Metal or Steel Pallets Affect Sprinkler Design?

1/25/2022

12 Comments

 
Do metal or steel pallets have any adverse effects on a storage system's (either racked or high-piled) sprinkler  demand or density?

I know plastic pallets can increase the commodity classification of class I-class IV commodities, but I don't think metal does. I have a storage facility that can't use wood pallets but also can't protect the level of plastic commodities required without a costly fire pump.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Anthony
1/25/2022 08:07:40 am

No adverse effect on the system. Non combustible is non combustible.

Reply
Jesse
1/25/2022 08:08:41 am

Nope. Non-combustible is non-combustible and won't contribute to the fuel load.

Reply
Glenn Berger
1/25/2022 08:11:41 am

One issue that I have come across -- Metal pallets can be viewed as causing solid shelving configuration. But as far as adverse effects going from plastic to metal pallets - none.

Reply
Franck
1/25/2022 08:35:24 am

This is true, but only with oversized pallets.
With normal pallet load sizes, the footprint is the same as wooden/plastic pallets and you keep the required longitudinal and transversal flue spaces in the racks.

Reply
Ed K
1/25/2022 09:41:20 am

I was curious about this and searched NFPA 13 (2019) for "slave". For the particular conditions listed, section 21.4.1.4.2 says to increase ceiling density 20% when using a solid, flat-bottom, combustible pallet in lieu of conventional pallets. The OP is considering non-combustible pallets, but I take from this that under the right (wrong?) conditions, a slave-type pallet can increase the hazard vs a conventional pallet. I'm not making sense of that - can anyone enlighten me?

Franck
1/25/2022 11:22:37 am

You're right, it is quite strange as if you are looking to the definition of open vs solid shelves, having a solid shelf less than 20 sq ft is considered as open rack (as you would still have the longitudinal and transverse flue space).
This would mean that the solid flat-bottom slave pallets are more than 20 sq ft, or they block somehow the longitundinal flue space... which is rarely the case.

The only additional issue I see, is that when you have no load on the slave pallet, you still have the footprint of the slave pallet in the rack that would prevent water from the ceiling reaching loads underneath (the slave pallet remains in the racks, as would solid shelving). And this footprint is combustible as would be a solid plank of wood, thus a potential for fire spread underneath it.
But this is only a guess.

This won't apply with metal pallets as they will remain with the load stored on it, not as a slave solid flat bottom metal pallet.

Franck
1/25/2022 08:32:25 am

It should even require a lower density (but NFPA has not gone that far…).
Take a class I commodity where the fire load is only related to the pallets. With metal pallets, there is no more potential for fire spread.
So no adverse effect. And no beneficial effect as a conservative approach

They are used in some nuclear power plants for radiological effect : wood is immediately considered as a radioactive waste, while plastic and metal pallets can be surface cleaned. And metal has the advantage to plastic regarding the combustible load.

Reply
Anthony c Brown
1/25/2022 08:37:24 am

Just finished an analysis for a pharmaceutical warehouse rack system and in doing so took a hard look at various pallets. The quotes on the steel pallets came in around $230-285 depending on size. The fire retardant pallets meeting client requirements were coming in at $140. Just wondering if you have done a complete life-cycle analysis of the pallets v. the Fire Pump.

Reply
Alex
1/25/2022 09:33:33 am

I agree with Anthony's thought here, but make sure you think of reoccurring costs down the road as well. Along with possible replacement parts/maintenance.

Reply
Greg
1/25/2022 08:42:57 am

In the question I see that a key issue is the cost of a fire pump. Are you absolutely certain that your current system can not provide ample water ? Remember k factor changes, increased main piping size, gridd-ing the system might be enough to get a sufficient density for your commodity, configuration and height. Have any improvements been made to the building's water supply...can any improvements be made (example; a commitment by the city to increase pressure or improve line sizing, etc.). Is the underground lead -in or backflow preventer stealing too much pressure? You might need every last psi to make something work, short of a fire pump. And....can the plant manager give any concessions on storage height, arrangement, etc. that will get you to the correct density.

Also, does NFPA 13, Chapter 24.1 help you. Use NFPA "Free Access" if you do not have a subscription.
24.1 * General.
24.1.1
Sprinklers intended to protect storage fire risks shall be permitted to be installed using water supply design criteria that are different from the design criteria specified for the sprinklers described in Chapters 20 through 23 and 25 when specifically listed for such use within the limitations described in this chapter.

Lastly, as for the metal pallets...unless they are being stacked on top of the commodity, it would seem to be a non-issue.

Hope this can help you.

Reply
Franck
1/25/2022 08:59:57 am

I can see anyway a great advantage of using metal pallets versus plastic pallets, even though the water supply and sprinkler system can cope with the plastic pallets: you eliminate the hazard related to the plastic pallets, which is present in the storage configuration (obvious aggravating factor for your commodity), but would also be present with pile storage of idle pallets somewhere in the same warehouse. Plastic idle pallets storage is a real nightmare!

Reply
Alex
1/25/2022 09:35:34 am

Echoing others, no effect. Noncombustible!

I agree with Frank though, the benefit to the metal pallets is the fact that you are not adding to the fire load. Sadly, there is no reduction in density at the moment for that.

Alex

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT