When using ESFR sprinklers to protect a low-piled storage/miscellaneous storage that is equivalent to an OH2 curve: what minimum operating pressure for the sprinkler do you use?
Do you just go by the nearest chart in the later storage chapters and go with the closest to your situation (so like 35 for a K16.8 and 15 psi for a K22)? Or do you just go with 7 psi like you do a standard sprinkler? The listings do not specify a minimum operating pressure except to say "per NFPA 13". Code references are always appreciated. Thank you for your time. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dan Wilder
8/23/2023 08:27:02 am
Is the configuration going to be used for higher storage in the future? This seems drastically more difficult and limiting for design and installation using ESFR vs a CMDA type sprinkler for this protection scheme.
Reply
Anthony
8/23/2023 10:12:26 am
Based on the referenced code below you could use any design criteria to meet the requirements of OH2. It begs the question why would you? As Dan also stated ESFR/CMSA is a vastly more restrictive method for protecting miss storage or other area. If you don't have to don't use ESFRs.
Reply
Pete H
8/23/2023 11:09:06 am
So I was spec'd into ESFR's when I asked this question.
Reply