MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Sprinkler Waterflow Alarm Silenceable?

11/13/2020

4 Comments

 
We have a project where the AHJ is telling us they want the waterflow alarm to be silenceable. Our understanding under NFPA 13-2019 7.7 and 28.2.3.1 is that there must be an audible alarm within 90 seconds (per NFPA 72) and must continue until the flow stops, not when the fire alarm system silences the flow.

Are we correct in that waterflow is a non-silenceable event, by code?

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Jonathan Griffin link
11/13/2020 10:15:01 am

Remember to look at the opening pages of every NFPA standard: The AHJ may make interpretations as they see fit, and may also direct the Building Owners (and their contractors) to follow rules, procedures and orders that may alter what the relevant NFPA standard has published.
So long as Life Safety & Property Protection are supported & provided, the AHJ has the final say, not the standard.

Reply
Jake
11/13/2020 10:15:12 am

As an AHJ, we require an exterior horn/strobe above the FDC. This H/S is to be programmed to activate upon waterflow and not able to be silenced until waterflow stops. This exterior H/S fulfills the requirements of 7.7 and 28.2.3.1.

The interior notification appliances can all be silenced per NFPA 72.

Reply
Franck
11/13/2020 12:03:48 pm

7.7 indicates that an audible alarm should be available on the premises within 5 min after the flow begins and until such flow stops.

But if you you go to 16.11, you will see a different possible interpretation.

So as usual, the answer to your question is : that depends.

The waterflow alarm through the water motor and gong assembly is normally installed to inform people outside the building that there is a fire inside, so that they can alert the fire department.
This is particularly important for buildings not constantly attended (at night and/or during the week end) where you can count on witnesses in the street to alarm firefighters.

But it is not fully reliable as if this is the only fire alarm, there might be a long delay during week ends and nights.

In addition, this sole audible sound is very lound on the outside of the building, close to the gong, but light not be audible inside the facility (when process is operating and noisy) especially when multiple separation walls are provided within the premises.

But if you are in a constantly attended location and the sprinkler alarms for each system are reported to this location, it might be acceptable per the AHJ not to have the local water motor and gong assembly in addition.
Alarm will sound on the alarm panel and inform the right person to make the right decision.
And he can (of course) decide to sound the alarm off once he has been advised (otherwise he might get crazy listening to the alarm and might be difficult to call outside fire fighters).

To fully answer your question, it depends on factors that are not indicated:
are you speaking of the water motor and gong assembly alarm from the riser ?
is the location constantly attended and alarms reported to a central station constantly attended ?

In the second case, the guards may decide to sound an evacuation / fire alarm and at the same time inform the fire department or on-site fire brigade.

Reply
Jason Lupa, PE
8/19/2021 08:51:47 am

A fire department connection (FDC) is required for most automatic sprinkler and standpipe systems. Fire apparatus can connect supply hoses to the FDC to pump additional water/ pressure into the suppression system.

The IBC and NFPA 13 both require an audible appliance by the FDC, but it is NFPA 13 (3-10.1) that tells how to arrange the equipment to provide this outdoor audible signal. NFPA 13 also describes how the audible signal must operate: continuously (non-non-silenceable) as long as water is flowing. Sometimes jurisdictions adopt a local ordinance to add a visual signal and may even require a unique color. NFPA 72 has no requirements for outdoor notification by FDC’s.

NFPA 13 has two methods of providing the outdoor audible signal. A water motor gong is a mechanical device that is pipped into the water main and operates with water movement to sound a bell. As long as the sprinkler system flows water, the water motor gong will operate. NFPA 13 also allows the audible notification to be provided by an electrical sounder such as a bell or horn. These 120vac appliances are wired to the normally open contacts of a water flow switch (usually switches have two contacts; DPST) and will operate until the water stops. There is no requirement for battery backup or supervision. NFPA 13 only states that this electric sounder is to be wired in accordance with the NEC. Either method is usually supplied by the sprinkler contractor; the electric option is the most common for new construction.

Some engineers specify a dedicated non-silencable circuit from the fire control panel to supervise and control an weatherproof 24VDC bell. The bell would be programmed to sound continuously only for sprinkler waterflow conditions.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT