Listed Approach to Prime Fire Pump w/ Seawater?

1/24/2022

12 Comments

 
We have an external fire protection network in a marine port that has been served by 2 main electrical-driven fire pumps.

The proposed solution on this project is to utilize two main end-suction-type fire pumps using the seawater as a water supply source. 

The seawater is near the seashore at a lower elevation than the fire pump base.

To overcome the low pressure of the Net Positive Suction Head, a vacuum priming pump is installed on the suction line to get enough pressure to prime the fire pumps.

Considering this whole assembly is not listed nor approved, and there is no space for a water storage tank, what feedback might you have about the non-listed solution?

We can't provide an extended platform here with a vertical shaft turbine pump, so I'm at a loss for solutions. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Steve Frederick
1/24/2022 08:13:29 am

At the risk of providing a grossly oversimplified answer, why not use a backhoe to dig a channel from the shoreline to a vertical turbine in the pump house on the shore, and bring the sea water to the pump, as opposed to bringing the pump to the sea water?

Reply
Franck
1/24/2022 08:15:53 am

Priming tanks are still used in Europe where horizontal fire pumps are still allowed to take suction under lift.
I am not a big fan of such installations as you may have some reliability issues.

For the little history, earlier editions of NFPA 20 allowed centrifugal pumps to operate under suction lift, when they were provided with tank of priming water. After several foot valve failures that caused the loss of the priming water that destroyed the pumps running them dry, they were outlawed by NFPA 20 standard, beginning with 1974 Edition.
You may find some information if you have access to these earlier editions.

Here are some tips (this will not fulfill the NFPA requirements, but help to limit possible issues):

The maximum depth from which the pump would suck should not exceed 3.2 m (10 ft 6 in.).
In practice, the pump should be installed at the nearest position to the suction location.
Independent suction pipes should be provided where more than one pump is supplied under lift from the same intake or suction well.

The size of the suction pipe should be such so that with all pumps operating at overload capacity (150%), the total operating suction lift will not exceed 4.6 m (15 ft).

The suction pipe should be immersed in water with an elbow, and a filter flap (or foot valve) should be installed to the suction pipe end side to keep water between the water level in the tank/pond/river and the pump casing.

There is no need to install a shut-off valve onto the suction line. The filter at the suction flap end should be occasionally cleaned up and prevented to be clogged with dirt and foreign substances.
During cleaning, this process should be conducted by removing the suction pipe without emptying the reserve tank.

A priming tank should be installed, to avoid that air is present in the casing instead of water.
The priming equipment should have sufficient capacity to displace the air from the pump and suction pipe within 3 minutes.


Reply
Franck
1/24/2022 08:17:28 am

And some information regarding the prriming tank itself:

The installation should be done in accordance with the following:
- A priming tank should be provided to fill the volume between the backflow preventer and the foot valve (upstream and downstream).
- Only one pump should be supplied per priming tank
- The bottom of the priming tank should be at least 1.5 m (5 ft) above the top of the pump
- Automatically filled tank only are accepted: volume at least 500 l (130 gal.) or 3 times the volume of the suction pipe + pump casing, whichever is the greater
- If a manually filled priming tank is provided anyway, the minimum volume should be at least 950 l (250 gal.) or 3 times the volume of the suction pipe + pump casing, whichever is the greater. Replacement with an automatic filled priming tank is then advised.
- The water supply to the priming tank should be capable of keeping the tank full at all times.
- The priming tank should be connected to the pump discharge upstream of the check-valve, with minimum DN 50 (2 in.) diameter pipe. The connecting point should ensure that all priming water enters the pump and suction side, and is not wasted in the discharge pipe of the pump.
- The priming connection should be fitted with a gate valve and a check-valve, as close as possible to the pump
- The priming tank should be fitted with a low level gauge, set at 2/3 of tank volume, to automatically start the pump on a low level condition, and allowing tank refill through a calibrated orifice

Reply
Shady
1/24/2022 01:12:56 pm

Your explanation is very clear enough but if you have a diagram or draft for this assembly it will be very fruitful.

Reply
Franck
1/24/2022 03:17:18 pm

Contact me @ [email protected]

Franck
1/24/2022 08:21:50 am

Note that in your case, you have the additional issue of using salt water.
You may use the good advices formluated in NFPA for water supplies provided in marine applications.


In particular, it could be a good practice to use an additional pressure tank.
• The tank should be filled with freshwater
• The size should be calculated for:
The flow requirement of the hydraulically most remote system demand for 1 minute for wet systems
The flow requirement of the hydraulically most remote system demand for 1 minute plus the volume to fill all dry piping for preaction, deluge and dry pipe systems


Reply
RJ
1/24/2022 08:32:38 am

At the risk of seeming stupid, (and having never been near the coastline), wouldn't sea water cause a lot of corrosion in the pipes?

Reply
Glenn Berger
1/24/2022 08:43:19 am

Stainless steel (good grade) is typically utilized for this application.

Reply
Franck
1/24/2022 11:27:22 am

In addition to marine applications (where salt water is used for some obvious reasons), it is quite common to find such installations for large plants on the Coast.

The water supply is generally limited to hydrants and hoses (with a dedicated fresh water supply for sprinklers), but sometimes also for sprinklers.

But not a real desirable situation because of the corrosion issue + possible salt and other deposits accumulation at some areas that could block the sprinkler orifice, preventing a proper water distribution pattern.

This requires much more maintenance and the maintenance cost, over the years, may overpass the cost for the provision of a dedicated freshwater tank supply.

Glenn Berger
1/24/2022 08:44:29 am

Overall - work with the AHJ on this custom design configuration.

Reply
Jesse
1/24/2022 08:47:22 am

I don't envy your position, and there is a lot that can go wrong. I think Franck covered all of the bases. Its not a perfect answer, but I don't think there is one to your situation.

Reply
Franck
1/24/2022 11:20:38 am

You're fully right
The solution can't be NFPA compliant and the final reliability would remain questionable, especially on the long term.

I really don't like horizontal pumps taking suction under lift when I found one during one of my inspections.
There is always an issue (leaking foot valve, issues with the priming tank...).

But this configuration is still allowed in some European places... and not unusual.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT