is literally above the ceiling, the insulation just makes it considered as part of the heated space below the ceiling as per A.5.4.2 of 13R (2016), even though, as seen in all of the figures, the head goes from the unheated space into the heated space. (Assuming the AHJ agrees that the Annex is acceptable code.)

Was this just to have pipe in the attic to protect the upper floor or was this to protect the attic?

If you're just protecting the upper floor, it's pipe that is literally in the attic, but is not considered in the unheated space due to the insulation method as per the figures.

If you're trying to protect the attic itself, you're correct, this will not work.

If you're in 13R, you might be able to omit protection in the attic as per section 6.6.6 (13R 2016) "Sprinklers shall not be required in attics, penthouse equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively to and containing only dwelling ventilation equipment, crawl spaces, floor/ceiling spaces, elevator shafts where the elevator installation complies with ANSI 17.1 and other concealed spaces that are not intended for living purposes or storage and do not contain fuel-fired equipment.

If you're in 13, and it's a wood attic, you gotta protect that, no omission, and yeah, this pipe either needs to be a dry system, an antifreeze system, or heat traced.

I don't know whether this is in 13 or 13R, both were referenced.

Pete H
4/1/2024 01:42:09 pm

For reference, the area above the blown in insulation on A.5.4.2(f) is labelled "unheated attic space"

S
4/1/2024 01:55:59 pm

Thank you Pete.

Dewayne Martinez
4/2/2024 12:54:11 pm

In the past on 13R projects we have had the GC make a "box out" of the pipe with the blue polystyrene insulation board, add some grill registers in the ceiling below to transmit some heat and then have the insulation contractor provide what they felt was enough insulation on top to maintain 40F.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT