Are there any requirements pertaining to mixing fire sprinkler k-factors or temperatures in the same room?
We often come across unit heater placement, so at least on the temperatures I suspect that mixing in the same room happens fairly commonly to accommodate heat sources. Posted anonymously by a member for discussion. Discuss this | Subscribe
8 Comments
Corey
2/14/2019 10:02:52 am
Yes, you can mix temperatures within the same area. See NFPA 13, 2016 edition 8.3.2.5 for more detail.
Reply
Dan W
2/14/2019 10:24:14 am
If you are using the different K-Factors to minimize over discharge a system, then not allowed (23.4.4.9.2-16'). 23.4.4.9.3 & 23.4.4.9.4 allows different orifices within small rooms (exposure protection & directional spray sprinklers) with the Annex explanation giving a little more insight.
Reply
PETE
2/14/2019 10:24:22 am
Mixing K-factors is acceptable, however, you will want to either designate areas that certain K-factors are to be used, or be very knowledgeable about fluid dynamics. If you have one K-factor in one area, and another K-factor in another area- both areas should be calculated. This also applies to standard and extended coverage in portions of systems.
Reply
PETE
2/14/2019 10:30:44 am
I should add, after reading DAN W's comment above: the example I gave was a directional nozzle deluge system for a pumping station near an exterior dock; in which non-flammable non-combustible liquids were being pumped- mainly ammonia.
Reply
ZS
2/14/2019 01:49:16 pm
Adding to what others have said.
Reply
Dan W
2/14/2019 05:52:42 pm
For the FR/QR/SR comment, it can be done in accordance with 8.3.3.5 '16. This has saved me on a couple of projects with EC sprinklers.
Reply
Franck Orset
2/19/2019 11:06:26 am
Mixing K-factor is not a good idea, unless you have good reasons for it (such as a deluge system where the K factor may different depending on the area for the entire surface coverage, but this is not a sprinkler system...).
Reply
7/28/2024 04:30:01 am
Thank you for the insightful information on mixing K-factors and temperatures in the same room! Your detailed explanation helps clarify how these factors interact and the impact they can have on room conditions. I appreciate the practical advice and the way you’ve made a complex topic more understandable. Your guidance is invaluable for optimizing room environments and ensuring accurate measurements. Thanks for your expertise!
Reply