MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Mobile X-Ray Equipment a Sprinkler Obstruction?

8/18/2021

9 Comments

 
Have you ran into issues where you get cited from the AHJ because movable X-Ray equipment can potentially end up right in the location below one of the sprinklers in the room (just 3 to 4 inches below)?

I have two rooms with a sprinkler at each end of the table, and the AHJ surveyor is citing it as a potential obstruction.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete
8/18/2021 06:31:56 am

I'd say that you shouldn't have this issue because NFPA 13 (2016) 8.5.5.3.2 - Sprinklers shall not be required under obstructions that are not fixed in place, such as conference tables, and you identified the equipment as movable....

But, I'm not the AHJ, and what the AHJ says goes... so either move the x-ray equipment or spray around it like an obstruction.

Reply
Alex
8/18/2021 07:15:18 am

HI Anonymous,

This is a tough one. We all know the AHJ is going to get the final word in this fight.

NFPA 13 (2016) 8.5.5.2.1 states that “continuous or noncontinuous obstructions less than or equal to 18in. below the sprinkler” shall be treated as an obstruction. In this case, I imagine the AHJ is treating your equipment as a noncontinuous obstruction. Is it possible for you to hang a sign stating that the equipment cannot be left near the sprinklers)?

Best of luck!
Alex

Reply
NK
8/18/2021 08:18:05 am

Yes this happens all the time at hospitals. We typically add extra sprinklers or space the sprinklers outside of the area where the equipment can be moved.

Reply
David Kendrick
8/18/2021 08:39:41 am

I seem to remember that the purpose of fire sprinklers was to notify qualified personel to address and contain a fire incident.

A single (1) obstructed sprinkler could operate with the machine directly beneath the sprinkler head. Activation would signal the need for qualified personel.

Only special design systems are intended to extinguish a fire. The remaining systems are to be ever present guardians.

Just an opinion.

Reply
Dan Wilder
8/18/2021 09:30:21 am

This is my personal opinion and I may be reading much more into this, however:

Please don't get into the "AHJ gets what they want" mentality.

They are there to site things that are wrong and provide the section of the adopted/amended Code and/or Standard that is the problem.

They identified a potential obstruction issue, NFPA has a specific section on this as noted above by others. Your job isn't to play what if...what if they fill the room with mattresses, what about 50 O² cylinders, what if the kitchen decides they need a room to store all their styrofoam cups and plastic silverware while they wrap each box in a plastic bag.... that small room rule spaced QR 1/2" sprinkler looks to be a big issue now right?

If they want peace of mind, offer a solution to the GC/Owner and get paid to add the sprinkler or get them (GC/Owner) to provide a letter stating that they won't store the equipment beneath the sprinkler (put tape on the ground, hang a sign...). The surveyor does have a point of a potential issue, let's mitigate it without blind compliance.

I have lots of respect for AHJ's, I do not respect the power trip that some try to instill because they "want" something.

Reply
Clinton Summers
8/18/2021 11:55:21 am

AHJ have always been fun to deal with in certain areas. I have been in Fire Protection for 49 years (Local 669 fitter Owner/Designer) and worked for a local department for 31 years (F/F) so good luck with your issues I had mine over the years

Reply
Jesse
8/18/2021 09:54:18 am

I spent almost 20 years in the fire service before getting into fire protection / HPR engineering. I used to say, what the AHJ doesn't know about automatic sprinkler systems can fill a book. And we call that book NFPA 13. The AHJ is expected to be a jack-of-all-trades and a master of none. I have never lost a fire code appeal 1) because I choose my battles wisely and 2) because I know my profession.

2016 NFPA 13 8.5.5.3.2 discusses obstructions and says that sprinklers do not need to be under that are not fixed in place like conference tables.

The illustration of a conference table is important, because its presumes the table isn't 3-4 inches from the sprinkler deflector. As such, I would submit 8.5.5.3.2 doesn't apply, and 8.5.5.3 does. 8.5.5.3 doesn't qualify the obstruction as being portable - just an obstruction.

I think the AHJ is correct here.

Reply
Dave
8/18/2021 10:50:46 am

^^ ^^

Especially if the table is usually located in the same spot, the term "potentially" made it unclear to me.

Reply
Randy
8/19/2021 09:18:59 am

As an AHJ, we are not always right. We interpret the Codes as best we can but the engineers and installers often have more in-depth than us. AHJ’s do not have to take detailed sprinkler design/install tests, just tests on reading and applying the Codes. That said, most AHJ’s are open to professional discussions on Code interpretation. Don’t argue, just cite Code details and common sense approaches. That goes a long way. And yes, unfortunately there are bad AHJ’s just like in any profession, that feel it is their way or nothing. Sorry.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT