Is it necessary to reduce the pressure serving hose connections or hose cabinets when there are the 1-1/2" or 1-inch hose connections installed in a facility?
What is the maximum allowable pressure for these type of hose connections? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
2/11/2022 07:15:23 am
As I just came across this the other day...
Reply
Jesse
2/11/2022 08:07:35 am
For 1.5" hose connections the maximum residual pressure is 100-psi and the minimum residual pressure is 65-psi
Reply
Barry Carr
2/11/2022 08:14:13 am
Class 2 Standpipe System with a 1 1/2 inch connection. The minimum design pressure for a standpipe system is contained in Section 7.8, “Minimum and Maximum Pressure Limits,” of NFPA 14. A hydraulically designed system is required to provide a minimum residual pressure of 100 psi at the most remote location in the building.
Reply
Jesse
2/11/2022 11:49:22 am
Not sure I agree here. 2016 NFPA 14 7.8 specifically references 2.5" connections. The OP's question involves 1.5" hose connections.
Reply
Glenn Berger
2/11/2022 08:32:41 am
Yes - It is necessary to reduce the pressure in hose stations that are intended for occupant-use. I recommend designing to the absolute minimums for these size hoses.
Reply
COLIN LUSHER
2/11/2022 11:59:57 am
If these are 1.5" hose connections are provided per NFPA 13, as required by the AHJ, then the requirements of NFPA 14 do NOT apply.
Reply
Alex
2/14/2022 08:13:54 am
Maximum residual pressure would be 100 PSI.