Is there any adopted or proposed sprinkler design criteria for Electric Vehicle charging stations that will be included in new parking garages?
The 2022 Edition of NFPA 13 is increasing the design for parking garages from Ordinary Hazard Group I to Group II, but I have not found anything about protecting the charging stations. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Pete H
2/8/2024 06:41:36 am
FM Data sheets have also increased the hazard category for parking garages and car parks from a category 2 to a category 3.
Reply
Chad
2/8/2024 08:24:13 am
San Francisco FD has a new ordinance regarding that.
Reply
Ricardo Gonzales Jr
2/8/2024 09:42:02 am
Is there a requirement for the sprinkler system to activate an EPO? Water and Electricity don't mix safely and the mix makes electrocution very possible.
Reply
Franck
2/8/2024 02:45:18 pm
Unfortunately with li-ion batteries, the only solution is water. Huge amounts of water…
Reply
Tony Bowers
2/8/2024 11:50:17 am
Miami-Dade now requires EH2 in the area of the charging station and an additional hose valve(s) on the floors the charging stations are present in parking garages.
Reply
L Scott
10/13/2025 12:02:44 pm
Do you know where Miami-Dade posts their local requirements?
Reply
Jesse
2/8/2024 01:35:33 pm
This is, in my humble opinion, the biggest issue NFPA is facing today. So much of the standards and codes that govern what we do are derived from loss experience .Effectively, its a super large scale trial and error model.
Reply
franck
2/8/2024 02:39:55 pm
In Europe, it is going to the equivalent of EH gr 1 to 2.
Reply
Todd E Wyatt
2/9/2024 08:40:23 am
The scoping Code (e.g. IBC-2021) determines WHERE an automatic sprinkler system (ASPS) is required to be installed based on the building’s/structure’s Occupancy Classification (OC) and/or Specific Building Areas and Hazards (per IBC-2021 903.2.11).
Reply
Logan
5/23/2025 02:56:58 pm
Hey everyone. Seeing if anyone has seen an update for this since last year.
Reply
NorCal FPE
5/28/2025 06:11:17 pm
Hi Logan,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed