NFPA 13 and NFPA 13R in Same Building?

1/25/2019

10 Comments

 
Is it permissible to have an NFPA 13 and 13R system in the same building, or by code is it an all-or-nothing prescriptive standard? The most common scenario we would see this apply is with first-floor retail/mixed use construction with residential above.

Posted anonymously by a member for discussion. Discuss this  | Subscribe
10 Comments
Robert Blakeman
1/25/2019 10:07:19 am

You cannot mix the two unless the two areas of the building are considered separate buildings under the building code.

Reply
Cameron Brown
9/19/2024 11:32:40 am

What constitutes 2 separate buildings? I have a 2-story building we are looking at z the first floor is a public assembly use (restaurant and bar), and the second floor is a residential use 1-2 family dwelling apartment. We are trying to achieve a 2-hour separation. This is a renovation-repurpose.

Reply
Claude
1/25/2019 10:30:46 am

If a residential building has an enclosed underground car park, do you use NFPA 13 for the car park and use 13R for the building

Reply
Dave
1/25/2019 10:48:47 am

While 13R is unlike 13 in that 13R is life safety, there are such scenarios, like the popular pedestal/podium scenario discussed here by Matt Klaus:
https://youtu.be/xHt5gGXMAmM

Reply
sean
1/25/2019 12:53:52 pm

the example you give, a mixed use retail first floor and residential apartments above could be a special building in the IBC a podium building and technically two buildings.

Lets look at something that is one building a hotel. The first floor has conference rooms, restaurant, etc. and then 2-3 floors of dwelling rooms (hotel rooms). The height is not exceeded per nfpa 13R and as long as the building area does not require NFPA 13 we go ahead with 13R. The controlling standard would be NFPA 13R, and 13R specially says that areas outside of the dwelling unit not specifically addressed in that standard should refer to NFPA 13. The building is being design and installed per NFPA 13R. While portions need to meet NFPA 13 the entire building only has one "system" for the building codes purpose.

Reply
Andrew Gonci
7/9/2025 06:18:31 am

This is partially true. A hotel is designated as an R occupancy and 13R that has areas needing to be covered by NFPA 13 like parking garage, kitchen, meeting rooms etc.

I am not so sure this is the same, though you make a valid point. I think the key here is that a hotel is one occupancy, vs a retail space and residents above is not.

We would consider this a commercial building, which falls under 13.

Reply
sean
7/9/2025 12:18:33 pm

my point is that one building means one standard.

James
2/13/2019 11:31:46 am

Like other's have said, it isn't permitted unless the buildings are considered to be constructed as separate buildings under the local code. Go into the explanatory information for Section 1.1 of NFPA 13R:

"Where buildings of mixed use can be totally separated so that the residential portion is considered a separate building under the local code, NFPA 13R can be used in the residential portion while NFPA 13 is used in the rest of the building".

Reply
miles
3/5/2020 12:32:31 am

A very thorough answer to this question can be found here:

https://www.meyerfire.com/blog/when-can-i-use-nfpa-13r-part-i

Reply
Andrew
7/9/2025 06:24:37 am

In this case you would require the building to be NFPA 13. Code is not the clearest but here you go.

If a building is mixed, the code would be based on the most demanding area. So Retail on the lower floor, residential on the upper floor, and these are two separate tenants, then it is 13.

Where you have a hotel with some retail, meeting rooms, parking garage, these are all incidental use spaces and the code addresses them. The building is 13R but the spaces that are commercial are protected in accordance with 13.

So this project would be consider 13

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT