MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is this Sprinkler Obstructed by Light Fixture?

5/7/2019

9 Comments

 
In a residential dwelling unit of a high rise building, would a drum light fixture (7"h x 14"d) qualify as an obstruction?

It’s a concealed head in a residential unit of a senior living building.

The contractor – of course – doe not have exact dimensions because it wasn’t reflected on the plans and was added later as a lighting option and only caught by my inspectors during Rough-In. As it is installed, the head is a few inches from the fixture in some units and “a few feet” in others. They want to add a head on the other side of the light, approximately 3 feet -4 feet away citing NFPA 13 8.10.6.2.1.4.

I feel that the light, while an obstruction, doesn’t count as continuous nor does it meet the requirements of a baffle, so if they want to add another head it’d have to be at least 6 feet away to prevent cold solder.

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Clifford Schulze
5/7/2019 11:02:48 am

NFPA defines obstructions as both continuous and non-continuous. Can you relocate the sprinkler head to meet the obstruction criteria, in this case 2'-6" - 3'-0" off the fixture?

Reply
Rob Stewart
5/7/2019 11:08:17 am

If a residential sprinkler head - it is 8' minimum distance between sprinkler heads

Reply
pari
5/7/2019 11:19:49 am

NFPA13 D Section 8.2.5.1.1 Pendent sprinklers shall be located at least 3 ft away from obstructions such as ceiling fans and light fixtures.
Section 8.2.5.1.3 where the sprinkler cannot be located 3 ft away from the obstruction, an additional sprinkler shall be located on the other side of the obstruction.

Reply
Clifford Schulze
5/7/2019 12:31:59 pm

He mentioned that this is a high rise building so 13D and 13R won't apply

Reply
PETE
5/7/2019 11:23:17 am

Echo what Clifford said. The inspector is correct. The scenario you described is a non-continuous obstruction to the discharge. Per §8.6.5.1.2 in NFPA 13, the sprinkler needs to either be spaced away from the obstruction based on the table. If you look at your concealed cut sheet and find that the deflector falls 1 1/2" out of the concealed head, you'd be 5 1/2" obstructed by the light (7"-1 1/2"). That would put your sprinkler 1'-6" to 2' away from the near edge of the light. That is to spray beneath it. The other option given under that section is to sprinkler on both sides of the light. Minimum spacing rules don't apply in this option because you're treating the obstruction like a wall. In other words, because of the obstruction the sprinklers won't spray on each other. The only requirement for the 2nd option is that the sprinklers are no more than the half distance of their maximum linear spacing from the center of the obstruction, again like it's a wall.

Reply
DaviD C
5/7/2019 02:48:58 pm

Pete well stated.

Just to expand on the cold soldering statement, if its treated as an obstruction or there is not the possibility of water from 1 head reaching the deflector of the other, it would not cold solder regardless of distance.

Cant tell you how many AHJ tried to state cold soldering when 1 head is 3 feet above another head in a different ceiling plane.

Reply
Jonathan Joseph
5/7/2019 12:25:43 pm

I would agree with Pari. You must be a minimum of 8 ' from the sprinkler or fixture in this case if you choose to add a sprinkler and keep the sprinkler that is obstructed.
I would try to re-locate if possible but it must be 3 feet away.
A light fixture cannot be considered a baffle because a tenant or owner can delete or change light fixtures at any time.

Reply
PETE
5/7/2019 12:45:07 pm

Anon did not state whether he was working per 13 or 13D, only that the space was a dwelling unit. Anon did state that the inspector objected to the placement per NFPA 13, so I assume it is an NFPA 13 job, not 13D.

Reply
Jonathan Joseph
5/7/2019 01:39:28 pm

It's a high-rise but the same rule applies to residential sprinklers.
NFPA 13 8.10.6.2.1.3(a) the four times rule or 3 feet away from light fixtures whichever works in the installers favor.

In this case the four times rule would be 4 foot 6 inches away and the obstruction table would be 4 foot to 4 foot 6 inches away if the deflector to obstruction vertical distance is 5 inches.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT