I have a Type V-A Group R-2 apartment building whose code summary indicates as having four stories atop two levels of basement, all of the same construction and occupancy, and requiring a 13R system type.
I’m no expert in the building code, but it's my understanding that in order to have a building taller than four stories and still use 13R, a 3-hour horizontal assembly would be required having Type I construction below such assembly and up to four stories above; this building looks to be Type V throughout six levels with no horizontal assembly. The large building is vertically separated into four individual buildings by 2-hour fire walls but I see no horizontal separation. Is there a way this proposed 13R sprinkler system can be code compliant (IBC 2015)? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
5/25/2022 06:23:44 am
Hi,
Reply
Todd E Wyatt
5/25/2022 08:26:35 am
Per 2021 IBC, a "BASEMENT" is defined as "a story that is not a story above grade plane."
Reply
Todd E Wyatt
5/25/2022 08:33:18 am
The prescribed requirements for utilizing an automatic sprinkler system in Group R occupancies per 2021 IBC is as follows :
Dan Wilder
5/25/2022 08:15:21 am
It also really depends on what allowances the Architect took, floor area increases, fire rating decreases.
Reply
Greg
5/25/2022 03:55:58 pm
I read the NFSA's explanation and looked at the picture of the residential and business use areas. I was left with the question about the depiction of the roof as 13R...
Reply
9/20/2022 06:31:12 pm
I'm interested to learn how a Mezzanine, as defined by IBC, fits within the 30 FT NSFA 13R limitation. A mezzanine, within parameters, does not contribute to building area or number of stories, but when measuring 30 FT does one include the mezzanine level height, or, rather measure up to the height of the floor of the base story within which a mezzanine exists?