MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Maximum Distance from FDC to Check Valve?

3/4/2021

15 Comments

 
Is there a recommended maximum distance between the Fire Department Connection (FDC) and check valve?

NFPA 13 does not include a required maximum distance between the check valve and the FDC. I understand the intent is to reduce the length of non-pressurized pipe. My project includes a warehouse with a free-standing FDC located about 125-feet from the building.

Is it best to locate the check valve indoors, where it can be easily inspected and maintained, or, located underground, closer to the FDC where it would be buried?

​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
15 Comments
matt
3/4/2021 09:14:39 am

I have seen it done both ways. One thing to consider - the buried check valve is only a realistic option if you can access it (without digging).

Reply
Rusty Scott
3/4/2021 09:58:50 am

Agree with Matt, the 5yr check valve inspection is required to have access, this can get expensive to create a vault just for this valve, though I believe alot are just buried.

Reply
Fouad Dr
3/4/2021 09:22:04 am

I would say keep the CV indoors for ease of maintenance.

Reply
CJ Bonczyk
3/4/2021 09:57:52 am

Best to locate the check valve inside for maintenance by the sprinkler contractor or maintenance personnel. Combination vaults are convenient as well depending on the brand. I prefer to keep the water checked off on the inside in the even the check malfunctions so that it can be replaced easier. Also if the check outside fails outside you need to rely on the ball drip to properly drain the residual water in the FDC line (which doesnt always happen if it gets clogged. We commonly place a redundant check inside at the spigot for the FDC even if there is one at the vault so that any residual water drains at the ball drip in the vault or FDC outside and the UG FDC line into the building is dry up to our check inside.

We have had many FDC's far away from the building due to the fire departments collapse zone requirements being 1½ times the wall height.

Reply
Chad
3/5/2021 10:41:46 am

As an AHJ myself, I have to ask, if the building collapses, what good is the FDC? There are plenty of other reasons for a remote FDC, without a doubt. Did you get a reason from them?

I'm not saying there couldn't possibly be a reason for this. Maybe I can learn something new. Or, maybe I can add it to the list of things I hear that are unreasonable/crazy my fellow FD's required.

Reply
Jerry Flanigan
8/23/2023 04:45:02 pm

I would say it's better if your not in an area that freezes to put the check valve on the remote fdc piping above ground and install the siamese right on top. Makes it much easier to inspect. Very easy to perform forward flushes and you avoid having to dig up anything for inspections.

Curtis Tower
1/9/2025 08:53:46 am

Hey Chad!

The question isn't about the usefulness of an FDC in the event of building collapse...it's a question about the safety of the personnel and the equipment in the event that the fire overtakes the suppression efforts. An FDC attached to the building during pump operations puts the pumper and the engineer/pump ops personnel at greater risk.

I'm a designer and a firefighter. Sometimes, in spite of our best efforts at suppression AND regardless of the operation of the sprinkler system, a fire can mock you. This is especially true in older combustible construction with roofs that have been built over older roofs. These are almost a guaranteed collapse event.

Just my .02 worth.

Franck
3/4/2021 10:04:48 am

In addition, if you keep your check valve inside (heated building), you reduce the possibility to have frozen portions of your FDC, as only the heated portion of the pipe (downstream the CV) will remain wet.

Reply
Mike R
3/4/2021 10:17:57 am

As the others said leave the check inside and the pipe outside to the FDC dry.
125' isn't that far in the whole scheme of things.

Reply
Randy Kimbro link
3/4/2021 10:28:06 am

The Cleveland (Ohio) Water Department requires that the backflow preventer be located at the street, even though they do not inspection or service that device. As the AHJ, we like this location since we know there is pressurized water all the way to the riser which is verified every year via a forward flow test. If the backflow is located in the building at the riser, the FDC underground piping would only be verified as usable every 5 years during the FDC hydro. On the other hand, the backflow preventer is harder to maintain in the underground vault. And it is harder for the fire protection company to perform the 5 year FDC hydro since they have to disconnect piping in the vault to isolate the FDC. Bottom line, there are positives and negatives to either location for the backflow.

Reply
Dave L.
3/4/2021 12:09:10 pm

We spec the check valve to be inside the riser room all the time. And I try to remember to remind Civil to show a ball-drip for the underground, which I have seen accomplished a few different ways. (I've seen ball drips installed in the incorrect orientation too.) The NFPA #13 Annex says to locate the check valve to maximize accessibility and minimize freezing potential. And recommends to "reduce" the length of the non-pressurized line. I have read of concerns about the volume of water that may be emitted for the ball drip, the amount of air that may be pushed into the system, and the that since this line is not monitored, less pipe is better. Certainly valid concerns, yet no maximum length has been established. And I'm not a fan of buried check valves.

Reply
Dave L.
3/4/2021 12:12:19 pm

(* when the FDC is not incorporated into the backflow vault assembly and the check valve is located inside the vault.)

Reply
MIGUEL D.
3/4/2021 02:18:57 pm

I understand that the empty pipe section between the FDC and the check valve should be protected against corrosion.

Reply
Mark S.
3/5/2021 09:19:40 am

The real problem with "dry" underground pipe to the FDC is if it is ever damaged during subsequent excavation (no water leak), the only time you're going to know it is when the fire department hooks up to the FDC and blows it out of the ground!

Reply
Cristian H
2/2/2024 08:13:28 am

I agree with Mark. You would also detect an issue during the 5 yr hydrstatic test required for the FDC, but that is only every 5 years.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT