MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Is Pipe Schedule Extra Hazard Equivalent to EH1?

11/2/2021

6 Comments

 
If an existing building has a pipe schedule system that is determined to be "extra-hazard", without any design information, would that system be equivalent to an Extra Hazard Group 1 hydraulically-calculated design curve of 0.30 at 2,500 sqft?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Alex
11/2/2021 05:32:50 am

Hi,

Yes, if the sign only reads “Extra Hazard”, I would say you can only assume it protects Extra Hazard Group 1 (0.3 over 2,500 as stated).

Although, I would say that if you are modifying the system in any way that you should calc the system to ensure adequate protection.

Alex

Reply
Anthony
11/2/2021 08:24:07 am

Depends what equivalent means in this case.

NFPA 13-2016 Explicitly says extra hazard systems shall be hydro calc'd

11.2.2.2 Pressure and flow requirements for extra hazard occupancies shall be based on the hydraulic calculation methods of 11.2.3.


Without any design (water flow data) information no. Even LH and OH pipe scheduled systems require some minor calculations namely can the available flow/pressure over come the losses due to elevation and back flow preventer.

I have seen several scheduled systems in my time that are code compliant but are not able to satisfy a hydraulic demand curve when calculated.

With all that said I have seen several scheduled systems in my time that are code compliant but are not able to satisfy a hydraulic demand curve when calculated.

Run a calc.

Reply
Jesse
11/2/2021 08:34:38 am

Great question. The short answer is probably "yes". The EHPS was intended to provide an EH1 density. Now of course, if using 2016 NFPA 13, we can't even modify an EHPS system without calculating it per 23.7. So, my recommendation is take the extra time and steps to calc the system to be sure it is hydraulically adequate to do what you expect to do.

Reply
Dan Wilder
11/2/2021 08:37:26 am

This one I'm going to disagree with. This is two separate design approaches and while they accomplish the same end result for allowable design, I would not interchange the two.

Pipe schedule systems were base on providing a minimum PSI at the base of riser, calculated via a required minimum at the remote sprinkler + elevation loss without account for friction loss through the pipe or over discharge. Then a maximum # of sprinklers allowed on a branch line was enforced (6 in this case).

While the EH minimum PSI were left up to the AHJ (Per the 1978 version of NFPA I could find), both OH1 & OH2 had the same starting pressure or 15PSI. Even using a 5.8K sprinkler, max spacing of OH is 130 this would cover an OH1 (19.5 GPM) but fall short of the OH2 (24 GPM)...this gets worse with as the K-Factor decreases. Note that this minimum has been revised up to a 20 PSI in current editions (not sure when this occurred).

The system would be equivalent to a pipe schedule system for EH (possibly EH1 or EH2 assuming # of sprinklers on the line, pipe sizing, sprinkler coverage of 90FT², system area no greater than 25,000 FT² are all followed), as for what density, that would be proven via hydraulic calculations.

Reply
franck
11/2/2021 10:05:55 am

Not necessarily.
Pipe schedule is no longer applicable for extra hazard occupancies.
Note that in the "good old time", the required densities were not the same (there even used to be an OH Gr 3 occupancy).
For example, in 1978, EH gr 1 was 0.29/2500 and EH Gr 2 was 0.37:2500 (now respectovely 0.3 and 0.4).

Thios being said, for a small room, the answer is probably yes as you pipes would be large enougfh for a large density relivered by your sprinklers.
For a large area, this is more problematic as your demand point (if calculated) could exceed your water supply (in flow and/or pressure).
The only way to determine if your water supply is able to fulfill your demand is to make an hydraulic caculation, as stated by all other peers above.

Then, my conservative approach : if you are really dealing with an extra hazard occupancy which is greater than just a small room (io.e. more than 6 sprinklers), don't gamble... make an hydraulic calculation to be sure you are able to control a fire in that area!

Reply
Joshua Freedman
11/2/2021 10:18:00 am

I would say although it is possible, most often times it is not. I am an inspector and have seen many pipe schedule systems over the years that have been hydraulically calculated later to determine it's actual design, and as a previous commenter stated, it is highly dependent on pressures available, as well as pipe diameter installed. Most Extra Hazard pipe schedule systems I have seen calculated, or have calculated myself, usually come up around 0.15 - 0.20 / 3000, around an OH2 output. An option you might look at that I see sometimes is installing a fire pump on the system to boost the pressures up - with fire pump installation I have seen pipe schedule systems get into the 0.33 - 0.45 range.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT