MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Limited-Area, OH1 for Oxygen Cylinder Storage?

5/23/2023

7 Comments

 
Contractor is proposing using a single head system using IFC 903.3.8 Limited Area Sprinkler Systems to satisfy the sprinkler requirement from IFC 5306.2.2 One-Hour Interior Room.

Oxygen cylinder storage at vet clinic, "120 gal" tanks, total of "1644 cu. ft.".

Section 903.3.8 only allows LH or OH1 hazards. It was originally proposed as EH1, revised to OH1 but has not substantiated with code. OH2 comes up in multiple locations (NFPA 13-19 26.11.1.1, NFPA 400 21.2.10.2).

Is there a special provision, or some other way OH1 is appropriate here?

At this point the only solution appears to be relocating the room to an exterior wall which allows a "single head for cooling", which seems to not require any specific density, or to provide a full building system with OH2 in the oxygen room.

Thanks for helping me sort this out. 

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
SCHULMAN
5/23/2023 08:34:37 am

Oxygen is flammable, but it is not combustible.
Does that help?
(not looking at code ...)

Reply
Paul Pinigis link
5/23/2023 11:38:54 am

Oxygen is NOT flammable or combustible, it is an oxidizer only. It cannot burn, but it can increase the rate (and efficiency) of combustion.

Reply
Glenn Berger
5/23/2023 09:32:43 am

Is there only 1 cylinder of O2 in play here? Or are their spare (full) cylinders?

If multiple cylinders, then rated construction and sprinklers would be my recommendation.

I do not like to use the limited-area provisions as that gives no flexibility.

Reply
Danial Bartle
5/23/2023 10:10:14 am

Compressed oxygen is considered an oxidizer and 1500 cuft is the MAQ unless the building is fully sprinkled or where stored or used in approved cabinets, gas cabinets, exhausted enclosures, gas rooms, as appropriate for the material. (NFPA 55-20 6.3.1.1). Gas rooms have requirements as well if they are used to increase the MAQ. Sprinklers and/or Gas rooms increase the MAQ 100% each.

Same standard 6.11.2.1 Where sprinkler protection is required, the area in which compressed gases or cryogenic fluids are stored or used shall be protected with a sprinkler system designed to be not less than that required by 11.2.3.1.1 of NFPA 13 for the Ordinary Hazard Group 2 density/area curve.

There are likely other items and things I missed but this is a good starting point in NFPA.

Reply
Danial Bartle
5/23/2023 02:26:56 pm

As an additional note provided from the National Fire Sprinkler Association TechNote that actually came out today:
Chapter 4 of NFPA 13 starts out by requiring sprinklers in all areas of the building, but allows limited-area systems to comply with NFPA 13 rules where installed and permitted by the codes. Any partial or limited area system needs approval by the AHJ but every partial system should meet the definition a sprinkler system (2022 NFPA 13, Section 3.3.216, 2020 NFPA 25, Section 3.6.4) with:

1. Water supply
2. Control valve
3. Waterflow alarm
4. Drain

When the partial system meets the NFPA 13 and NFPA 25 definition above, then NFPA 25 would apply. Identifying and enforcing NFPA 25 on partial systems is difficult, but necessary.

The IBC, starting in the 2015 edition, (Section 903.3.8) lowered the extent of the limited area system with the following criteria:

1. Up to six sprinklers per fire area
2. Only in light or ordinary group 1 hazard fire areas
3. Connected to a wet standpipe or to domestic if capable of demand
4. Valves are indicating and supervised
5. Provide hydraulic calculations for approval

Reply
Naj
5/23/2023 11:46:00 am

Let the contractor install safety cabinets with the O2 cylinders in them.

Reply
David Toshio Williams
5/23/2023 03:36:51 pm

I just used the NFPA 101, 9.7.2 &9.7.3 limited area system for a LOX maintenance building that had a small (200SF) O2 storage room. I initially was confused about the EH/OH2 criteria in NFPA 13, as it initially pointed me towards 0.3gpm/SF over 2500 SF but it seemed the provision single for 0.15gpm/sf says ANY hazardous area that requires not more than 6 sprinkler heads and to only calculate the room area (200SF).

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT