MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Vertical Light Fixture a Sprinkler Obstruction?

4/10/2024

6 Comments

 
Good morning! Is there any NFPA 13 prescriptive option for this type of obstruction?

These are ceiling waves with a horizontal fall chain lighting system.
Picture
Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
4/10/2024 07:27:18 am

If the fixtures are below the sprinklers >18", there isn't any additional requirements for sprinkler coverage, unless they are over 48" wide and solid top, but an "open" top gets more inventive. If they are attached to or start within that 18" zone, best bet is to place sprinklers on either side and treat the light as a vertical obstruction. This can be very instance specific so reviewing each design for impact is needed.

The top picture would likely have a sprinkler layout around the circumference of the lights as a whole (that rounded soffit area) with additional sprinklers located within the light fixture vertical stranding as needed (would need a plan view to place sprinklers). The bottom picture, I would not have any additional protection as the top of the lights look "open" in addition to the distance below the ceiling (may not be 70% open but there's a good argument for install effort vs result with this atrium setup - heat collection/spray pattern development).

One of my previous projects with a "3D trapezoid light fixture" that we dropped sprinklers inside (you can see the darker sprinkler plate at the bottom)

https://www.gannett-cdn.com/-mm-/c47227a8de36cdd28558e322e7e37b0ae829cf4c/c=0-185-3200-1993/local/-/media/2015/12/10/Phoenix/Phoenix/635853534323258491-West-Valley-Casino-5.jpg?width=3200&height=1680&fit=crop

or similarly, we had several vertical strung light fixtures over various bar areas, we ended up placing sprinklers behind and in front (picture left), but others that were not obstructions (picture right) received no additional sprinkler consideration.

https://www.enr.com/ext/resources/Issues/Southwest_Issues/2020/11-Nov/02-Nov/Best-Projects/desert-diamond-casino3_Interior.jpg?t=1603898914&width=1080

Reply
Anthony
4/10/2024 07:36:16 am

Most likely to be open above so you can treat it as a non obstruction as Dan says above.

Alternatively say this was attached to the ceiling you could surround the fixture with closely spaced sprinklers working with an FPE to define discharge criteria to isolate it from rest of the building. you'd need AHJ sign off, but I've seen this for art instilations in the past.

Reply
Pete H
4/10/2024 08:02:32 am

Second pic looks to be a corridor so I'd call a suspended obstruction in light hazard and use NFPA 13 (2016) Figure 8.6.5.2.2. You look well below 18" under where I'd expect the deflectors to be so this should get you out of the need to protect around that.

The first pic looks to be in a mercantile space and is no longer light hazard.

So then I'd say if I'm running this strictly by code it matters the width of the obstruction. If it's under 4'-0", treat it as such and use 8.6.5.3.3 to void the need for protection. If it's over, and it looks over.... you technically should have to protect underneath the obstruction.

Though I'd note and restate Dan's points about how open these things are at the top of the obstruction is also of major relevance.

I say technically because your case seems unique enough and "direct underneath the obstruction" protection seems like it'd be an eyesore as well as not provide necessary protection while being liable for false trips as lights tend to generate heat. Your best bet might be asking the AHJ if they'd be okay with tight protection in the circumference of the circle around the obstruction and a sprinkler dead set in the middle over it. As Anthony outlines, an FPE would be very useful for this.


Reply
Franck
4/10/2024 08:40:25 am

As indicated above, may be problematic only under some circumstances when the lateral side do present an. obstruction because located too close to ceiling sprinklers

Reply
Jesse
4/10/2024 12:07:14 pm

Is this fixture open at the top?

Reply
Glenn Berger
4/10/2024 06:32:06 pm

I just one of these scenarios in a Las Vegas showroom. The spacing of the verticals did not really look that close. In this case I would consider it a non-obstruction.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT