What is maximum distance above a ceiling before concealed-space sprinklers have to be installed?
I can't find the code reference, but seems like there was a 3-foot maximum if it was non-combustible with insulation on the pipe? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
12/27/2021 08:06:35 am
NFPA 13 does not have a stated minimum distance between the ceiling and the structure for the determination of where sprinklers would be required.
Reply
Dan Wilder
12/27/2021 08:09:39 am
13-'19 Edition
Reply
Dan Wilder
12/27/2021 08:31:55 am
The 36" trigger is more related to the concealed sprinkler listings and/or requirements but many of those allow up to 60" deep when I've looked through the latest data sheets.
Reply
Alex
12/27/2021 08:20:08 am
Hi,
Reply
Jesse
12/27/2021 08:29:48 am
There is no 3-ft exclusion in 13 that I'm aware of. There are however a lot of good information in NFPA 13 8.15.1.
Reply
Anthony
12/27/2021 08:33:47 am
Any space that is non occupied has no storage or low fire load and build with non combustion construction is allowed to be omitted from sprinkler protection.
Reply
sean
12/31/2021 06:20:21 pm
non-combustible concealed spaces typically do not require sprinkler protection
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop March '25 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
April 2025
PE PREP SERIES |