What are the minimum number of design areas required for a new sprinkler system design?
It is based on hazard classification or system type? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Glenn Berger
5/24/2023 08:05:27 am
Simple answer to the question is: Yes and Yes
Reply
Jesse
5/24/2023 08:11:14 am
I always prove, and have my design staff prove multiple hydraulically remote areas. We only have to prove the most hydraulically remote area assuming a homogenous occupancy hazard class (i.e. all OH 2). However, its not necessarily intuitive. Hydraulically remote doesn't always necessarily mean most physically remote. So if I submit a set of AS plans with a single remote area to the AHJ, the reviewer may think that other area(s) are more remote. I usually only design high challenge stuff myself, but I did a fire station last week where I proved 4 different emote areas. I want to make it as easy on the reviewer as possible.
Reply
Barry L Brainard
5/25/2023 09:47:45 am
Being an AHJ myself, I always try to understand the rationale behind the number of design areas an engineer (NICET or PFE) places onto their working plans. I know according to NFPA 13 it states the most hydraulically demanding area, but that can be very subjective.
Reply
This is all contingent on your design. If you have a basic tree system, with all branch lines sized the same, and a single occupancy classification, one would suffice.
Reply
Vinnie
5/24/2023 08:22:45 am
Simply put...as many as it takes to prove that your design works
Reply
5/24/2023 08:30:31 am
Well, tell us a bit about the system and maybe we can guide you in the right direction. Is this an NFPA 13, 13R, or 13D system? What is the hazard classification? Is it a limited-area system?
Reply
Anthony
5/24/2023 08:32:17 am
There is no minimum number of sprinklers in a density area calculation for a full NFPA 13 system. Often in an NFPA 13D or 13R system you'll see calculations for only 1 sprinkler usually a 20x20 or 18x18 covering a largeish room.
Reply
Jay
5/24/2023 03:31:05 pm
The minimum number of sprinklers using the density area method is 5.
Reply
Casey Milhorn
5/24/2023 08:41:50 am
Very subjective and ultimately up to whoever has the final say so on approval, and also on your own piece of mind. My designers probably are overkill on number of calculations. If you are an engineering technician (NICET) or a FPE, hopefully pure ethics drives those in these categories to do the right thing. Many times the reviewers could easily be fooled by the designer not calculating a more demanding area. I would estimate that I, and most other experienced designers, could probably find a more remote area on up to 50% of shop drawings being put out today. I've seen many times where a designer picks the most geographically remote area without consideration for delta flow, additional fittings, mixed K factors, elevation changes, etc... Those of us that started with HASS and doing hand calculations have the advantage of more intimate knowledge of how water flows through a system. Many designers now a days just start playing with pipe size first and stop there, and never get into the nuts and bolts. Anyway, I could go on and on about calculations. The short answer is that these are life safety systems and you should do as many calculations as it takes for you to feel like you've met the intent of NFPA 13 (or other applicable NFPA) and that you can sleep at night knowing you designed a system that will work.
Reply
5/24/2023 08:55:29 am
The minimum for 13 is one, the minimum for 13R is two (compartment & lgt haz area), but if your 13 remote area pipe sizes are larger than other areas, if the heads are a different k-factor in another area or if there's a different density in another area, then you would need to add hyd calcs to prove those areas. Also, if the pipe does something unusual in an area, you may want to add a hyd calc. This would apply to light, ordinary, extra hazard occupancy & storage hyd calcs. Basically, if your remote area has the same pipe size, height above ff, heads & density as the other areas on the job, then one hyd calc of the most remote area is all that is needed.
Reply
It is important to justify the design to the reviewer. If there are multiple hazard levels in the system, I would recommend minimally one or two design areas per hazard level depending on location within the system. Depending on building size and height, as well as the hazard level, the demand can change greatly and it is important that the level of detail provides confidence in the design.
Reply
Dan Wilder
5/24/2023 11:21:51 am
I take the approach that the area that has the calc...does it define all other areas of the building for pipe sizing, lengths, elevations, hazards and configurations?
Reply
Barry L Brainard
5/25/2023 09:46:54 am
Being an AHJ myself, I always try to understand the rationale behind the number of design areas an engineer (NICET or PFE) places onto their working plans. I know according to NFPA 13 it states the most hydraulically demanding area, but that can be very subjective.
Reply